Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@johnmo max flow temp of 32C! Do you have huge radiators or very little heat loss? You can’t be describing ufh since it’s responding too quickly.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
@johnmo max flow temp of 32C! Do you have huge radiators or very little heat loss? You can’t be describing ufh since it’s responding too quickly
It's UFH on 300mm centres, but prior to starting today I had been messing about with the heat pump a few days, so floor (or return temp was 20.8 this morning) so not much energy was needed to get it back to steady state. The return temp has been sitting at 21.1 degs for the last 10 hrs with no further heat input. Even though its cool here, we have no real need to add heat, but it was cool enough to play with ASHP.
Run data
Run 1 started at 07.55. Force stopped first cycle at 27.5 flow temp at 25 min run time (08:25).
Run 2 starts 08.35 (10 mins off) stops at 09.05 run time 30 mins. No changes
Run 3 starts 09.25 (20 mins off) stops at 09.45 run time 20 mins. No changes
Run 4 start 10.10 flow temp 21.5 at restart (25 mins off) stops at 10.35 run time 15 mins. Increase B25 to 0.5 to increase off time and run time.
Run 5 temp 21.2 at restart 11.12. 35 mins off. Run. Stops 11.30 run time 18 mins
Run 6 DHW 35 mins
Sun comes out house at 21.5. return temp 21.1
Running curve set to 25 degs at 12 OAT and 32.6 at -5 OAT. Restart delta 6.8 so unlikely to automatically restart until OAT gets down to about 8 or 9 degs, which should be fine. May need to fine tune a little in the heating season.
Had to make a small change this morning as the summer house had cooled to 18 degs this morning, because the heat pump wasn't starting. The 25 degs start temp on the WC curve was slightly too low. So instead of the WC curve starting at 25, I changed to 26 at 10 OAT. It did 4 starts between 7 and midday running an hour and 33 mins in total run time. Weather got warmer once house hits 21 ASHP sits waiting. Return temp is about 0.2 degs above the restart temp at the moment.
Just thought I would post back in this thread for any future viewers as what what Ive discovered.
It appears that the Samsung controller does not have any way of allowing a user to alter the hysteresis settings directly. They are set to the Samsung default.
Indirectly you can manipulate the level of cycling by opening/having more emitters and raising the flow temperature. This means that even though you might be able to heat your house at a lower flow temperature, you may need to keep it artificially high (and at a reduced COP) to reduce cycling.
Samsung heat pumps can be fitted with an extra PCB (MIM-B19N) to allow reading and setting of operating values directly via modbus. I would be interested to know if the hysteresis settings can be changed this way, if anyone has any experience of using the board.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyappears that the Samsung controller does not have any way of allowing a user to alter the hysteresis settings directly. They are set to the Samsung default.
The method applied here (below) can get around the issue with water law and thermostat. Basically run time is dictated by thermostat hysterisis on top of the water law curve.
Take a look here, post 28 of 63
@johnmo Thanks for the link. I am in effect running it in pure weather compensation mode as my samsung controller/thermostat is in my hall not my living room and set to 24C (which it never reaches). I am wondering if it might be better to extend the cable and put it in the living room and lower the thermostat temperature to turn off the pump when it hits 22.5C.
I have seen some posts which mention changing FSV #2092 which supposedly changes the amount of time the pump runs for after the heat pump is turned off. This would seem to be helpful but I cant verify these settings looking at the Samsung documentation.
If the hysteresis setting could be changed via modbus then its something i would like to play around with. If nothing else it would make a nice project 😉
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Some people even enjoy weeding their gardens I’m told!😉 Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodles@bontwoody Some people even enjoy weeding their gardens I’m told!😉 Toodles.
If you like weeding, we have a nice 45 Deg bank full of weeds, or is that a wild flower meadow? I think it's a wild flower meadow, the wife weeds.
@johnmo Beauty is in the eye of the beholder…😉 Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodles@bontwoody Some people even enjoy weeding their gardens I’m told!😉 Toodles.
LOL at least I can do my hobby out of the rain!
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @AnonymousPosted by: @bontwoodyappears that the Samsung controller does not have any way of allowing a user to alter the hysteresis settings directly. They are set to the Samsung default.
The method applied here (below) can get around the issue with water law and thermostat. Basically run time is dictated by thermostat hysterisis on top of the water law curve.
Take a look here, post 28 of 63
This is essentially how I have been running my Samsung - FSV #2091/2092 set to option 1 so the compressor can only be turned off by the 3rd party room stat. My unit is oversized and wants to cycle because it's putting out too much heat. I'd like LWT of 30C at 15C OAT, but the lowest the unit will achieve is 33-34C.
So I just let the 3rd party room stat switch ON/OFF calling for heat, set to 19C (we like it on the cooler side) and let the unit find it's own minimum LWT. Additionally, I can vary the hysteresis of my room stat.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @bontwoodyIndirectly you can manipulate the level of cycling by opening/having more emitters and raising the flow temperature. This means that even though you might be able to heat your house at a lower flow temperature, you may need to keep it artificially high (and at a reduced COP) to reduce cycling.
The COP may actually be better at that higher flow temp due to the reduced (or elimination of) cycling? All else being equal, a lower flow temp will give a better COP, but all else isn't equal when the unit is constantly cycling.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
- 26 Forums
- 2,645 Topics
- 61.8 K Posts
- 604 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
No, I agree entirely. There shouldn't be a need for an ...
By Majordennisbloodnok , 9 minutes ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 53 minutes ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 58 minutes ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 1 hour ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 14 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 23 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 24 hours ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 4 days ago