@derek-m thanks Derek
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I think what you have posted/said is very good.
The Pron-N will produce 6KW @ -5.2˚C with house temp of 21˚C (that's with a buffer as well)
The property this Pro-N is installed in @ -3˚C has a heat loss of 6.53kW. Temperature this morning outside was -6˚C, house was @ 21.1˚C flow temp was 32.7˚C
Did they mention air changes at all as these are normally over estimated. They could have also done an airtightness test to get a more accurate heat loss calc.
The Pro-N unit would have been fine especially as Helen doesn't like the house warm and only wants 19˚C. For the number of days @ -3˚C with the possibility to add a layer (though unlikely required) vs the increased running costs the rest of the time, with the larger unit in milder weather and cycling.
Not that I'm particularly any expert when it comes to ASHP, still learning.
Posted by: @bontwoodyif you have time could you please look at my reply in the post above and give me your opinions. Either I've got this totally wrong or they have or they are being deceitful. Thank you Mark
I agree with most of your comments and I especially agree the installer is either making things up or is really incompetent. On the sizing issue the 16kW model seems too big on the info you have. However, I'm not sure the smaller one would be enough, even with the numbers you quote. With the extension, the smaller unit seems borderline. Last night my ASHP was defrosting regularly even at -4 deg and that (IMO) cuts output 15-20%. A borderline ASHP would not have been able to heat my house last night. And don't forget about DHW; that can cause the heating to be off for quite a long time (30-60 mins) depending on usage.
I know your neighbour likes the house cool but if she has received any funding the design will have to comply with MCS, which won't allow for 18 deg living areas.
I think the installer has concluded the smaller unit is too small and just gone for the next size they supply/have in stock rather than use a different manufacturer and are now trying to wriggle out of it. Maybe they should have gone for a different manufacturer or turned the job down.
@deano Thanks Andy. Nice to have you in the forum. It’s really useful to have some real world data I can include in my response to disprove his assertion.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@kev-m Thanks Kev. I take your point about the sizing of the smaller unit. I am reassured however by the fact that Helen at the last minute decided to fit underfloor heating in her lounge area which should allow lower flow temperature and access the upper end of the output range. She also has mentioned a desire to have a wood burning stove in the lounge so I doubt she will suffer In a cold winter 😂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody can't see anything wrong with your reasoning. As per @kev-m, there is potentially a case that the smaller unit isn't quite enough - but in that situation the installer should have initiated a conversation about whether supplementary heating was going to be available for the worst case days (sounds like it is), or whether there was tolerance for running cooler (again sounds like there is) . At the very least , they should have proposed a design using a different manufacturer's unit, one that has a "medium sized" unit in the range, that better meets the specs needed.
The jump to the "large", just because "that's who they use" is what makes this not an acceptable piece of practice to me. But I've posted about this before - its common for two businesses to have preferred supplier relationships which are commercially favourable to both, and that negatively affects "what is right technically" decision making . So , making an informed guess that installer's sole preferred supplier is Acond, then I would assume they would have just gone with that because cheaper and easier (for them). Moving to a different brand would have cost them time and money, they might not be trained on any other brand, they might have had to back out of the project.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
they also fit Ariston and Mastertherm, Mastertherm would have suited much better with a Boxair 26l which is up to heat loss of 8.5kWh
@iancalderbank Thanks Ian, I totally agree with your assessment. It would, in hindsight, been a lot easier if she had not mentioned the possible extension and then if it went ahead heated it with an air to air heat pump (if necessary). I have one in my kitchen, its great 🙂 Ive responded now to Thermal Earth so the ball is in their court. At the minimum my intervention has caused them to make contact with Helen and arrange a handover date!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Just an update. Following my response, the company have stated that the design flow temperature is 45C which puts the output smack in the middle of my ranges and proves their statement of outputs at -3C demonstrably wrong. They are coming for a site visit/handover on Monday.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
The moment of truth approacheth then!
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@editor @toodles @deano @iancalderbank @derek-m @kev-m
So we had the meeting today with an Andrew Lloyd and whilst we didnt agree on everything it was a useful meeting. Access to the heat pump settings via a local website page was achieved and changes made to the settings to allow a reduction in running costs. Agreement was made to sort out the snagging issues with insulation etc.
Where we couldnt agree was over the size of the heat pump with Andrew insisting the the larger model would be able to successfully modulate low enough to avoid cycling in the shoulder seasons. In the end I asked for a written commitment from them to this effect and what they would do about it if it did. We shall see what I get!
Out of interest Andrew insisted that that it was the norm for heatpumps to heat DHW all through the day using a setpoint. say a drop of 5C. This isnt my experience, what is the experience out there please? I would have thought this arrangement would increase thermal losses from the cylinder and be more expensive to implement due to always heating water at the highest temperature
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Sounds like an OK meeting overall.
I'd be surprised if the larger pump would modulate that low, the small one (which I have) wont go any lower than 480w and 2200w of heat on a mild day, eg today. Flow temp 28˚C
Mine was setup to constantly heat hot water 🤣
DHW run from the lowest possible temp is far more efficient. I have mine set 12 hours apart, reheats overnight after the dishwasher and washing machine have used any hot water if they're going to.
On the clock icon top left, then down the bottom, select DHW TimeTable, dont forget it runs in CET so it's an hour out.
- 26 Forums
- 2,149 Topics
- 47 K Posts
- 27 Online
- 5,667 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
Something isn't right here, you don't design ufh to wor...
By JamesPa , 1 hour ago
-
RE: Electricity price predictions
the post code lottery is only one thing that is very wr...
By Judith , 2 hours ago
-
RE: How Do I Know When the Hot Water Has Run Out?
@grahamf Personally I would consider bypassing one of t...
By JamesPa , 5 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
No I'm not mining anything @drei but I am doing R&...
By Transparent , 5 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
Yes, the 'global warming potential' GWP of R32 is quote...
By Temperature_Gradient , 6 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Wasps caused frequent tripping of my lighting circuit a...
By JamesPa , 6 hours ago
-
This is one of my biggest bugbears these days, how AI d...
By cathodeRay , 7 hours ago
-
RE: Ecodan & MelCloud scheduling
Yes, the 2 are separate. To add to the complex desig...
By HCas , 2 days ago
-
I should clarify that the FoxESS web interface is not l...
By Old_Scientist , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
@robs Hi Rob, At the end of a note to Mitsu UK, thank...
By DavidAlgarve , 3 days ago
-
RE: Why so many sigenergi installer recommendations?
@adamk Tesla is a great option, it’s also one we instal...
By SAEnergy , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As a potential heat pump customer, it would be good to ...
By Temperature_Gradient , 4 days ago
-
RE: Octopus replacing the fixed 15p/kWh export rate with a market tracking one
@trbob I have just extracted the details for Agile Expo...
By Toodles , 4 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
The Ultimate Guide to Heat Pumps is less than a month a...
By Mars , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor Hi Mars, We have just installed a Grant Aerona...
By GrahamF , 5 days ago
-
RE: Sanity check please. Battery storage and inverter sizing.
There are MCS guidelines about how close to the edge/ri...
By Old_Scientist , 5 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I estimated our usage on the following basis. The mos...
By Old_Scientist , 5 days ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 6 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 1 week ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 1 week ago