Heat Pump starting current
There's been a bit of discussion e.g. here and here, and very recently here originally, I think, introduced by @transparent about expecting high starting currents on heat pumps as pressures build up to operating pressure.
The interest on the forum in HP starting current particularly relates to correctly sizing an inverter if the HP is running off backup battery storage (though for a grid-tied inverter supplying the HP/house in parallel with grid power, any current beyond the capacity of an inverter is then supplied by the grid)
Looking at the manual for our NIBE F2040 HP, it has a specified maximum operating current of 23A (5.5kW) and a starting current of 5A. So it looks like high starting currents may be characteristic of some HPs but not others.
Out of interest, I took 1-second readings from a current clamp on our HP starting up today, and it does appear to be a well-controlled rise:
this corresponds with this pressure and flow temperature rise:
In our discussions over @ivanhoew 's system (Harnitek 12 kw ashp), graphs of operating current are at a useful sample rate (2 per minute) there does not seem to be any sign of turn-on surges, so I'm wondering if I'm either looking at the wrong thing, or there can be very different behaviour between heat pumps, which will need to be understood when considering maximum current handling, particularly for inverters.
Interested to hear what others experience and understanding is ..
End 1980's terrace in Southern England
NIBE 12kW air source heat pump
2 solar water panels
1 x Ohme ePod
1 x VW ID Buzz
Here is the last 24 hours for my heat pump with amps added to the plot. Note that I do not have solar or batteries or inverters, just mains electricity:
But the steepness is very dependent on zoom level. I can flatten the apparent gradient by zooming in to an hour (either side of the bigger spike just before 2200). The actual gradient is of course the same, but it looks far less:
Amps look OK, what is more interesting to me is why, after running in steady state at the start of the hour, it suddenly starts cycling for no obvious reason.
Here's the 11th Jan with -4 degrees OAT in the early hours:
Looks rather alarming, however if I zoom in to one of the worst hours:
Again, the amps, though high (max 23-24 amps, but it was very cold, COP was terrible, and it needs those amps to get sufficient output), aren't spikey. The cycle starting at 0610 is a defrost cycle, and it interesting to see how long it affects output: 20 minutes. Not so good.
There is absolutely no doubt in my mind that defrost cycles are a major problem. Others have asked the question before, but I don't think I've ever seen an answer: how do our friends in Europe with colder climates deal with this? Have they found a fix, or do they just put up with it?
Midea 14kW (for now...) ASHP heating both building and DHW
If your talking about inrush current I suspect non of our monitoring systems are capable of capturing the resolution needed for that?
“Anything worth doing, is worth doing right.”
Posted by: @irmartiniIf your talking about inrush current I suspect non of our monitoring systems are capable of capturing the resolution needed for that?
That is indeed possible, but if there is an inrush it must be very short (and so does it really matter?). I sample every minute, @ivanhoew samples every 30 seconds, and @s_gatorator every second. Also it is surprising that a sample never happens during an inrush (if they do occur, but we always miss them).
What we appear to have here is three different makes of heat pumps, none of which show start up surges in current. I'm not sure that is that surprising, isn't that what modern inverter driven pumps are supposed to do?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayThat is indeed possible, but if there is an inrush it must be very short (and so does it really matter?)
Just because it is short doesn't mean it doesn't matter!
Running on mains it probably doesn't matter, but if your running on an inverter supplied by a battery only maybe it would?
I'm not knowledgeable enough to know either way, I'm just aware we might not be seeing the whole picture.
If these modern heatpump motors don't have any inrush then great 😀 it doesn't matter.
“Anything worth doing, is worth doing right.”
Posted by: @irmartiniI'm not knowledgeable enough to know either way, I'm just aware we might not be seeing the whole picture.
I agree, always be sceptical, always question whether what you think you see is what is actually going on. I think another pertinent question here is how exactly does an inrush current do harm? I can see that sustained overloads might do harm, but a short inrush? Isn't that what happens every time internal combustion car starts its engine using a battery?
Edit @transparent may have something to add here.
Midea 14kW (for now...) ASHP heating both building and DHW
I do try and question everything and have learn't a lot from forums like this by doing that, however I often don't have the knowledge to ask or know to ask the right questions.
A Cars battery is designed for starting a a cars engine, it has a CCA rating in the hundreds of Amps and so can provide that very high current for a short periods.
I believe if your system what ever it is is not capable of providing the current being drawn even for a very short period the consequence is the voltage drops and this can effect if devices start-up cleanly or can negatively effect electrically sensitive devices that are already running.
A quick bit of googling does seem to suggest that modern ASHP have soft starts and so don't have large inrush currents but that is generic info not specific to any makes and models.
“Anything worth doing, is worth doing right.”
Posted by: @irmartiniI do try and question everything and have learn't a lot from forums like this by doing that, however I often don't have the knowledge to ask or know to ask the right questions.
Someone after my own heart. We do try to stick to the 'there is no such thing as a stupid question, the stupid thing is not to ask' way of doing things here.
I agree car batteries have high CCA ratings and so are suited to their tasks. What I am hoping is that @transparent (the source of much light on these matters) can tell us a bit more about the actual damage that occurs from high start up currents. Is there a scrapyard somewhere full of dead ASHPs killed off by high start up currents? Or is it more of a theoretical risk (like for example Legionella)?
I agree most modern heat pumps advertise themselves as being soft start devices. But, as you say, there may be exceptions (and we can be pretty sure they won't advertise the fact!).
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayWhat I am hoping is that @transparent (the source of much light on these matters) can tell us a bit more about the actual damage that occurs from high start up currents. Is there a scrapyard somewhere full of dead ASHPs killed off by high start up currents?
🤣
No.
I'm raising the issue due to the problems it creates for the grid...
or for ensuring that an inverter can deliver a sufficiently high current to allow a heat-pump to start.
There's no 'damage' caused to the heat-pump.
It will quite happily take whatever current it needs.
From the viewpoint of the grid, the major headache for DNOs is a demand-surge that occurs when
- they re-energise a sub-station following an outage
- ASHPs in a locality all experience freezing fog and switch on their defrost cycle
How do I know that?
- because a senior DNO engineer told me
- because I can see the switch-on surges when I look at sub-station current data
That graph shows averaged data.
The actual switch-on surge is much higher than shown here.
Save energy... recycle electrons!
Posted by: @cathoderayAgain, the amps, though high (max 23-24 amps, but it was very cold, COP was terrible, and it needs those amps to get sufficient output), aren't spikey. The cycle starting at 0610 is a defrost cycle, and it interesting to see how long it affects output: 20 minutes. Not so good.
There is absolutely no doubt in my mind that defrost cycles are a major problem. Others have asked the question before, but I don't think I've ever seen an answer: how do our friends in Europe with colder climates deal with this? Have they found a fix, or do they just put up with it?
Hi @cathodeRay , aren't all of the cycles in your chart defrost cycles? The clue I'm seeing is in the OAT graph, which has a small spike just after the compressor stops, presumably due to your outside temperature sensor being near the external unit and it getting some heat from the warm air at the end of the defrost cycle when the fan restarts. I have the same think on ours.
If the temperatures are lower, as in Europe, the moisture freezes out of the air and it looks like frosting does not occur below -7C or above 5C (quick internet search). Otherwise, here, I agree, it's a problem.
End 1980's terrace in Southern England
NIBE 12kW air source heat pump
2 solar water panels
1 x Ohme ePod
1 x VW ID Buzz
-
Weather compensation- why you should use it
2 days ago
-
Where has Watson gone?
2 months ago
-
First time wall mounting an ASHP
2 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
Rodents! A word of warning for heat pump owners
3 months ago
- 26 Forums
- 2,391 Topics
- 54.2 K Posts
- 134 Online
- 6,074 Members
Join Us!
Worth Watching
Latest Posts
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally can I just check the obvious- the kWh usage you'...
By benson , 45 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
The Solis has an export limitation feature. This was ac...
By Batpred , 2 hours ago
-
Hot water heating in parallel with space heating
One of the downsides of most ASHP installations (compar...
By Temperature_Gradient , 3 hours ago
-
RE: Heat pump not reaching flow temperature
@johnd, what you’re experiencing is common with air sou...
By Mars , 4 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 4 hours ago
-
RE: Air source heat pump circuit not operational
Welcome to the forums. If the thermostat shows it’s c...
By Mars , 4 hours ago
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
From what you describe, it sounds like you’ve done a so...
By Mars , 5 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Of course it is not helpful to frogstar fan club member...
By Batpred , 6 hours ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 7 hours ago
-
@steelbadger, I’ve pretty much decided now that there’s...
By Majordennisbloodnok , 8 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
That makes plenty of sense. Perhaps more importantly, O...
By Majordennisbloodnok , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
It does but it almost all applies to boiler systems and...
By JamesPa , 12 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
So theres a problem for starters. This means that the ...
By JamesPa , 12 hours ago
-
RE: Insulating a pitched roof with kingspan, has anyone done it?
Thank you everyone for all of the information, it looks...
By TRBob , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@transparent Yep, they didn’t even mention it. When ...
By Papahuhu , 1 day ago
-
RE: Setback savings - fact or fiction?
They are lovely, and I feel lucky to live in one, but t...
By cathodeRay , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Worth adding that, for this tariff, the Octopus app has...
By Batpred , 1 day ago
-
RE: APP for remote Daikin ASHP Operation
Thanks, @newhouse87. Understood. I was only asking on...
By Majordennisbloodnok , 1 day ago
-
@mike-patrick A propos, I think my heat pump generates ...
By dr_dongle , 1 day ago