Posted by: @tomasmcguinness

Air changes made a big difference and I ended up with figures between 6.5kW and 8.5kW heat loss. 

I still reckon my heat loss is around 7kW based on my heat meter measurements, but it’s clear there is still a big margin of error!!

I really wouldn't get to hung up on exact figures. Really ball park is good enough, no matter what anyone says. You are going to be choosing the next size up anyway. So 6 or 7kW will still end up with the same size unit.

You need to leave time for DHW heating when sizing also. So say (7 x 24hrs) / 21hrs, give you 8kW at your lowest likely ambient. Using a Samsung for example, the 8kW unit isn't good enough at -7 and 45 will only put out under 7kW. So you need to go to the next size which is 12kW. And that covers all your range of kW, 8 kW doesn't really over any of them allowing for DHW.

Well setup and an open system, no issues.

Spend you time designing the system, for low pressure drop, and low flow temperature.

 

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
👍
1
ReplyQuote
(@tomasmcguinness)
Trusted Member Member
208 kWhs
Joined: 12 months ago
Posts: 20
Topic starter  

12kW heat pump way too big for this house. Its min output wouldn’t be too far from 5kW, which is what my boiler’s minimum is. That boiler already cycles like crazy in mild weather. 

The Vaillant 7kW aroTHERM looks like what I’m after and should be able to modulate down to maybe 2.5kW or 3kW.

 

What makes up the 7/24/21 formula? I’ve not seen that one before.

Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Next big project is a heat pump!


   
ReplyQuote
(@johnmo)
Prominent Member Member
2299 kWhs
Joined: 2 years ago
Posts: 422
 

Posted by: @tomasmcguinness

What makes up the 7/24/21 formula? I’ve not seen that one before

You have two modes for the heat pump, central heating and DHW. While you are doing DHW you are heating the house.

So heat demand from heat meter you said was 7kW, you multiply that by 24 (hours per day) to get kWh heat required per day.

You need to allocate time for heating DHW, so based on my experience we heat for about 2 to 3 hours per day. So I chose 3 hrs.

24 (hours per day) less 3 hours is 21.

Divide (7x24) by 21 to get the power output required from the heat pump, so it can heat the house and make DHW. Make sure your heat pump can deliver that energy on you coldest day. You won't go short of hot water or be cold or have to use a secondary heat source such as the in built immersion kicking on costing you loads.

Don't get hung up on a size, stated on the box, every manufacturer uses a different scale. Samsung is the max output, so output on a hot day, Vaillant is the output on the coldest. They are very similar in output not magnitudes different as the name would suggest.

I am not suggesting you go with a Samsung unit, I just used them as an example where model line made the choice for you. In you case look at a different brand

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote



(@johnmo)
Prominent Member Member
2299 kWhs
Joined: 2 years ago
Posts: 422
 

Posted by: @tomasmcguinness

min output wouldn’t be too far from 5kW, which is what my boiler’s minimum is. That boiler already cycles like crazy in mild weather. 

I would guess you have many thermostats or radiator valves, shutting off system volume, rather than an issue with minimum turn down of 5kW from your gas boiler. You only need about 40L of water engaged to stop short cycling from a 5kW input.

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@tomasmcguinness)
Trusted Member Member
208 kWhs
Joined: 12 months ago
Posts: 20
Topic starter  

Far from it. I have no TRVs at all and I use a single point of control, with the current temperature being an average of every room in the house. When the demand is only 2.6 or 2.7kW, a boiler that can't do less than 5.5 is going to overshoot. My flow temp in weather like that can be less than 40 and they hysteresis is +/- 6, so it can cycle quite a bit.

Owner of a ridiculously oversized 35kW boiler and trying to make it as efficient as possible. 4.8kW solar PV with 5.4kWh storage. EV driver.
Follow my journey at https://www.youtube.com/@tomasmcguinness
Next big project is a heat pump!


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4742 kWhs
Joined: 3 years ago
Posts: 703
 

@johnmo Hi can you explain this statement about the 40L

I can appreciate that having a larger body of water to heat will slow the onset of cycling, but I cant see how it would prevent it. If your heat loss is 1kW and your minimum output is 3kW then eventually you will reach a point where the heat in the water cannot escape quickly enough and the heat pump will stop heating.

I suppose that if the water pump keeps running then the stored heat in the water would eventually dissipate and this could be some time before it reaches the point when the heat pump will start again. Is this what you mean?

I have a large amount of radiator volume (but cant remember the exact value off the top of my head) but i can still cause my heat pump to cycle rapidly if I reduce the flow temperature sufficiently.

Thanks

Addendum: Just done a quick calculation and I have way more volume available than 40L (over 60L) and my heat pump is a 5kW output

This post was modified 6 months ago 5 times by bontwoody

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@johnmo)
Prominent Member Member
2299 kWhs
Joined: 2 years ago
Posts: 422
 

Posted by: @bontwoody

Hi can you explain this statement about the 40L

You just about explained it yourself.

Image a kettle, it has 3kW element, if you put a cup of water in it it boils very quickly, full it it takes a while to heat up. 

So a boiler or heat pump has a target flow temperature, the heater controller will use a hysterisis above and below this to manage heat input. If you say the hysterisis is around 5 to 8 degs, 40L and 5kW comes out about right and gives around 10 mins running, off time will depend on heat dispersion rate. More volume gives a longer run time, less volume, shorter runs and quicker cool down.

Posted by: @bontwoody

have a large amount of radiators (but cant remember the volume off the top of my head) but i can still cause my heat pump to cycle rapidly if I reduce the flow temperature sufficiently.

I had a similar issue and had to increase the target flow temp hysterisis which fixed the issue. See here for explanation 

https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/hp-cycling-expected-or-undesirable/paged/3#post-32091

 

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@johnmo)
Prominent Member Member
2299 kWhs
Joined: 2 years ago
Posts: 422
 

Posted by: @tomasmcguinness

so it can cycle quite a bit

What sort of run and off time do you get?

Can you change the setting for how many degrees of heat the boiler adds per minute. Mine had a setting hidden away, called gradient, the default setting was way to high, changed to 2 degs a min, made a huge difference

 

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4742 kWhs
Joined: 3 years ago
Posts: 703
 

@johnmo I though I had LOL, then its the hysteresis I need to look at, Im not sure how to change that on my Samsung so a bit of digging is needed.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



(@mike-h)
Reputable Member Member
1827 kWhs
Joined: 3 years ago
Posts: 196
 

Posted by: @bontwoody

@johnmo I though I had LOL, then its the hysteresis I need to look at, Im not sure how to change that on my Samsung so a bit of digging is needed.

I believe that the Samsung compressor stops when LWT rises approximately 1degC above target LWT and restarts when LWT falls 2degC below target LWT. 

If system volume is 50L and the emitters are dissipating heat at 3kW, then the off time is around 3.5 minutes. This fits with your heatpumpmonitor graph more or less. 

I believe that the on time is longer because the power that heats the water up by the same 3degC is the difference between what the heat pump produces when it restarts and the 3kW that the emitters are emitting. 

For example, if the heat pump restarts at 4.5kW, which is 1.5 kW in excess of the emitters, then the on time should be approximately 7 minutes.  Your cycle time for the on   cycle plus the off cycle is about 8.5 minutes. When my 12kW Samsung short cycles, it also cycles on and off every 8.5 minutes and I have seen the same with other Samsungs. 

I don’t think that you can change the hysteresis on a Gen 6 Samsung. It appears to have one of the least sophisticated ways of avoiding short cycling of any common ASHP. Perhaps that is why a buffer is commonly installed as standard. 

 


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
4742 kWhs
Joined: 3 years ago
Posts: 703
 

@mike-h I had a search yesterday and that fits with what I was able to find, so no tweaking of hysteresis for me. 

I think that I might be able to push for a lower flow temperature once I get my extension built and have more emitters. 

It’s not really a problem as it only happens in warmish weather and the COP is fine running at over 5. 

On an academic level I wonder if it would be possible to change the hysteresis values via a modbus connection?

This post was modified 6 months ago by bontwoody

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
Page 3 / 3



Share:

Join Us!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security