Insulation of flow and return Heat Pump piping
I know mention has been made of ties on insulation runs reducing the insulation. Well, I have my installers coming on Wednesday to take remedial action on the external pipework runs. As will be seen in the photos, there is a ‘strap’ that has come undone and whilst I was taking this photo, I noticed how deep the plastic ties were compressing the insulation next to it. (I have very limited vision at present [12 months on, still waiting for a horsepiddal appointment] and as both the insulation and the ties are black, I had not noticed before). I know the strap is easily rectified and I think the control cables running in the plastic hose will need to be clipped to the wall separately and a few wall clips should be fitted but… am I right in thinking the insulation run is likely to remain compromised in terms of insulation value and will not recover anytime soon? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Hi @toodles That external insulation looks pretty poor to me, but not unlike my original insulation. Cable ties are definitely not to be recommended. I would recommend Dave Smith's products - see https://primary-pro.co.uk
He is very helpful and his insulation solutions make a lot of sense.
@toodles An interesting question so I did some research. An uninsulated 28mm pipe with a 55C difference between the water temperature and ambient will lose 76W/m. Insulating that with 1 inch foam will take that down to 10W/m i.e. 0.1 W/cm. Assume that compression doubles the losses to 0.2 W/cm and that each compromised section is 2 cm then the additional loss is 0.2 W per zip-tie. Assume 300 hrs per annum where the outside temperature is around 0 C then you get 60 Wh per zip-tie per annum, slightly under 2p. [someone might like to check my figures!]. On the other hand sections of bare pipe will be losing heat at nearly 8 times that rate and may be much longer. My external pipe runs look like the ones in Mike H's photo but I'll be been checking out the joints and exposed fittings in my garage just in case ..
There are many assumptions in this and I would imagine that the zip-ties don't destroy the insulation, merely move it around so the insulation will still be there, just moved to the adjacent bits of pipe.
@dr_dongle From your figures, this suggests the heat loss is undesirable but fairly insignificant. As to moving the insulation around, I’m not so sure as the overall diameter on either side of the tie does not increase in my experience, it is just that it is compressed where the tie applies pressure. I have now had the ties removed and the crushed sections have all been replaced with new; the replacement ties have been placed on top of adhesive ‘straps’ which spread the load and the ties are minimal tightness to perform the job. The vertical pipework no longer has any ties as the electrical ‘hose’ has been retained in a different fashion now. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles undesirable but insignificant sums it up pretty well though the cumulative effect may be another matter. I have a retro-fitted hybrid system here so I have two lots of everything with valves to separate them so I tallied 70 zip-ties (20 in the garage where temperatures can plummet), two pumps with shut-off valves, two filters ditto, three other pairs of shutoff valves, two air bleed valves, two drain points and four large compression fittings at the buffer tank. That is all in the plant room and some of that is in the return but it is all exposed brass and it all adds up. It was an interesting exercise and I'll do the calculation properly when I have a minute. 76 W/m on exposed copper is quite a thought ..
@dr_dongle Even at ‘insignificant’ levels, all those ties certainly add up! As best as I can see, no insulation has been squashed, squeezed or crimped on my system now; once those external pipe runs I photographed enter the brickwork, they are in the airing cupboard and there, the hot runs are insulated cleanly too. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles Sounds like you're sorted - these things niggle though once you spot them. I totted up the bare metal on the flow side of my system and I came up with just over a metre so on the coldest night in theory that could be 80 watts - unlikely for lots of reasons and it would provide some frost protection but it was an interesting calculation. The biggest single items were the pump with its isolating valves and a motorised valve.
@dr_dongle I saw a YouTube presentation from one of insulation makers; they showed how to create bespoke covers around pumps and various valve devices, very neat if fiddly to create! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 282 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Heat pump not reaching flow temperature
@davec Ive had a look at the screenshots. Lots of th...
By JamesPa , 16 minutes ago
-
RE: Vaillant aroTherm not heating with many faults
When I had a series of apparently unrelated faults my i...
By JamesPa , 33 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I cant see how that is the case if the earth is provide...
By JamesPa , 1 hour ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
OK, TBH I dont know enough about MLCP to comment with a...
By JamesPa , 3 hours ago
-
RE: Predicted Heat Loss from MCS calcs vs EPC vs actual
My gut feeling is that the heat pump is right sized. ...
By Tim441 , 4 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 5 hours ago
-
RE: Running from backup generaor in powercut?
@batpred In our case, 3 times each day when the Octopus...
By Toodles , 6 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Hi @sheriff-fatman Cycling at 5C and below is usuall...
By RobS , 6 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Here's the latest Fogstar ready built pack....
By Bash , 8 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick yes, even though the current system is ru...
By Tim441 , 8 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Solis confirmed that the S6 works with a single battery...
By Batpred , 8 hours ago
-
RE: Who has a V2G EV installation
I am wondering if in any V2X, would the car battery eve...
By Batpred , 9 hours ago
-
RE: Setback savings - fact or fiction?
Yes, by calculating it manually from the minute data, w...
By cathodeRay , 10 hours ago
-
Fan unit Making terrible noise HELP!!
One of a pair of fan units on an Earth Save Classic II ...
By GutoFfowc , 11 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
OK. I think your system, which seems well designed, is...
By JamesPa , 12 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 1 day ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 1 day ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 1 day ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 1 day ago