Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hi Ann,
Whilst you collect some data, it may be useful if I explain what it may be possible to do to make your system more efficient.
ASHP's extract energy from the outside air, the warmer the air then the more energy is available, so the heat pump does not have to work so hard. Obviously, the lower the outside air temperature, the harder the heat pump has to work.
The larger the home and/or the greater the heat loss, then the harder the heat pump has to work.
ASHP's are more efficient when they are heating the central heating water to low temperatures, the higher the water flow temperature the harder the heat pump has to work.
Unfortunately, it is not just a matter of reducing the water flow temperature, because you will get to a point where there is insufficient heat energy being emitted from the radiators and/or UFH to meet the heat demand, the indoor air temperature would then start to fall.
To maintain a reasonably constant indoor temperature, it is necessary for the water flow temperature to be varied to meet the heat demand.
The best way of achieving this balance is by using weather compensation to vary the water flow temperature as the ambient air temperature varies.
If there is anything that you are not certain about then please ask.
Posted by: @anng@derek-m when you say read meter do you mean the actual electric meter rather than the smart meter which reads ever half hour?
Hi Ann,
Sorry I forgot that you have a smart meter. The totaled reading on both should be the same, so the reading from the Smart meter is fine, in fact 30 minute readings would possibly be better.
@derek-m The LG engineer who came yesterday set the water temp to 50 as the AI setting wasn’t suitable at the moment (he said). We really had to get heating up to at least 20 as when he arrived the temp was not getting above 16.5. I’m just conscious that it is costing us a fortune as we seem to be eating kWh at least £20 per day!!! He also said that the 16kw LG was working exactly as it should with all the readings and data he took. He is questioning the thermostat and rads he is going to white a report in the next few days
Posted by: @anng@derek-m The LG engineer who came yesterday set the water temp to 50 as the AI setting wasn’t suitable at the moment (he said). We really had to get heating up to at least 20 as when he arrived the temp was not getting above 16.5. I’m just conscious that it is costing us a fortune as we seem to be eating kWh at least £20 per day!!! He also said that the 16kw LG was working exactly as it should with all the readings and data he took. He is questioning the thermostat and rads he is going to white a report in the next few days
Hi Ann,
Because of the lower water flow temperature preferred by heat pumps, it can take quite some time to warm up a home from cold, and like a car accelerating to pick up speed, your heat pump will use more energy until the desired temperature is reached. £20 a day at 26p per kWh would equate to approximately 76 kWh, which would seem rather high for a property of the size of yours. By collecting the necessary data it should hopefully start to highlight some possible problem areas.
Other than say that weather compensation was not suitable, did he give any reason why?
Hi Derek, I’ve been trying to send data but the links don’t seem to work for me. I’ve taken pictures of the last 5 days of data. I can break down the half our readings if that helps.
@batalto no we have had to change our thermostat to 19 degrees as when we set it to 21 just to get some heat it just about managed to get to 20…but only using loads of kwh and costing a fortune..we can’t cope with the ongoing cost it’s frightening!!! The rads when we set the thermostat to 23 do get hot but it takes such a long time …most of the day
Posted by: @anngHi Derek, I’ve been trying to send data but the links don’t seem to work for me. I’ve taken pictures of the last 5 days of data. I can break down the half our readings if that helps.
Hi Ann,
Whatever information that you can provide may help identify the root cause of the problem. I too have sometimes had difficulty attaching files to the forum, I thought it may be something to do with my old, tired laptop. I will make Mars aware that there may be some sort of problem.
If you cannot post data to the website, you could try sending it directly to my e-mail address.
derek_marsh_aicss@yahoo.com
I look forward to hearing from you.
@anng the radiators aren't getting hot at all? Are some of them hot? Can you check to see? You might need to balance your radiators
- 27 Forums
- 2,745 Topics
- 64.5 K Posts
- 108 Online
- 7,149 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
@davidb I can’t help you with contacts at Vaillant unfo...
By Mars , 53 minutes ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@Ian-S, I actually think this is a pretty reasonable pl...
By Mars , 56 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@toodles I invested on Miele a pair of frodge frozor wh...
By AgentGeorge , 5 hours ago
-
RE: Flushing system, cleaning and inhibitor
Flush and fill all complete. Octopus kindly gave us a...
By Old_Scientist , 5 hours ago
-
RE: Wood burner with ASHP - direct air?
For what it's worth I installed a wood burner in this o...
By BlizzardGreen , 6 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
I think I saw a diagram for an exhaust air dhw tank wit...
By JamesPa , 1 day ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks, however that's an answer to a subtly different ...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Such elegant symmetry. look at my lumpy bag of...
By Papahuhu , 4 days ago
-
RE: PV and battery long payback - sense check query
Quite probably not, but you can get a 32A relay and a S...
By JamesPa , 4 days ago
-
I don't notice mine defrosting, and most of the time Im...
By JamesPa , 5 days ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 6 days ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 6 days ago