In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
Posted by: @cathoderayThe heat pump logic says it is warm outside, so the house needs less energy (only enough to balance the heat loss at that OAT), but in fact the house needs more.
That's exactly what my analysis above would predict. After the rise in oat the bit of the house you live in continues, for a while, to lose energy to the middle of the walls at a higher rate than would be the case in the steady state at the new oat. This continues until a new thermal gradient is established which falls continuously from inside to outside, rather than having a minimum in-between. The heat pump supplies energy corresponding to the steady state at the higher OAT and thus there is a deficit. This is a direct consequence of the fabric thermal mass (heat capacity in scientific terms). I would expect the converse to happen if there is a sudden fall in oat.
My boiler, which had a control loop based on iat, exhibited different, but no less annoying, deviations from perfect control. The problem for the designers of heating control systems is, i imagine, that they don't know the characteristics of the house (which will vary widely) and can't rely on installers or homeowners to dial them in. That's where controllers which learn about the house over a period of time have the edge!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A similar pattern happened again last night and into this morning, low overnight OAT, followed by rapid rise in OAT fooling the heat pump into thinking the house was warm, IAT must be fine when in fact it was anything but, it was actually falling:
I have now written some extra code in my auto-adapt script to detect this and if detected, then add a boost to the WCC end points. I will report back once it has had a chance to run, and can be seen to be working.
Midea 14kW (for now...) ASHP heating both building and DHW
I look forward to seeing the results of your script.
I fiddle with our WC curve increasing/decreasing between 0.55 and 0.75 according to the extent of wind chill. Strong winds and driving rain doesn’t get adequately compensated by WC alone, even on Vaillant’s active mode.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithI look forward to seeing the results of your script.
Thanks for your interest. It hasn't really been tested yet. The recent modification to the code was to deal with a rather specific circumstance, a rapid rise in OAT after a cold spell dialling down output prematurely, and that hasn't happened since adding the modification (I suppose a bit like it never rains when you take your umbrella!). What it doesn't (yet) do is deal with wind chill, which we have had rather a lot of recently. The script does do its thing, but it does it assuming no wind chill, meaning it doesn't (yet) do enough auto-adaption.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,372 Topics
- 53.8 K Posts
- 197 Online
- 6,053 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Weather compensation- why you should use it
@morgan i should have made clear ... LG call their vers...
By Tim441 , 20 minutes ago
-
RE: Forum updates, announcements & issues
@transparent D'Oh - I did look before I posted but I mi...
By dr_dongle , 36 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson is using an esphome controller which integrates...
By Mosibi , 50 minutes ago
-
Cascade 2x Grant Areona 10kw ASHP - Ongoing setup issues
I initially posted last winter and thanks to both the i...
By adam , 2 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Maybe you should buy your additional batter...
By Bash , 2 hours ago
-
RE: Data Accuracy Problem: Daikin 8kW Heat Pump's Onecta App vs MMI Power Consumption
@nursethescreens Yes, comfort and happiness of the fami...
By Toodles , 3 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 I have just realised that I omitted the Decembe...
By Toodles , 3 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
Thanks folks. I had tried googling an ethernet lab adap...
By z8lccda , 17 hours ago
-
RE: Changing from 4-port buffer to volumizer
@toodles I'm not concerned that the behaviour is not no...
By Andy1618 , 18 hours ago
-
-
RE: Setback savings - fact or fiction?
I agree, and I think there are two things in play here....
By cathodeRay , 23 hours ago
-
RE: Water Hammer After Heat Pump Install
That's really helpful. Yor last sentence confirms it'...
By JamesPa , 1 day ago
-
RE: Help needed with Grant Aerona 3 issues
First time posting so bear with me. Some bits that have...
By Adamp , 2 days ago
-
RE: Mitsu PUHZ-SW120YHA + EHSC-VM20Uk - Performance
All understood. Obviously its a bit house de...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 3 days ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 3 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 3 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 4 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 4 days ago