Posted by: @webcmgDoes anyone happen to know the current month energy consumption update interval for the 700/6 controller? It certainly isn't realtime (no idea why not!) and I have a significant variation in usage at the meter vs usage at the controller. If I can figure out when the controller updates I can rule out something else using so much energy.
Thanks,
Chris
Hi,
Check to see if you have a booster heater (immersion) or backup heater that may be operating.
@Derek-m @kev-m @alec-morrow @mike-patrick @mattengineer
General update. Vaillant attended and resetup the controller and checked the glycol levels. They set the programmer to 0.7 heat curve and 21 deg desired heat temperature. Room stats in hall and landing set to 18 deg c, others set to 21 (kitchen/snug area), lounge and dining room currently set to frost protection. At night the thermostats are set to three degrees below day time temperature as advise by the engineer. Hot water set to 50 deg c and recharges if it drops by 5 deg between 05:00 and 21:00.
I've been monitoring temps and, sadly, it's the same story. Warm downstairs, cold upstairs with room temps (now measured by my array of disconnected tado wireless trvs repurposed from my old house) between 14 and 18 deg c (see image). The landing stat does not turn off unless sun is shining directly through the window for an hour or so in the middle of the day and the temp, on the landing only, reaches 20 deg, other rooms remain at or, below 18 deg c. Rooms with vaulted ceilings and lots of windows (Bed 1 and 4) tend to be the coldest, ensuites are also very cold - not ideal at all.
24 hour Kwh at the meter is as follows, I think the latest is still reletively high:
16/01/2022 - 56.2 kwh
17/01/2022 - 48.7 kwh
18/01/2022 - 67.1 kwh
The installation plumber attended and measured the flow and return temperatures on each of the radiators. They were all within 2-3 deg c with flow ranging between 35-37 and return 32-35 deg c. He is happy that the plumbing is working as intended. Flow rates on UFH pumps have been decreased. Flow rate of radiator pump set to its highest setting. Flow rate indicators typically @ 2.5 litres per minute.
To experiment and optimise, what steps would you take now to try to increase heat whilst maintaining some level of economy? Should I:
- Leave on 24/7 at 18-20 deg across the whole house?
- Increase the night time temperature?
- Increase the desired temperature from 21 deg c on the VRC700?
- Increase the heat curve?
~£12 per day seems expesive given upstairs isn't warm 🙁
Thanks in advance for any further advice.
Posted by: @derek-mPosted by: @webcmgDoes anyone happen to know the current month energy consumption update interval for the 700/6 controller? It certainly isn't realtime (no idea why not!) and I have a significant variation in usage at the meter vs usage at the controller. If I can figure out when the controller updates I can rule out something else using so much energy.
Thanks,
ChrisHi,
Check to see if you have a booster heater (immersion) or backup heater that may be operating.
Immersion is off at the switch - how might I identify a backup heater? I think the difference in values is probably just a timing issue.
Just for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week. Our flow temps vary between 30-35 depending on how cold it is outside.
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
@webcmg is you need a higher curve for radiators than the floor…but more heat means more energy consumed.
and the floor temps need to be mixed down by a mixer controlled by the vr71 which works with the vrc700
You can’t get any manageable out come with out installing as vaillant design engineers (in Germany) intend
Professional installer
Posted by: @colinJust for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week .
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
Wow, this sounds incredible. When you say max assume you mean any TRVs and thermostats at say 25 deg c or something? What is your desired temp set at on the vrc700?
Posted by: @alec-morrow@webcmg is you need a higher curve for radiators than the floor…but more heat means more energy consumed.
and the floor temps need to be mixed down by a mixer controlled by the vr71 which works with the vrc700
You can’t get any manageable out come with out installing as vaillant design engineers (in Germany) intend
And I found out that it was Vaillant themselves who 'outsourced' the system design... sigh.
@colin assume your setup has a controlled mixer?
Are you using vaillant mixers for the floor? Or is there a pump for each floor zone?
raise heat curve and shut down all the floor and see how the rads respond?
Professional installer
Posted by: @webcmgPosted by: @colinJust for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week .
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
Wow, this sounds incredible. When you say max assume you mean any TRVs and thermostats at say 25 deg c or something? What is your desired temp set at on the vrc700?
Pretty much. I have the radiator TRVs mostly up to max, and the UFH zones mostly set to 25 deg, then let the heat curve adjust the flow temp. I use the TRV to limit the temp in the kids rooms. The key is to get the flow temp as low as possible while keeping the house at a comfortable temp. Our indoor temps are around 22-24 degrees, based in a relatively cold/exposed part of Scotland, but it's a well insulated new build.
Posted by: @webcmg@colin assume your setup has a controlled mixer?
That, I'm not sure I can answer. We have a Snug Underfloor Heating solution, which has manifold, actuators etc and it looks like it mixes but still trying to figure that part out. The heating engineer is due back soon to install the Internet Gateway and cooling resistor option so hopefully I'll get a better hand-over than I've had.
Posted by: @colinPosted by: @webcmgPosted by: @colinJust for some comparison, our house is a similar size with an Arotherm Plus 12kw, Unistor and VRC 720. We're just relying on the outdoor temp sensor with the curve set to 0.4. We just have the UFH and radiators stats set to max and on all the time and we're averaging 30kw per day for the past week .
We've adjusted the heat curve over time and 0.35 - 0.4 seems to suit our home best. Hope you get to the bottom of your issue soon.
Wow, this sounds incredible. When you say max assume you mean any TRVs and thermostats at say 25 deg c or something? What is your desired temp set at on the vrc700?
Pretty much. I have the radiator TRVs mostly up to max, and the UFH zones mostly set to 25 deg, then let the heat curve adjust the flow temp. I use the TRV to limit the temp in the kids rooms. The key is to get the flow temp as low as possible while keeping the house at a comfortable temp. Our indoor temps are around 22-24 degrees, based in a relatively cold/exposed part of Scotland, but it's a well insulated new build.
Thanks going to give this a try...
-
Installing your own ASHP - DIY
2 weeks ago
-
New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
1 month ago
-
Volumiser placement in Vaillant Arotherm + system?
2 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
ASHP heating issues / error code - advice very much appreciated
2 months ago
- 25 Forums
- 1,442 Topics
- 30.2 K Posts
- 15 Online
- 1,225 Members
Join Us!
Latest Posts
-
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 12 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 12 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 14 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 14 hours ago
-
RE: Effect of buffer tank or volumiser on heat pump system
I think that you will find that the best location for a...
By Derek M , 15 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 1 day ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 1 day ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 2 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 2 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 3 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 3 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 3 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 4 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 4 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 4 days ago
Heat Pump Humour
Latest Topics
-
By David999 11 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 6 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 7 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago