The schematic on page 24 is the closest I could find with your system, the difference is you have a buffer tank instead of a 40 litre decoupler but they do similar jobs.
The system design is not straight forward and I would strongly recommend working your way through the components to understand the potential impact of each. I’ve also had issues with laser thermometers on pipes so would recommend some clip on pipe dial pipe thermometers from a plumbers merchant.
Record the temps in order:
1. Hex module (box on wall) right side red and blue are the feed from the heat pump and return. This is the closest to the heating source and will give you a means of comparison to the Vr10 temp probe which is in the top of the buffer tank and should be readable from the VR700 under the configuration screen assuming you have the installer codes.
There are a number of adjustable points in this system, hex module pump, radiator pump, ufh pump, not to mention just balancing the radiators. This added with the fact it looks like you have bypass valves on both the flow to the radiators and the ufh (which could be passing flow in to the return).
All these points can be adjusted but consistently measuring the temps from around the system you will be able to locate if it is system setup or design.
Posted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
I can't remember if you said yours is a newly installed system that has never performed correctly?
I have been working for while with a lady experiencing similar problems to yourself, and after numerous tests I'm coming to the conclusion that the main problem is associated with the water flow around the buffer tank.
If the water flow around the buffer tank is correct, then the temperature of the water flowing out of the buffer tank to your radiators and UFH, should be approximately the same temperature as the water flowing into the buffer tank from the ASHP. In the same manner, the return water from the buffer tank to the ASHP, should be at approximately the same temperature as the return water from the radiators and UFH going into the buffer tank. When the system is functioning correctly there should be a delta T of approximately 5C between flow and return temperatures.
As an example, if the water flow temperature coming from the heat pump is 35C, then the water going to the radiators and UFH should be approximately the same. The return water coming from the radiators and UFH should be in the region of 30C, as should the temperature of the return water to the heat pump. Any large differences would probably be caused by mixing within the buffer tank, which of course will affected the operation and efficiency of your system.
You could try measuring the temperature of the pipework around your system by using your IR temperature gun, but if you do not get meaningful results then purchasing one or two cheap temperature meters may be worthwhile.
Posted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
Did you manage to resolve your problems? Feedback would be welcome.
Posted by: @derek-mPosted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
I can't remember if you said yours is a newly installed system that has never performed correctly?
I have been working for while with a lady experiencing similar problems to yourself, and after numerous tests I'm coming to the conclusion that the main problem is associated with the water flow around the buffer tank.
If the water flow around the buffer tank is correct, then the temperature of the water flowing out of the buffer tank to your radiators and UFH, should be approximately the same temperature as the water flowing into the buffer tank from the ASHP. In the same manner, the return water from the buffer tank to the ASHP, should be at approximately the same temperature as the return water from the radiators and UFH going into the buffer tank. When the system is functioning correctly there should be a delta T of approximately 5C between flow and return temperatures.
As an example, if the water flow temperature coming from the heat pump is 35C, then the water going to the radiators and UFH should be approximately the same. The return water coming from the radiators and UFH should be in the region of 30C, as should the temperature of the return water to the heat pump. Any large differences would probably be caused by mixing within the buffer tank, which of course will affected the operation and efficiency of your system.
You could try measuring the temperature of the pipework around your system by using your IR temperature gun, but if you do not get meaningful results then purchasing one or two cheap temperature meters may be worthwhile.
@Derek-M what was the solution to this issue?
Hi @webcmg
The ladies problem has not yet been fully resolved, to do so may mean alterations to the pipework around the buffer tank.
With your particular system I would suggest that you identify where the pipework around your buffer tank is connected, check for any closed valves and whether or not any pumps are running. Then measure the temperatures of the pipework and to try to ascertain where the water may be flowing.
Posted by: @derek-mPosted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
Did you manage to resolve your problems? Feedback would be welcome.
Hi @derek-m - the plumber popped over today so was able to get some readings which are as follows:
Buffer
Flow 34
Return 31
Radiator circuit
Flow 34
Return 29
Radiator circuit (nearer buffer)
Flow 34
Return 31
UFH circuit without running radiators
Flow 31
Return 27
From ASHP to buffer
36 flow
33 Return
Radiator circuit when also running UFH
30 Flow
28 Return
Underfloor when also running Radiators
32 flow
28 return
All looks pretty normal?
Posted by: @derek-mSo what are the room temperatures?
@derek-m It's hard to tell because it's been warmer outside (10 degrees today) and I had to put the heat curve up to 0.9 in order to get any heat in the rads. It's now been escalated within Vaillant because they've accepted that the system isn't operating as per their design specification (i.e. comfort at the right level of economy).
Posted by: @webcmgPosted by: @derek-mSo what are the room temperatures?
@derek-m It's hard to tell because it's been warmer outside (10 degrees today) and I had to put the heat curve up to 0.9 in order to get any heat in the rads. It's now been escalated within Vaillant because they've accepted that the system isn't operating as per their design specification (i.e. comfort at the right level of economy).
Hi,
What I meant is what is the actual temperature in the various rooms, and are they remaining reasonably constant or are they varying with the outdoor air temperature?
@webcmg why did you want heat in the radiators…the whole point of any heating system is to have warm rooms, NOT hot radiators!
Professional installer
Posted by: @alec-morrow@webcmg why did you want heat in the radiators…the whole point of any heating system is to have warm rooms, NOT hot radiators!
Yes, but if the radiators aren't even warm... Then it's unlikely the room will be warm either. Quick update. Vaillant have been investigating, no real progress, no major changes proposed. Upstairs cold when it's cold outside. Seriously frustrated and disappointed.
-
Rodents! A word of warning for heat pump owners
2 hours ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
UFH and ASHPs
3 months ago
-
Installing your own ASHP - DIY
4 months ago
-
ASHP install contract and BUS grant money
6 months ago
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 31 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Rodents! A word of warning for heat pump owners
Hradline in Telegraph: Brace for plague of rats after s...
By Tim441 , 2 hours ago
-
What crazy nonsense are inverter limits and why are they imposed?
I’ve recently found out a DNO can impose an inverter li...
By AdamK , 3 hours ago
-
RE: Why so many sigenergi installer recommendations?
@saenergy for me I feel the powerwall gives me for flex...
By AdamK , 4 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As a potential heat pump customer, it would be good to ...
By Temperature_Gradient , 5 hours ago
-
A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
I felt it would be helpful to share some lessons about ...
By GrahamF , 6 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
Hi David We have an FTC7 but the settings seem to be ...
By RobS , 11 hours ago
-
RE: Octopus replacing the fixed 15p/kWh export rate with a market tracking one
@trbob I have just extracted the details for Agile Expo...
By Toodles , 12 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
The Ultimate Guide to Heat Pumps is less than a month a...
By Mars , 13 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor Hi Mars, We have just installed a Grant Aerona...
By GrahamF , 1 day ago
-
RE: Sanity check please. Battery storage and inverter sizing.
There are MCS guidelines about how close to the edge/ri...
By Old_Scientist , 1 day ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I estimated our usage on the following basis. The mos...
By Old_Scientist , 1 day ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 2 days ago
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 3 days ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 4 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 4 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 5 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 5 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 6 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 7 days ago