In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
Posted by: @cathoderayThe heat pump logic says it is warm outside, so the house needs less energy (only enough to balance the heat loss at that OAT), but in fact the house needs more.
That's exactly what my analysis above would predict. After the rise in oat the bit of the house you live in continues, for a while, to lose energy to the middle of the walls at a higher rate than would be the case in the steady state at the new oat. This continues until a new thermal gradient is established which falls continuously from inside to outside, rather than having a minimum in-between. The heat pump supplies energy corresponding to the steady state at the higher OAT and thus there is a deficit. This is a direct consequence of the fabric thermal mass (heat capacity in scientific terms). I would expect the converse to happen if there is a sudden fall in oat.
My boiler, which had a control loop based on iat, exhibited different, but no less annoying, deviations from perfect control. The problem for the designers of heating control systems is, i imagine, that they don't know the characteristics of the house (which will vary widely) and can't rely on installers or homeowners to dial them in. That's where controllers which learn about the house over a period of time have the edge!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A similar pattern happened again last night and into this morning, low overnight OAT, followed by rapid rise in OAT fooling the heat pump into thinking the house was warm, IAT must be fine when in fact it was anything but, it was actually falling:
I have now written some extra code in my auto-adapt script to detect this and if detected, then add a boost to the WCC end points. I will report back once it has had a chance to run, and can be seen to be working.
Midea 14kW (for now...) ASHP heating both building and DHW
I look forward to seeing the results of your script.
I fiddle with our WC curve increasing/decreasing between 0.55 and 0.75 according to the extent of wind chill. Strong winds and driving rain doesn’t get adequately compensated by WC alone, even on Vaillant’s active mode.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithI look forward to seeing the results of your script.
Thanks for your interest. It hasn't really been tested yet. The recent modification to the code was to deal with a rather specific circumstance, a rapid rise in OAT after a cold spell dialling down output prematurely, and that hasn't happened since adding the modification (I suppose a bit like it never rains when you take your umbrella!). What it doesn't (yet) do is deal with wind chill, which we have had rather a lot of recently. The script does do its thing, but it does it assuming no wind chill, meaning it doesn't (yet) do enough auto-adaption.
Midea 14kW (for now...) ASHP heating both building and DHW
- 22 Forums
- 2,037 Topics
- 44.4 K Posts
- 33 Online
- 3,250 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 4 hours ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@majordennisbloodnok, the same thought occurred to me, ...
By Morgan , 4 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I agree with @mars. My install was not dissimilar. ...
By JamesPa , 4 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 4 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 21 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 2 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 2 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 2 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 2 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 3 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 3 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 4 days ago