In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
Posted by: @cathoderayThe heat pump logic says it is warm outside, so the house needs less energy (only enough to balance the heat loss at that OAT), but in fact the house needs more.
That's exactly what my analysis above would predict. After the rise in oat the bit of the house you live in continues, for a while, to lose energy to the middle of the walls at a higher rate than would be the case in the steady state at the new oat. This continues until a new thermal gradient is established which falls continuously from inside to outside, rather than having a minimum in-between. The heat pump supplies energy corresponding to the steady state at the higher OAT and thus there is a deficit. This is a direct consequence of the fabric thermal mass (heat capacity in scientific terms). I would expect the converse to happen if there is a sudden fall in oat.
My boiler, which had a control loop based on iat, exhibited different, but no less annoying, deviations from perfect control. The problem for the designers of heating control systems is, i imagine, that they don't know the characteristics of the house (which will vary widely) and can't rely on installers or homeowners to dial them in. That's where controllers which learn about the house over a period of time have the edge!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A similar pattern happened again last night and into this morning, low overnight OAT, followed by rapid rise in OAT fooling the heat pump into thinking the house was warm, IAT must be fine when in fact it was anything but, it was actually falling:
I have now written some extra code in my auto-adapt script to detect this and if detected, then add a boost to the WCC end points. I will report back once it has had a chance to run, and can be seen to be working.
Midea 14kW (for now...) ASHP heating both building and DHW
I look forward to seeing the results of your script.
I fiddle with our WC curve increasing/decreasing between 0.55 and 0.75 according to the extent of wind chill. Strong winds and driving rain doesn’t get adequately compensated by WC alone, even on Vaillant’s active mode.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithI look forward to seeing the results of your script.
Thanks for your interest. It hasn't really been tested yet. The recent modification to the code was to deal with a rather specific circumstance, a rapid rise in OAT after a cold spell dialling down output prematurely, and that hasn't happened since adding the modification (I suppose a bit like it never rains when you take your umbrella!). What it doesn't (yet) do is deal with wind chill, which we have had rather a lot of recently. The script does do its thing, but it does it assuming no wind chill, meaning it doesn't (yet) do enough auto-adaption.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 428 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
In mild conditions, yes I turn the heating off. This i...
By trebor12345 , 45 minutes ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
Hi HenriWe were puzzled by a thread being moved into he...
By Sheriff Fatman , 2 hours ago
-
RE: Electricity price predictions
@transparent The Totnes Society seems to operative l...
By Batpred , 3 hours ago
-
RE: Grant Aerona circulation/system pump staying on
My AERONA 3 circulation pump runs constantly whatever t...
By damonc , 4 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Thanks, @sheriff-fatman. Happy for you to search any po...
By Majordennisbloodnok , 6 hours ago
-
Thanks, @cathoderay. I was aware of some changes to ...
By Majordennisbloodnok , 6 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
It's buried within what has become my ongoing post-inst...
By Sheriff Fatman , 11 hours ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 15 hours ago
-
This is what I answered, I really have no hope: "......
By Batpred , 1 day ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj oh yes they offer Daikin 8kW, they tried to fo...
By AgentGeorge , 1 day ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Good point! Just in case anyone re...
By Batpred , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 It would be very useful if you could tell us...
By trebor12345 , 1 day ago
-
RE: Benefits of an extra horizontal loop for GSHP
A correct sized collector is all you need. Saying this,...
By greenlight , 1 day ago
-
RE: Grant Aerona Short Cycling
@mikefl, thanks for sharing your operating data, very i...
By Steam Powered , 1 day ago
-
-
RE: Here is my heat pump installation with questionable COP in Italy
@jamespa Sorry for the late reply, I apologize for the ...
By materox345 , 2 days ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@editor Yes BUT that was 3 years ago installed in Janua...
By rob heatpump bob , 2 days ago
-
Thanks for your response. I have UFH downstairs and ...
By GeorgeA , 2 days ago