Heat pump's integral circulator pump
Acting on current advise from this channel and others, I'm planning to ask my installer to remove the 4 port buffer and associated circulator from my 200 square meter UFH system over two floors.To be fair to them I had originally (naively) intended to use zoning controls. I'm running weather compensation - fully open loop and I have balanced the zones to achieve desired room temperatures 😀 .
My concern is "will the Daikin integral water pump be powerful enough to provide sufficient circulation" ?
6kW Daikin-ERGA06EAV3A - Indoor Hydrobox Model: EHBH08EF6V
Secondary circulator - Grundfos 25-50 180 (set to minimum speed )
Any advise please.
The quick answer to your question is that the Daikin's own circulation pump probably won't be powerful enough. So in instances like this, if the installer has calculated that it's insufficient, they can repipe your 4-port buffer into a volumiser and then utilise your Grundfos post volumiser to help flow.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Iam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
I understand how important feedback to a question can be, so here is mine.
With no disrespect intended to Mars, I decided to chance it and go ahead with the removal of the 20ltr. 4 port buffer and secondary water circulator to further simplify my system, retaining the redundant components with the proviso that they could be re-instated if needed, .
By using only the Daikin's integral circulator the flow rates appear to be sufficient with no increase in cycling frequency.
I'm very pleased with the results so far, with a COP (using Daikin's on-board energy meter figures!!) of just above 400%- with a happy wife to boot!
@ubert767, I'm really pleased to hear that your pump is strong enough. That’ll definitely be interesting reading for those with Daikins. I’ve been in private contact with a homeowner who’s had issues with Daikin’s defrost cycling and distribution pumps, so it’s great to hear yours is working well.
For the benefit of others, did you remove or bypass the buffer tank yourself, or did you have someone do it for you?
This is a great example for anyone still doubting whether buffer tanks actually improve system efficiency!
And, just to clarify, my doubts about the Daikin pump weren’t unfounded – most installers I’ve spoken to say that because buffer tanks are so commonly used, many manufacturers cut corners on the power of the internal pumps, leaving them with insufficient head.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @alfapat@ubert767 Thanks , no wonder I get too much of a temp drop , mine is 200L , too much mixing .
Ours is 100 litre and it's been piped for maximum distortion/mixing with an X shape between the pipes. Ridiculous. We're planning to get ours repiped in late spring.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
In order to answer my doubts about my buffer vessel I built a cheapish temperature logging system from a Raspberry Pi and five DS18B20 temperature sensors(one sensor on each buffer port and one measuring O.A.T.) This allowed me to see the differentials across the flow and return ports, to check the distortion in the buffer vessel and record the system cycling intervals.
Posted by: @alfapatIam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
It provides extra system volume which is useful for defrost but may well not be necessary. Have you any idea what volume of water you have in your secondary circuit.
One of the ports at top and the other at bottom to ensure it's actually both heated by the water passing through and engaged in the flow. Otherwise you could end up with most of the water in the volumiser just being 'bypassed'
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 121 Online
- 3,351 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman Thank you for a very detailed review of...
By ASHP-BOBBA , 11 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 12 hours ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
I'm more than happy to try to help. Are you op...
By JamesPa , 16 hours ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 16 hours ago
-
RE: 5 Star Service from Havenwise
@sheriff-fatman Good post. I am also considering Hav...
By Morgan , 21 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 21 hours ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet This is great assuming now the down stairs...
By ASHP-BOBBA , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 2 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 2 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 3 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 3 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
I would switch it off and see if anyone noticed. We use...
By Anonymous 5011 , 3 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 4 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 4 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 5 days ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 6 days ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 6 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 6 days ago