Hi Ann,
Whilst you collect some data, it may be useful if I explain what it may be possible to do to make your system more efficient.
ASHP's extract energy from the outside air, the warmer the air then the more energy is available, so the heat pump does not have to work so hard. Obviously, the lower the outside air temperature, the harder the heat pump has to work.
The larger the home and/or the greater the heat loss, then the harder the heat pump has to work.
ASHP's are more efficient when they are heating the central heating water to low temperatures, the higher the water flow temperature the harder the heat pump has to work.
Unfortunately, it is not just a matter of reducing the water flow temperature, because you will get to a point where there is insufficient heat energy being emitted from the radiators and/or UFH to meet the heat demand, the indoor air temperature would then start to fall.
To maintain a reasonably constant indoor temperature, it is necessary for the water flow temperature to be varied to meet the heat demand.
The best way of achieving this balance is by using weather compensation to vary the water flow temperature as the ambient air temperature varies.
If there is anything that you are not certain about then please ask.
Posted by: @anng@derek-m when you say read meter do you mean the actual electric meter rather than the smart meter which reads ever half hour?
Hi Ann,
Sorry I forgot that you have a smart meter. The totaled reading on both should be the same, so the reading from the Smart meter is fine, in fact 30 minute readings would possibly be better.
@derek-m The LG engineer who came yesterday set the water temp to 50 as the AI setting wasn’t suitable at the moment (he said). We really had to get heating up to at least 20 as when he arrived the temp was not getting above 16.5. I’m just conscious that it is costing us a fortune as we seem to be eating kWh at least £20 per day!!! He also said that the 16kw LG was working exactly as it should with all the readings and data he took. He is questioning the thermostat and rads he is going to white a report in the next few days
Posted by: @anng@derek-m The LG engineer who came yesterday set the water temp to 50 as the AI setting wasn’t suitable at the moment (he said). We really had to get heating up to at least 20 as when he arrived the temp was not getting above 16.5. I’m just conscious that it is costing us a fortune as we seem to be eating kWh at least £20 per day!!! He also said that the 16kw LG was working exactly as it should with all the readings and data he took. He is questioning the thermostat and rads he is going to white a report in the next few days
Hi Ann,
Because of the lower water flow temperature preferred by heat pumps, it can take quite some time to warm up a home from cold, and like a car accelerating to pick up speed, your heat pump will use more energy until the desired temperature is reached. £20 a day at 26p per kWh would equate to approximately 76 kWh, which would seem rather high for a property of the size of yours. By collecting the necessary data it should hopefully start to highlight some possible problem areas.
Other than say that weather compensation was not suitable, did he give any reason why?
Hi Derek, I’ve been trying to send data but the links don’t seem to work for me. I’ve taken pictures of the last 5 days of data. I can break down the half our readings if that helps.
@batalto no we have had to change our thermostat to 19 degrees as when we set it to 21 just to get some heat it just about managed to get to 20…but only using loads of kwh and costing a fortune..we can’t cope with the ongoing cost it’s frightening!!! The rads when we set the thermostat to 23 do get hot but it takes such a long time …most of the day
Posted by: @anngHi Derek, I’ve been trying to send data but the links don’t seem to work for me. I’ve taken pictures of the last 5 days of data. I can break down the half our readings if that helps.
Hi Ann,
Whatever information that you can provide may help identify the root cause of the problem. I too have sometimes had difficulty attaching files to the forum, I thought it may be something to do with my old, tired laptop. I will make Mars aware that there may be some sort of problem.
If you cannot post data to the website, you could try sending it directly to my e-mail address.
derek_marsh_aicss@yahoo.com
I look forward to hearing from you.
@anng the radiators aren't getting hot at all? Are some of them hot? Can you check to see? You might need to balance your radiators
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 16 Online
- 5,662 Members
Podcast Picks
Latest Posts
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 7 hours ago
-
@ashp-bobba interesting insights. We also chatted after...
By Mars , 8 hours ago
-
RE: Why so many sigenergi installer recommendations?
I’ve not come across this brand, but then again I don’t...
By Mars , 8 hours ago
-
Sanity check please. Battery storage and inverter sizing.
I had one installer essentially wanting to install a ti...
By AdamK , 18 hours ago
-
RE: Rodents! A word of warning for heat pump owners
The gaps and holes have reduced on heat pumps over the ...
By dgclimatecontrol , 23 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: EGP01 Manufacturer: Samsung Model: 8K...
By EGP01 , 1 day ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 1 day ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 1 day ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 2 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 3 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 4 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 4 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 5 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 5 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 6 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 week ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 week ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago
Members Online
No online members at the moment