External stat issue
Hi
I'm back after running the ASHP for 7 months now with a different topic.
The pump runs fine with a constant temp of 20 degrees inside. It does cycle. I think we decided it's too big at 9kw.
Anyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers. The mercury is nearer predicted temperatures by forecast.
I would consider this important but should I make a thing of this?
Thanks
Cliff
Is it reading high or low?
Measurement of the outside temperature will directly affect Weather Compensation where the target flow temps are determined by the outside temperature, but if it's out by a known margin (3-4C), you may be able to offset the WC curve by the same amount.
It may also affect functions such as anti-freezing (if your heat pump has such features), which may be set to trigger at temps below 5C, either meaning the do not trigger when intended or trigger too early depending if it's reading high or low.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
I mean OAT. I have an external stat facing north around 2m up
Posted by: @cliffhangerI mean OAT. I have an external stat facing north around 2m up
If it is measuring (and only measuring) the OAT, it is a sensor, if it measures the OAT and then does something like turn the heating on or off, then it is a (thermo)stat. It is difficult to answer your original question (how important is accuracy) if we don't know what you are talking about!
Midea 14kW (for now...) ASHP heating both building and DHW
Right. It's the outside weather sensor that's wrong compared to Mercury.
I'm running the pump on external weather compensation.
@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
As mentioned earlier it is 2m up sand facing north.
Looks like I will have to make curve changes as it is consistently inaccurate. Still under guarantee incidentally. Are they as accurate normally as Mercury?
Posted by: @cliffhangerStill under guarantee incidentally.
That's probably the most important point, maybe see if you can get a replacement fitted?
Midea 14kW (for now...) ASHP heating both building and DHW
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 542 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: DHW heat loss through pumps.
@ubert767 Interesting. So the relay detects you are...
By JamesPa , 3 minutes ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And the saga continues… So today a Senior Grant Engin...
By Crimson , 19 minutes ago
-
RE: Electricity price predictions
The plan is not to switch off for extended periods. Al...
By Jeff , 53 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
The problem comes only if you can't turn the ft down su...
By JamesPa , 1 hour ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa Yes, the OAT sensor is situated on the back pa...
By Toodles , 3 hours ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
Just to clarify, returning water from UFH is colder tha...
By lukewarmbath , 3 hours ago
-
RE: 10kw heat pump run in 24*7 data?
A different heat pump (Midea 14kW) but a stark reminder...
By cathodeRay , 3 hours ago
-
From what I see, the work to upgrade the cable, etc all...
By Batpred , 3 hours ago
-
RE: Confusion over Octopus Tariffs
That's sounds great. I have no ASHP, but 15kwh storage....
By Batpred , 4 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Locked environments are difficult to manage, it also me...
By Batpred , 4 hours ago
-
RE: Do Heat Pumps need to start up at Full Power?
@steelbadger Attached is the plot for various parameter...
By Toodles , 8 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Hi all, I had a 15kw installed 3 weeks ago. The past we...
By jamesh , 9 hours ago
-
Adia Therma - 'autopilot for heat pumps'
Thought I'd pop this one in here as the Adia proposal a...
By seatonian , 23 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
Don't know answer to final question. Your contract p...
By JamesPa , 23 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Ah, it seems PACE BMS are easy to source on AliExpress,...
By Batpred , 24 hours ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
@jamespa Agreed I don't feel concerned about this, espe...
By jeegnesh , 1 day ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@toodles Yep, and it is not even a sticking plaster ...
By Jeff , 1 day ago
-
RE: Renewables & Heat Pumps in the News
I agree, imperfect systems like voting for politicians ...
By Batpred , 1 day ago
-
RE: Gov wants to alter our FIT contracts from rpi to cpi
The consultation is just part of the normal process for...
By Jeff , 1 day ago