Insulation of flow and return Heat Pump piping
I know mention has been made of ties on insulation runs reducing the insulation. Well, I have my installers coming on Wednesday to take remedial action on the external pipework runs. As will be seen in the photos, there is a ‘strap’ that has come undone and whilst I was taking this photo, I noticed how deep the plastic ties were compressing the insulation next to it. (I have very limited vision at present [12 months on, still waiting for a horsepiddal appointment] and as both the insulation and the ties are black, I had not noticed before). I know the strap is easily rectified and I think the control cables running in the plastic hose will need to be clipped to the wall separately and a few wall clips should be fitted but… am I right in thinking the insulation run is likely to remain compromised in terms of insulation value and will not recover anytime soon? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Hi @toodles That external insulation looks pretty poor to me, but not unlike my original insulation. Cable ties are definitely not to be recommended. I would recommend Dave Smith's products - see https://primary-pro.co.uk
He is very helpful and his insulation solutions make a lot of sense.
@toodles An interesting question so I did some research. An uninsulated 28mm pipe with a 55C difference between the water temperature and ambient will lose 76W/m. Insulating that with 1 inch foam will take that down to 10W/m i.e. 0.1 W/cm. Assume that compression doubles the losses to 0.2 W/cm and that each compromised section is 2 cm then the additional loss is 0.2 W per zip-tie. Assume 300 hrs per annum where the outside temperature is around 0 C then you get 60 Wh per zip-tie per annum, slightly under 2p. [someone might like to check my figures!]. On the other hand sections of bare pipe will be losing heat at nearly 8 times that rate and may be much longer. My external pipe runs look like the ones in Mike H's photo but I'll be been checking out the joints and exposed fittings in my garage just in case ..
There are many assumptions in this and I would imagine that the zip-ties don't destroy the insulation, merely move it around so the insulation will still be there, just moved to the adjacent bits of pipe.
@dr_dongle From your figures, this suggests the heat loss is undesirable but fairly insignificant. As to moving the insulation around, I’m not so sure as the overall diameter on either side of the tie does not increase in my experience, it is just that it is compressed where the tie applies pressure. I have now had the ties removed and the crushed sections have all been replaced with new; the replacement ties have been placed on top of adhesive ‘straps’ which spread the load and the ties are minimal tightness to perform the job. The vertical pipework no longer has any ties as the electrical ‘hose’ has been retained in a different fashion now. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles undesirable but insignificant sums it up pretty well though the cumulative effect may be another matter. I have a retro-fitted hybrid system here so I have two lots of everything with valves to separate them so I tallied 70 zip-ties (20 in the garage where temperatures can plummet), two pumps with shut-off valves, two filters ditto, three other pairs of shutoff valves, two air bleed valves, two drain points and four large compression fittings at the buffer tank. That is all in the plant room and some of that is in the return but it is all exposed brass and it all adds up. It was an interesting exercise and I'll do the calculation properly when I have a minute. 76 W/m on exposed copper is quite a thought ..
@dr_dongle Even at ‘insignificant’ levels, all those ties certainly add up! As best as I can see, no insulation has been squashed, squeezed or crimped on my system now; once those external pipe runs I photographed enter the brickwork, they are in the airing cupboard and there, the hot runs are insulated cleanly too. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles Sounds like you're sorted - these things niggle though once you spot them. I totted up the bare metal on the flow side of my system and I came up with just over a metre so on the coldest night in theory that could be 80 watts - unlikely for lots of reasons and it would provide some frost protection but it was an interesting calculation. The biggest single items were the pump with its isolating valves and a motorised valve.
@dr_dongle I saw a YouTube presentation from one of insulation makers; they showed how to create bespoke covers around pumps and various valve devices, very neat if fiddly to create! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 432 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 10 seconds ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 34 minutes ago
-
I cannot see the complete rcbo, since the photo is cut....
By Batpred , 47 minutes ago
-
RE: What determines the SOC of a battery?
The answer from Fogstar was crisp. My hypothesis, su...
By Batpred , 57 minutes ago
-
RE: Electricity price predictions
I am always impressed with how you keep abreast of so m...
By Batpred , 1 hour ago
-
RE: Setback savings - fact or fiction?
I fully understand your reasoning, same steady inputs s...
By cathodeRay , 1 hour ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 3 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 4 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 7 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 7 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 9 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 23 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago