How to turn ASHP heating off!?
Hi
Ive just taken a reading from my Ecodan. I dont need heating, so put it on defrost mode on my handheld thermostat 8 week ago.
Over the last 8 weeks the ASHP has used consumed 198Kwh, much of that is on heating, even though I have the heating turned off.
Is there another way to disable the heating? The Ecodan does say that its heating is prohibitive.
At the moment I have only have the DHW come on once every 2 days to heat the cylinder for showers/washing up. (Im a very low user), so not sure why the heating is coming on at all.
Thanks
Posted by: @tuftyHi
Ive just taken a reading from my Ecodan. I dont need heating, so put it on defrost mode on my handheld thermostat 8 week ago.
Over the last 8 weeks the ASHP has used consumed 198Kwh, much of that is on heating, even though I have the heating turned off.
Is there another way to disable the heating? The Ecodan does say that its heating is prohibitive.
At the moment I have only have the DHW come on once every 2 days to heat the cylinder for showers/washing up. (Im a very low user), so not sure why the heating is coming on at all.
Thanks
Hi @tufty
I believe the Ecodan automatically adds about 2.8 kWh per day to the ‘energy used’ data. I spoke to a Mitsubishi engineer recently who said this occurs when the ecodan is in standby mode. However the energy hasn’t actually been used. He couldn’t tell me if this was a one off daily amount or a proportionate amount depending on cycling frequency.
It sounds like this might be happening with your unit. (198kw spread over 8 weeks equates to about 3.5kw a day)
If you had some defrost cycles in April you may have had additional values added to the energy useage data. Mitsubishi say it’s an estimated energy useage calculation and is not an actual metered reading.
This is an irritant for anybody trying to view performance of their heating system since the COP calculation is derived based on the inaccurate energy used data!
I guess a small comfort might be that your daily energy useage may be 2.8 kw less than the recorded data. So you could manually correct your daily energy used and work out a different COP for your system…. After all it would be just as accurate/inaccurate as the Mitsubishi calculated estimate… wouldn’t it?
Second Guessing (I’ve been trying to imagine why this 2.8 kw might be added to a daily consumption file and I think this might be linked to cycling which if happens frequently does literally reduce the efficiency of the heat pump. So it might be that regular cycling through the day might add up to an average energy loss of 2.8 kw However if stand by mode is seen as cycling - if this were the case - the 2.8 kw add on would be completely unnessessary. In the end it’s a correction factor that Mitsubishi have built in)
@sunandair Thanks for that answer. Very useful, and hopefully this is what it is.
Im pretty sure its adding the kwh to my main meter (not sure how I could actually check) so presumably Im paying for that energy that Im not using. 😐
Like you say, it completely skews the figures!
While I was in the garden the other day in the midday sun, I did hear the fan switch on, even though it was at a different time to what Ive set on the DHW schedule. I thought it odd as theres no reason (that I can think of) why it would come one. Ill never understand this system. 😐
Posted by: @tufty@sunandair Thanks for that answer. Very useful, and hopefully this is what it is.
Im pretty sure its adding the kwh to my main meter (not sure how I could actually check) so presumably Im paying for that energy that Im not using. 😐
Like you say, it completely skews the figures!
While I was in the garden the other day in the midday sun, I did hear the fan switch on, even though it was at a different time to what Ive set on the DHW schedule. I thought it odd as theres no reason (that I can think of) why it would come one. Ill never understand this system. 😐
If your electricity supply meter is recording energy usage, then it must be being used somewhere, since energy cannot be created or destroyed, it can only be changed in form.
If you have a Smart meter and the time, you could monitor usage and look for unexplained increases. Alternatively you could take hourly readings from your mains meter and again look for unexplained usage. Then check what the heat pump was doing at the time.
Posted by: @tuftyThanks for that answer. Very useful, and hopefully this is what it is.
Im pretty sure its adding the kwh to my main meter (not sure how I could actually check) so presumably Im paying for that energy that Im not using. 😐
So if you can isolate additional energy use coming from your heat pump there cold be various things happening. This is difficult to advise on without knowing quite a bit about your existing settings. And also your personal experience of accessing the menus on your main controller.
some examples of erroneous energy use might be:
- Freeze stat function set too high
- DHW temperature too high so needing immersion heater assistance
- Legionella setting activated frequently
etc. Of course it might be none of these and what you are seeing is the energy use on your DHW alternate daily heating cycle.
A quick check might be to see what outdoor temperature your Heat Pump switches on to protect your pipework from freezing. This is part of the “Freeze Stat Function”.
Our factory setting for this function was when the outdoor ambient temperature was as high as 15C which meant it came on a lot if the time. We now have it set to 3C. (We don’t have glycol or it could be lower)
Freeze stat function is located in the “operation settings” menu
Main controller/ Menu Button/ Service Menu/ Operation Settings/ Freeze Stat Function
Here you can see what the existing ambient is set at…. (the ambient can also be adjusted up or down.)
Can you confirm if you are familiar with the service menu? And what setting you have if you can locate it? Also can you confirm what part of the country you are located?
Any other information on your setup would also help eg hp size house style etc.
Posted by: @tuftyIve just taken a reading from my Ecodan. I dont need heating, so put it on defrost mode on my handheld thermostat 8 week ago.
Hi I’ve just been reading a few of your earlier posts so I can see you’ve been getting familiar with quite a bit of your ecodan settings already. With earlier discussions.
I note from above comment you have switched to “defrost” with your hand held thermostat. I’m guessing you’re still using the Salus third party thermostat? I don’t think this will turn off or alter your room heating settings on the Ecodan -as far as I am aware. As I understand it you cannot operate in Auto Adaptive mode with the Salus thermostat.
so if your system is still operating in weather compensation or flow temperature mode the change to the thermostat won’t switch it off.
The simplest option to switch off the room heating while keeping the system active so you can boost the DHW is to:
open the right hand menu (button 4) and pick the house button until you get the 🚫 sign show on the House icon. That will prohibit the heating from coming on.
Apologies if you already know this but I hope this helps.
I’ll post a picture of what the home heating screen will look like:
the home heating icon is the third image
Addendum
In your first comment you said:
“The Ecodan does say that its heating is prohibitive”. I think this is a slight misunderstanding in that the term PROHIBIT is used in their manual to describe stopping the heating or stopping the DHW etc.
Thanks so much guys.
@SUNandAIR : Yes, its starting to come back to me now, last spring I probably did as youre saying: go into the Ecodan interface itself and turn off the heating. (I have a short memory! 🙄 )
Im away for a few days, back on tuesday, so Ill investigate further then. Many thanks.
Hi @tufty
It was handy to skim read some of your earlier posts to learn what equipment your system is using and what kind of thermostat you had. I hope the suggestion is easy to follow and solves things for you.
Ive just turned off the heating on the Ecodan. I will check the readings in a few weeks and compare. Thanks!
It's handy that you can turn the heat pump off (CH that is) on the Mitsubishis. Our heat pump doesn't give you the option so we have to turn off all stats to stop calling for heat, which is a bit of a pain if temperatures do fluctuate in spring and autumn.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
On the Grant system you can either turn the ASHP controller off, but that also turns off the timed hot water boost. Or turn the 3rd party thermostat off, which is what I've done. The weather compensation characteristic will disable heating anyway if the outdoor temperature rises above 20degC, and from about 18degC upwards it turns the compressor off for extended periods due to minimum turn down of the unit being higher than heating load demand. It's pretty self-balancing to avoid overheating the house. In the cooler early morning, the ASHP will come on, but then cycle with long off periods during the day if the load demand is low. I found toward the end of the heating season this worked well, just taking the chill off in a morning, but not cooking the house come later in the day. It was very economical too. (Well it would be, with the compressor off!)
I've got the MMRS package and noticed Ecodan uses about 0.5-0.6kwh a day when idle (seen somewhere about 24 watts per hour which sounds about right). So you're looking at 15kwh a month just being on without any heating or hot water in addition
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 167 Online
- 3,410 Members
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
Watching Gary Does Solar’s latest YouTube video on the ...
By ChandyKris , 12 hours ago
-
Benefits of an extra horizontal loop for GSHP
Hello everyone, We're in the process of installin...
By thewiseoldbird , 16 hours ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 1 day ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 1 day ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 2 days ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 3 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 4 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 4 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 4 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 6 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 7 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 7 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 7 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 7 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 7 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago