Heat Pump SCOPs – The Truth Might Not Be What You Think
When it comes to ASHP efficiency, there’s often a lot of discussion and misunderstanding. SCOP (Seasonal Coefficient of Performance) is a key measure of efficiency, but what does it really tell us, and how can we interpret it? After analysing data from the top 20 heat pumps on heatpumpmonitor.org – all with SCOPs above 4.0 over the past 365 days – I’ve uncovered some insights that might surprise you.
What the Data Reveals (At Time of Writing)
- Air Source Dominates: Of the top 20 heat pumps, 19 are air source, and only one is ground source.
- System Volume is Often Overlooked: Surprisingly, 75% of users don’t calculate or record their system volume. For those that do, systems with 15 litres per kW of peak capacity or more perform best. The top-performing system has 16 l/kW. However, going far beyond 15 l/kW offers diminishing returns, and there isn’t enough data to confirm its benefits.
- Manufacturer Diversity: The top-performing models come from a range of manufacturers, including Viessmann, Nibe, Vaillant, Grant, Samsung, Mitsubishi and Acond. This highlights that system design is often more critical than the brand.
- Refrigerants Don’t Make a Big Difference: Among the top six ASHPs, there is an even split between those using R290 and R32 refrigerants, suggesting no significant efficiency advantage to either.
- Single-Zone Systems Rule: Every system achieving a SCOP above 4.0 is a single-zone setup. Multi-zone systems seem to struggle to match this level of efficiency.
- Flow Temperatures are Key: Systems with a maximum flow temperature of 45°C or lower dominate the top-performing list. Higher flow temperatures tend to drag down efficiency.
- Modest DHW Settings Win: The top six ASHPs have domestic hot water (DHW) set to an average temperature of 45°C, reinforcing the importance of keeping DHW temperatures modest for better efficiency.
- Building Efficiency is Less Relevant: Interestingly, building efficiency (measured in W/m2) varies wildly among the top systems, from 19 to 76 W/m2. This suggests that SCOP is influenced more by system design than the property’s insulation or efficiency level.
- Supplementary Technologies Enhance Results: Over half of the top 20 systems either don’t heat DHW or use supplementary technologies such as hybrid boilers, photovoltaic (PV) panels or solar thermal systems to improve performance.
Notable Features in Top Systems
- Buffer Vessels: These are present in many high-performing systems.
- 10mm Microbore Pipework: Often considered suboptimal, this pipework appears in some top-performing setups, proving that careful system design can overcome perceived limitations.
- Thermostatic Radiator Valves (TRVs): Despite some reservations, TRVs are used in many systems, likely in specific zones like bedrooms.
Key Takeaways
From this analysis, a few clear lessons emerge:
- Aim for 15+ l/kW System Volume: This seems to be a reasonable rule of thumb for optimising efficiency.
- Focus on System Design: The manufacturer matters less than a well-designed, balanced and commissioned system.
- Refrigerant Choice Isn’t Critical: Both R290 and R32 perform equally well in top systems.
- Stick to Single-Zone Systems: Multi-zone setups don’t achieve the same efficiency levels.
- TRVs Are Acceptable: While they may reduce efficiency slightly, TRVs can work well if carefully implemented, likely in specific areas like bedrooms.
- Keep Flow Temperatures Below 45°C: Lower flow temperatures are crucial for high SCOPs.
- Lower DHW Temperatures: Reducing DHW temperatures has a substantial positive impact on system efficiency.
- Don’t Stress About Building Age or Efficiency: A correctly sized heat pump can deliver excellent results in properties with varying levels of efficiency.
- Supplementary Technologies Help: PV, solar thermal, and hybrid systems can boost overall system performance.
Some super interesting findings. Not surprised about heating DW to 45C being the most efficient way to go. That's what we set ours to.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Thanks Mars I am getting 3.7 Scop with an oversized Mitsubishi 8.5 kw heat pump . Still
Trying different settings to try and improve it. Have installed open energy monitoring and
It’s under Dalkieth. Set hot water 47c . Does anyone know if switching down pump speed helps presently 25.61 l/m
Cheers Andrew Scotland
Does anyone know if switching down pump speed helps presently 25.61 l/m
Pump speed needs to be sufficient to carry away the energy, any less wont do, any more is wasting energy.
The energy carried away is flow rate (l/s) * specific heat capacity of the transfer medium (water or glycol as appropriate) * deltaT at the heat pump (normally designed for 5).
Assuming water and 5C DT thats 25.61/60*4200*5 =8.9kW, so just abut right for an 8.5kW pump!
If the heat pump is oversized then there may be the potential to reduce the water pump speed. Some heat pumps modulate pump speed according to energy demand. If yours does or can then thats an option. Otherwise you could try turning it down on the water pump itself but the heat pump may complain. The energy saving from turning down the water pump is small however so this isnt likely to make a massive difference.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have tried my 8.5kw Ecodan at various pump speeds its currently at pump speed 2 that gives 14L/min, the recommended flow rate for 8.5 Ecodan is 15.4L/min, to achieve the optimum dT of 8, not 5 that you see quoted.
Using the mass flow calc James quoted you get to 8.6kw at dT8 so that makes sense as well.
The advantage of using a lower flow rate is that the Ecodan doesn't have its own internal pump so ours is in the airing cupboard so the slower the pump the less noise it makes too
Two other things that greatly effect SCOP but havent been mentioned are the climate where you are living and what you deem to be a comfortable internal temperature.
Someone living in London who is happy with a 19C indoor tempearture will have a much better SCOP than someone with exactly the same system living in the North of Scotland who likes a 22C room.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @david-stanford
Aim for 15+ l/kW System Volume: This seems to be a reasonable rule of thumb for optimising efficiency.
Can you explain the mechanism for this effect? Could it just be coincidental rather than causal? System volume may prevent short cycling, but there are other ways of achieving that.
Yes I have room temperature 20.5 and live in central belt . Perhaps I was overthinking scop it’s gone back to daily cop of 4.5 . Will try lower pump speed as heat pump comes off and on 2 or 3 times an hour
thanks for commenting
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 25 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Rodents! A word of warning for heat pump owners
@tim441 Or as they didn’t quite say in the space travel...
By Toodles , 4 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
Update: I have found that the contractor had changed on...
By DavidAlgarve , 16 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor Hi Mars, We have just installed a Grant Aerona...
By GrahamF , 16 hours ago
-
RE: Sanity check please. Battery storage and inverter sizing.
There are MCS guidelines about how close to the edge/ri...
By Old_Scientist , 19 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I estimated our usage on the following basis. The mos...
By Old_Scientist , 21 hours ago
-
RE: Why so many sigenergi installer recommendations?
It’s a really simple answer, GivEnergy. Installers ...
By SAEnergy , 1 day ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 2 days ago
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 2 days ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 3 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 3 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 4 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 5 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 6 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 6 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 7 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 1 week ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 week ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 week ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago