Hi Ann,
Whilst you collect some data, it may be useful if I explain what it may be possible to do to make your system more efficient.
ASHP's extract energy from the outside air, the warmer the air then the more energy is available, so the heat pump does not have to work so hard. Obviously, the lower the outside air temperature, the harder the heat pump has to work.
The larger the home and/or the greater the heat loss, then the harder the heat pump has to work.
ASHP's are more efficient when they are heating the central heating water to low temperatures, the higher the water flow temperature the harder the heat pump has to work.
Unfortunately, it is not just a matter of reducing the water flow temperature, because you will get to a point where there is insufficient heat energy being emitted from the radiators and/or UFH to meet the heat demand, the indoor air temperature would then start to fall.
To maintain a reasonably constant indoor temperature, it is necessary for the water flow temperature to be varied to meet the heat demand.
The best way of achieving this balance is by using weather compensation to vary the water flow temperature as the ambient air temperature varies.
If there is anything that you are not certain about then please ask.
Posted by: @anng@derek-m when you say read meter do you mean the actual electric meter rather than the smart meter which reads ever half hour?
Hi Ann,
Sorry I forgot that you have a smart meter. The totaled reading on both should be the same, so the reading from the Smart meter is fine, in fact 30 minute readings would possibly be better.
@derek-m The LG engineer who came yesterday set the water temp to 50 as the AI setting wasn’t suitable at the moment (he said). We really had to get heating up to at least 20 as when he arrived the temp was not getting above 16.5. I’m just conscious that it is costing us a fortune as we seem to be eating kWh at least £20 per day!!! He also said that the 16kw LG was working exactly as it should with all the readings and data he took. He is questioning the thermostat and rads he is going to white a report in the next few days
Posted by: @anng@derek-m The LG engineer who came yesterday set the water temp to 50 as the AI setting wasn’t suitable at the moment (he said). We really had to get heating up to at least 20 as when he arrived the temp was not getting above 16.5. I’m just conscious that it is costing us a fortune as we seem to be eating kWh at least £20 per day!!! He also said that the 16kw LG was working exactly as it should with all the readings and data he took. He is questioning the thermostat and rads he is going to white a report in the next few days
Hi Ann,
Because of the lower water flow temperature preferred by heat pumps, it can take quite some time to warm up a home from cold, and like a car accelerating to pick up speed, your heat pump will use more energy until the desired temperature is reached. £20 a day at 26p per kWh would equate to approximately 76 kWh, which would seem rather high for a property of the size of yours. By collecting the necessary data it should hopefully start to highlight some possible problem areas.
Other than say that weather compensation was not suitable, did he give any reason why?
Hi Derek, I’ve been trying to send data but the links don’t seem to work for me. I’ve taken pictures of the last 5 days of data. I can break down the half our readings if that helps.
@batalto no we have had to change our thermostat to 19 degrees as when we set it to 21 just to get some heat it just about managed to get to 20…but only using loads of kwh and costing a fortune..we can’t cope with the ongoing cost it’s frightening!!! The rads when we set the thermostat to 23 do get hot but it takes such a long time …most of the day
Posted by: @anngHi Derek, I’ve been trying to send data but the links don’t seem to work for me. I’ve taken pictures of the last 5 days of data. I can break down the half our readings if that helps.
Hi Ann,
Whatever information that you can provide may help identify the root cause of the problem. I too have sometimes had difficulty attaching files to the forum, I thought it may be something to do with my old, tired laptop. I will make Mars aware that there may be some sort of problem.
If you cannot post data to the website, you could try sending it directly to my e-mail address.
derek_marsh_aicss@yahoo.com
I look forward to hearing from you.
@anng the radiators aren't getting hot at all? Are some of them hot? Can you check to see? You might need to balance your radiators
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 376 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Great to hear! I just figured this out a day or tw...
By anotherdaveuk , 2 minutes ago
-
RE: Setback savings - fact or fiction?
@robssunandair That is a lot of defrosting! Perhaps we ...
By Toodles , 5 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
No. That's uncommon. It goes back to the days when ho...
By Transparent , 10 minutes ago
-
RE: Fan is clipping ice build up from the front of unit.
@editor Ta Yes mine is missing, I hope intentional...
By Papahuhu , 36 minutes ago
-
RE: Running from backup generaor in powercut?
Our DNO has updated our restore time to 21:00, after th...
By Mars , 44 minutes ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
This would help, electric showers are very power hungry...
By Grantmethestrength , 1 hour ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 5 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 1 day ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 1 day ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago