Heat pump's integral circulator pump
Acting on current advise from this channel and others, I'm planning to ask my installer to remove the 4 port buffer and associated circulator from my 200 square meter UFH system over two floors.To be fair to them I had originally (naively) intended to use zoning controls. I'm running weather compensation - fully open loop and I have balanced the zones to achieve desired room temperatures 😀 .
My concern is "will the Daikin integral water pump be powerful enough to provide sufficient circulation" ?
6kW Daikin-ERGA06EAV3A - Indoor Hydrobox Model: EHBH08EF6V
Secondary circulator - Grundfos 25-50 180 (set to minimum speed )
Any advise please.
The quick answer to your question is that the Daikin's own circulation pump probably won't be powerful enough. So in instances like this, if the installer has calculated that it's insufficient, they can repipe your 4-port buffer into a volumiser and then utilise your Grundfos post volumiser to help flow.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Iam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
I understand how important feedback to a question can be, so here is mine.
With no disrespect intended to Mars, I decided to chance it and go ahead with the removal of the 20ltr. 4 port buffer and secondary water circulator to further simplify my system, retaining the redundant components with the proviso that they could be re-instated if needed, .
By using only the Daikin's integral circulator the flow rates appear to be sufficient with no increase in cycling frequency.
I'm very pleased with the results so far, with a COP (using Daikin's on-board energy meter figures!!) of just above 400%- with a happy wife to boot!
@ubert767, I'm really pleased to hear that your pump is strong enough. That’ll definitely be interesting reading for those with Daikins. I’ve been in private contact with a homeowner who’s had issues with Daikin’s defrost cycling and distribution pumps, so it’s great to hear yours is working well.
For the benefit of others, did you remove or bypass the buffer tank yourself, or did you have someone do it for you?
This is a great example for anyone still doubting whether buffer tanks actually improve system efficiency!
And, just to clarify, my doubts about the Daikin pump weren’t unfounded – most installers I’ve spoken to say that because buffer tanks are so commonly used, many manufacturers cut corners on the power of the internal pumps, leaving them with insufficient head.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @alfapat@ubert767 Thanks , no wonder I get too much of a temp drop , mine is 200L , too much mixing .
Ours is 100 litre and it's been piped for maximum distortion/mixing with an X shape between the pipes. Ridiculous. We're planning to get ours repiped in late spring.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
In order to answer my doubts about my buffer vessel I built a cheapish temperature logging system from a Raspberry Pi and five DS18B20 temperature sensors(one sensor on each buffer port and one measuring O.A.T.) This allowed me to see the differentials across the flow and return ports, to check the distortion in the buffer vessel and record the system cycling intervals.
Posted by: @alfapatIam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
It provides extra system volume which is useful for defrost but may well not be necessary. Have you any idea what volume of water you have in your secondary circuit.
One of the ports at top and the other at bottom to ensure it's actually both heated by the water passing through and engaged in the flow. Otherwise you could end up with most of the water in the volumiser just being 'bypassed'
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 50 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
it does, but the schedule says a 12kW in Im not too muc...
By JamesPa , 39 seconds ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 36 minutes ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 3 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 5 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 6 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 17 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 20 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 21 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 23 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 6 hours ago
-
SolarPV tables / online calculator
By MichelleC 13 hours ago
-
By Toodles 2 days ago