LFranklin
(@lfranklin)
Estimable Member Member
Joined: 2 years ago
Posts: 42
Topic starter  

I have a 12kW Samsung ASHP with Hive thermostat that my installers (Greener Living) don't seem to be able to make work consistently or economically.

The whole system is installed into the loft with the thermostat down in the L shape living/dining room. about 2 weeks ago the bedroom it sits over can hear what i think is the expansion vessel working and its very annoying when trying to sleep! - wasn't that loud until then so not sure why it is loud all of a sudden)

It's been installed since end of December now and i'm struggling with it not heating up last two rads on the system (which are downstairs in the living/dining room). They have added a second pump onto the return side of the system and that seemed to help for a few hours when first installed but now not coming back on again. if i turn the TRV off on others earlier in the system off the last two do get warm but even then not hot)

so the system is taking a lot of kWh to run to get the living room up to temp and then the temp is dropping quickly once it reaches 18 degrees as not enough ambient heat from the working radiators on the system.

i have had to take to turning thermostat down as couldn't afford the £15 per day electricity bill it was generating.

We had solar installed at the time too (16 x 405w panels) and even that isn't working right at just 1-1.8kwh per day generation at the moment which seems extremely poor for this size of system that works on PV and min 7 hours daylight at the moment.

All in all feel at my wits end with it all


   
Quote
(@dangermousie)
Eminent Member Member
Joined: 2 years ago
Posts: 16
 

Did they repressurise after the settling in period? My Vaillant shut itself off when it detected the low pressure. Our installer warned us that this was going to happen and was on the scene as soon as it did. 


   
ReplyQuote
Dunlorn
(@dunlorn)
Estimable Member Member
Joined: 3 years ago
Posts: 79
 

@lfranklin. I've a similar system to you, 2 x 12kW Samsungs controlled by Hive and 5.6kW PV array, south facing. 

The trouble with PV and ASHPs is the yield from the first is tiny just at the time the demand from second is greatest. These last couple of months have been similarly challenging for me, with a PV average for Jan 2kWh/day and December 1.5kWh/day although come the summer I'm expecting 10x these. I reckon yield and demand will be much closer matched in Spring/Autumn and then around 4 months of free power in summer. You should see similar so don't despair juat yet.

It sounds like your radiators aren't balanced. I had a load of air in mine for weeks after the ASHP commissioning so if you're not regularly bleeding them I'd start there. Make sure you keep repressurising or you'll find water not reaching all the extremities as well! Also worth checking how your system is controlled - is it in 'weather compensation' mode (the controller will say 'Water Law' if it is) and what the temperature settings are - the manual should tell you how to do this but if not please repost. Your radiators won't feel hot like with a gas boiler but should feel warm and - in weather compensation mode - should get warmer as it gets colder outside. 

2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.


   
👍
2
ReplyQuote
LFranklin
(@lfranklin)
Estimable Member Member
Joined: 2 years ago
Posts: 42
Topic starter  
@dunlorn I think it is in compensation mode. Can you tell me what the settings should be at please? Our home is an old stone house built in 1800's.
 
I have checked rads for air but doesn't seem to be any. The rads when they do heat up are hot at top and cold at bottom so the opposite of what usually happens with air.
 
Found out the expansion vessel has an internal leak .. would that have any bearing?
 

   
ReplyQuote
LFranklin
(@lfranklin)
Estimable Member Member
Joined: 2 years ago
Posts: 42
Topic starter  

@dunlorn can I ask how many KWH you're using roughly per day for each 12kw system?

What system are you using for monitoring.. I have shinephone app. 

 I've found my graph shows massive spikes of power regularly through day and thermostat only set to 17° 😭

Screenshot 20230129 083731

  

 


   
ReplyQuote
Dunlorn
(@dunlorn)
Estimable Member Member
Joined: 3 years ago
Posts: 79
 

@lfranklin

Consumption is very much dependant on external temperature. In the recent freezing spells in December and early Jan (we're in Scottish Highlands) our system had a few days with a truly eye-watering 120-130kWh! A more typically cold day, say 1-3°C, will use around 60-70kWh and if it gets to a balmy 5 or 6° or more we'll see 50kWh or lower. In October/early Nov we were using 20-30kWh. I generally only use a single unit as not at all convinced that the second has any value other than increasing bills - it's something I've asked the installer to look at.

The consumption range has come as something of a surprise but, if you consider a single ASHP drawing around 5kW at low temperatures and on for 15-20hrs per day, then you can soon get to these numbers. At milder ambient temperature the unit may only draw 3kW, and be on for less of the day, so you can see the difference. Part of the reason for the drop in efficiency when you get near to freezing is the regular defrost cycles. Mine were happening around every 45 mins at peak and - whilst they need to happen - they do end up drawing heat from your system and can mean you never get up to set point water temperature.

I don't think your spikes are defrosts, more like on/off cycling. The Hive only has to drop 0.1°C from its target to start the heat pump. This isn't ideal. A lower water temperature may help but this is a matter for experimentation. I also tried moving my thermostat to different locations as I found some were very prone to generating on/off cycles.

I've deliberately not changed my installers settings for weather compensation (yet) but I think these are too high, 50°C at 2° ambient and 42°C at 15° ambient. Notwithstanding that, I've never seen my unit discharge water at more than 44°, even when freezing outside, so we never get near the set point!

There's no monitoring btw, just me popping my head in a few times a day and making a note. I certainly don't want to be doing this for the rest of my days! 

2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.


   
👍
1
ReplyQuote



(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @dunlorn

@lfranklin

Consumption is very much dependant on external temperature. In the recent freezing spells in December and early Jan (we're in Scottish Highlands) our system had a few days with a truly eye-watering 120-130kWh! A more typically cold day, say 1-3°C, will use around 60-70kWh and if it gets to a balmy 5 or 6° or more we'll see 50kWh or lower. In October/early Nov we were using 20-30kWh. I generally only use a single unit as not at all convinced that the second has any value other than increasing bills - it's something I've asked the installer to look at.

The consumption range has come as something of a surprise but, if you consider a single ASHP drawing around 5kW at low temperatures and on for 15-20hrs per day, then you can soon get to these numbers. At milder ambient temperature the unit may only draw 3kW, and be on for less of the day, so you can see the difference. Part of the reason for the drop in efficiency when you get near to freezing is the regular defrost cycles. Mine were happening around every 45 mins at peak and - whilst they need to happen - they do end up drawing heat from your system and can mean you never get up to set point water temperature.

I don't think your spikes are defrosts, more like on/off cycling. The Hive only has to drop 0.1°C from its target to start the heat pump. This isn't ideal. A lower water temperature may help but this is a matter for experimentation. I also tried moving my thermostat to different locations as I found some were very prone to generating on/off cycles.

I've deliberately not changed my installers settings for weather compensation (yet) but I think these are too high, 50°C at 2° ambient and 42°C at 15° ambient. Notwithstanding that, I've never seen my unit discharge water at more than 44°, even when freezing outside, so we never get near the set point!

There's no monitoring btw, just me popping my head in a few times a day and making a note. I certainly don't want to be doing this for the rest of my days! 

I would suggest that you consider adjusting your weather compensation settings and then set your hive to 1C or 2C above the desired temperature. Doing so should hopefully reduce your consumption.

 


   
ReplyQuote
LFranklin
(@lfranklin)
Estimable Member Member
Joined: 2 years ago
Posts: 42
Topic starter  

@derek-m thanks what setting would that be please ..in 201* &


202*

And what settings would you suggest I enter at first?

I work from home full time so tend to have at around 17-18° max through day and maybe 19-20° on an evening (well in a perfect world where its working ok)


   
ReplyQuote
Dunlorn
(@dunlorn)
Estimable Member Member
Joined: 3 years ago
Posts: 79
 

@derek-m Thanks, I'll give that a go.

The installer (along with an engineer from Joules) has promised me a visit on 23rd Feb and I've a loooong list of questions. Most pressing is what controls the second (slave) unit, why it sends out water around 6° cooler than the master (when set-up appears identical) and why it makes no difference to comfort levels. Also, we've now had two days where for some reason LWT is stuck around 30°, and the system on constantly as it never reaches our 18 ° internal target. The list is getting longer. 

2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.


   
ReplyQuote
LFranklin
(@lfranklin)
Estimable Member Member
Joined: 2 years ago
Posts: 42
Topic starter  

@dunlorn what does your compensation settings currently say in 201/202?


   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @lfranklin

@derek-m thanks what setting would that be please ..in 201* &


202*

And what settings would you suggest I enter at first?

I work from home full time so tend to have at around 17-18° max through day and maybe 19-20° on an evening (well in a perfect world where its working ok)

I'm afraid that I have to go mow the grass (she who must be obeyed has spoken), so I will formulate a reply shortly.

 


   
👍
1
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @lfranklin

@derek-m thanks what setting would that be please ..in 201* &


202*

And what settings would you suggest I enter at first?

I work from home full time so tend to have at around 17-18° max through day and maybe 19-20° on an evening (well in a perfect world where its working ok)

Now that I am back with the 'living', so that there is no confusion, could you clarify what is meant by 201 & 202 and to which manual you refer. I don't have a Samsung heat pump to play with and have downloaded a number of Samsung manuals.

Using the reference number and the text description would probably be best.

 


   
ReplyQuote