Posted by: @colin@webcmg Good luck! Bear in mind it'll take a while heat up the screed etc. I've got the Room temp Mod set to inactive so it solely relies on outdoor temp/Weather Comp.
@colin You know you want to get the problem sorted when you get out of bed to set this up! I also have room temp mod set to "none".
Do you have Adaptive heat curve set to "No"?
What is your desired heating temp set to on the controller ? 21 deg c?
Posted by: @webcmg@colin You know you want to get the problem sorted when you get out of bed to set this up! I also have room temp mod set to "none".
Do you have Adaptive heat curve set to "No"?
What is your desired heating temp set to on the controller ? 21 deg c?
🤣Yep, I've been out of bed to fine tune ours regularly for a few months. The Mrs is happier at least now she's warmer.
Adaptive Heat Curve should be off when only relying on external sensor, you'll notice that's the recommended setting in the system diagrams.
I don't rely on my indoor sensor (my VRC 720 is in the garage) and don't have it assigned to any zones. I don't need to set a desired indoor temp. Hopefully you can find the VRC 700 settings to match.
Posted by: @alec-morrowAre you using vaillant mixers for the floor? Or is there a pump for each floor zone?
raise heat curve and shut down all the floor and see how the rads respond?
No, I think there is a pump for each manifold and actuators for each zone. Will try this if Colin's approach isn't working. Thanks.
@colin You know you want to get the problem sorted when you get out of bed to set this up! I also have room temp mod set to "none".
Do you have Adaptive heat curve set to "No"?
What is your desired heating temp set to on the controller ? 21 deg c?
🤣Yep, I've been out of bed to fine tune ours regularly for a few months. The Mrs is happier at least now she's warmer.
Adaptive Heat Curve should be off when only relying on external sensor, you'll notice that's the recommended setting in the system diagrams.
I don't rely on my indoor sensor (my VRC 720 is in the garage) and don't have it assigned to any zones. I don't need to set a desired indoor temp. Hopefully you can find the VRC 700 settings to match.
By the sound of it you're in my parallel universe in Scotland! Wife unhappy and cold, controller in the garage, new build home, similar ASHP setup....
I don't have an indoor sensor either and that setting is also turned off already, but the panel has a desired temp setting which helps to modulate the water flow temp. At 21 deg the target flow temp was 33 deg so will monitor and adjust as required.
Thanks for your help, I will definitely buy you a pint if this turns out to work for us.
I’m a heating engineer and use these controls regularly
Vrc700/720 should be in occupied space so it can measure room temperature usefully.
it’s not a good idea to use anything other than vaillant controls with vaillant heat pumps. So if you have them jut programme them as a top limit stat.
with rads and UFH then a vrc71 or 70 should control electronic mixers to create zones. Multiple zones then appear in the screen. Each zone should be uniform emitters and floor structure/covering.
it’s a spectacular bit if kit, but vaillant not very good at promoting it and in a bid to build market suggest it will work with on off controls which it can do. But frankly I would never do that as it’s unfair to end users.
if you have multiple zones with on off controls I would expect to see a vr71 box somewhere..by the heat pump
bein elsewhere
Professional installer
@colin do you know or can you measure the flow temp to and from your radiators and ufh? Upstairs still freezing, rads cold despite 3 litres per minute flow on each circuit. Suspect you have a mixer built into the system.
Can you see any zones and different temp flow/heat curve for the radiator zones? If not I'm baffled by how it works.
Downstairs is toasty though!
Posted by: @alec-morrowI’m a heating engineer and use these controls regularly
Vrc700/720 should be in occupied space so it can measure room temperature usefully.
it’s not a good idea to use anything other than vaillant controls with vaillant heat pumps. So if you have them jut programme them as a top limit stat.
with rads and UFH then a vrc71 or 70 should control electronic mixers to create zones. Multiple zones then appear in the screen. Each zone should be uniform emitters and floor structure/covering.
it’s a spectacular bit if kit, but vaillant not very good at promoting it and in a bid to build market suggest it will work with on off controls which it can do. But frankly I would never do that as it’s unfair to end users.
if you have multiple zones with on off controls I would expect to see a vr71 box somewhere..by the heat pump
bein elsewhere
@alec-morrow I'm coming to the realisation that this is indeed the problem. There is a single zone and no electronic mixer. We have a VRC700 indoors in the garage next to the heat pump.
Sorry, but what does uniform emmiters and floor stucture/covering mean?
Is it likely to be expensive to resolve by adding a mixer? You can probably see the setup from pics in post 1
Ps I assume you meant vrc700 rather than vr70 or vr71, or are these different components?
@webcmg I have multiple Zigbee temp sensors to monitor temperature throughout the house, I stuck one on a radiator and also use an electricity smart meter and collect all the data into Home Assistant for monitoring it all. I have one sensor stuck to a radiator. I've attached a couple of diagrams so you can see the temp you can expect to see from the radiators and electricity usage.
The Heat Pump panel tells me the flow rate but that's an overall figure for both radiators and UFH depending on what's active which is both most of the time.
Do you have a motorised valve that control radiators and/or UFH ? Our engineer installed a timer for the valve supplying the radiators. If you have one, check the valve is open. Your radiators shouldn't be cold if the valves open. When I first moved in, we found things hadn't been set up correctly and had to manually override a valve and all worked after that.
Were your radiators specced for a low flow temp?
A mixer will give you control over the lower desired temp circuit, ideally the UFH. Given the rooms with rads are cold you either need a bigger rad or a higher flow temp. (Higher flow temp is bad for efficiency)
The real question is what size rads do you need to warm up the room. You can see from the calculation below that for the current flow temp the rad needs to be 4x the size then for a conventional gas boiler setup.
Assuming the top end of average flow to rads is 36deg and an air temp of 18.5deg I.e. a delta of 17.5 the rad would put out only 26% of the quoted delta t at 50deg. (Most rad figures are quoted in this figure)
Posted by: @webcmg@colin do you know or can you measure the flow temp to and from your radiators and ufh? Upstairs still freezing, rads cold despite 3 litres per minute flow on each circuit. Suspect you have a mixer built into the system.
Can you see any zones and different temp flow/heat curve for the radiator zones? If not I'm baffled by how it works.
Downstairs is toasty though!
Hi,
How are you measuring the flow rate and where is this being done? 3 litres per minute would seem rather low to me, I do believe the normal flow rate would be in the region of 10 to 25 litres per minute.
If downstairs is toasty, then check that any zone valves are operating correctly, or any pumps are operating when required. If you have a wireless thermostat then check to see if you are suffering dropout, which is closing any valve or shutting off any pump prematurely.
Posted by: @derek-mPosted by: @webcmg@colin do you know or can you measure the flow temp to and from your radiators and ufh? Upstairs still freezing, rads cold despite 3 litres per minute flow on each circuit. Suspect you have a mixer built into the system.
Can you see any zones and different temp flow/heat curve for the radiator zones? If not I'm baffled by how it works.
Downstairs is toasty though!
Hi,
How are you measuring the flow rate and where is this being done? 3 litres per minute would seem rather low to me, I do believe the normal flow rate would be in the region of 10 to 25 litres per minute.
If downstairs is toasty, then check that any zone valves are operating correctly, or any pumps are operating when required. If you have a wireless thermostat then check to see if you are suffering dropout, which is closing any valve or shutting off any pump prematurely.
Hi @derek-m
There are little caps on top of the manifold, which are between 2.5/3 when the heating is active. I assumed this was litres per minute, but could be wrong. All valves are open but I have just noticed that the UFH water is coming off the top of the buffer and the radiators from the bottom of the buffer. The lower pipes to the radiators are certainly colder than the top pipes - is this to be expected from a buffer? I've deactivated the UFH to see if the radiators heat up.
Posted by: @mattengineerA mixer will give you control over the lower desired temp circuit, ideally the UFH. Given the rooms with rads are cold you either need a bigger rad or a higher flow temp. (Higher flow temp is bad for efficiency)
The real question is what size rads do you need to warm up the room. You can see from the calculation below that for the current flow temp the rad needs to be 4x the size then for a conventional gas boiler setup.
Assuming the top end of average flow to rads is 36deg and an air temp of 18.5deg I.e. a delta of 17.5 the rad would put out only 26% of the quoted delta t at 50deg. (Most rad figures are quoted in this figure)
@mattengineer I have been told the radiators have been oversized to the requirements of the ASHP system. The radiator on the landing is a triple radiator and the others are probably slightly larger than normal, but not massively. How can I tell if they are suitable?
-
UFH and ASHPs
2 weeks ago
-
Installing your own ASHP - DIY
1 month ago
-
ASHP install contract and BUS grant money
3 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
3 months ago
-
Heat Pump starting current
4 months ago
Currently viewing this topic 1 guest.
- 22 Forums
- 2,076 Topics
- 45.5 K Posts
- 51 Online
- 3,355 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: I worry I've messed my Samsung settings up somehow
@alfapat that's this time of year? Maybe I'm just ex...
By Joshua , 7 hours ago
-
RE: 5 Star Service from Havenwise
@sheriff-fatman Exactly this is why a lot of our users ...
By HCas , 12 hours ago
-
RE: Solar Thermal DHW and ASHP
I'm beginning to think solar thermal is something that ...
By Alex_N , 14 hours ago
-
Feasible solutions to expand existing Sunsynk battery capacity
I have a 6.3kWp solar array with a 5kW Sunsynk inverter...
By Sheriff Fatman , 14 hours ago
-
RE: Commencing on an ASHP Installation Process
I received the BUS Grant permission email yesterday eve...
By Sheriff Fatman , 16 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
510kWh of solar PV from my 4kW Hyundai panels and SMA S...
By JulianC , 2 days ago
-
RE: Is my Samsung heat pump working too well?
Thats in itself is interesting. I have a Vaillant heat...
By JamesPa , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent Not a swell season then ☹️
By Toodles , 3 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 3 days ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 4 days ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 5 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 5 days ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 5 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 5 days ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 5 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 6 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 6 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 1 week ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 1 week ago