Flowmeter and glycol
We have just had our Valiant ASHP serviced and the report has come back that we only have plain water in the circuit and we lack a flow meter.
Do we need both glycol and a flow meter (if so our bloody useless installers have mucked up yet again) if not why are they recommended by the servicing team?
At around £800 it more bloody remedial work on this installation.
Cheers
Mark
Posted by: @witchcraftWe have just had our Valiant ASHP serviced and the report has come back that we only have plain water in the circuit and we lack a flow meter.
Do we need both glycol and a flow meter (if so our bloody useless installers have mucked up yet again) if not why are they recommended by the servicing team?
At around £800 it more bloody remedial work on this installation.
Cheers
Mark
You should not need an additional flow meter. The ASHP should have a flow rate sensor which is enough for normal use. This will throw an error code if the flow is too low. I have an external flow meter but this is for MMSP monitoring. You should ask the engineer why a flow meter is needed? Maybe they are just fishing for work?
The system would normally be filled with a glycol mix on commissioning. If not, anti freeze valves are an alternative. If you have neither then there is a risk that if/when there is a power cut and it's very cold the ASHP could freeze up and be damaged. Unfortunately it's quite an expensive job to refill with glycol.
Posted by: @witchcraftWe have just had our Valiant ASHP serviced and the report has come back that we only have plain water in the circuit and we lack a flow meter.
Do we need both glycol and a flow meter (if so our bloody useless installers have mucked up yet again) if not why are they recommended by the servicing team?
At around £800 it more bloody remedial work on this installation.
Cheers
Mark
I would suggest that you ask your installer to add the glycol that they should have added during the installation. If they refuse then make a complaint to MCS and any other body who have supposedly accredited their service.
Posted by: @witchcraft@derek-m But these installers are the lovely mob I took to court and they then went bust
They should have indemnity insurance against which you should be able to claim.
@witchcraft, your MCS installers will have been insured by HEIS or another body. It’s a requirement and it’ll be in your paperwork.
On the subject of glycol, it’s usually added in systems to prevent accidental freezing in the event a heat pump stops working or if there’s a power outage. Most installers add it to be “safe”. I’m not sure it’s a requirement though.
I’m with Kev on the flow meter. The pump should have this built in as it cuts out when there’s insufficient flow. Surely Vaillant heat pumps have their own flow sensors without the need for additional external ones.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
You don’t need glycol or a flow meter….
glycol is just a terrible solution to the ‘power cut in the middle of winter’ problem…. Caleffi anti freeze valves are £150-200 a pair, Chinese ones are £40 a pair.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 38 Online
- 5,662 Members
Podcast Picks
Latest Posts
-
RE: Ecodan & MelCloud scheduling
@majordennisbloodnok Thank you. I will now stick to sch...
By DavidAlgarve , 7 minutes ago
-
RE: Rodents! A word of warning for heat pump owners
Did you take any photos @tim441?
By Mars , 21 minutes ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: EGP01 Manufacturer: Samsung Model: 8K...
By EGP01 , 2 hours ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 3 hours ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 4 hours ago
-
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 1 day ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 2 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 3 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 3 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 4 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 5 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 6 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 6 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 7 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 1 week ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 week ago