External stat issue
Hi
I'm back after running the ASHP for 7 months now with a different topic.
The pump runs fine with a constant temp of 20 degrees inside. It does cycle. I think we decided it's too big at 9kw.
Anyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers. The mercury is nearer predicted temperatures by forecast.
I would consider this important but should I make a thing of this?
Thanks
Cliff
Is it reading high or low?
Measurement of the outside temperature will directly affect Weather Compensation where the target flow temps are determined by the outside temperature, but if it's out by a known margin (3-4C), you may be able to offset the WC curve by the same amount.
It may also affect functions such as anti-freezing (if your heat pump has such features), which may be set to trigger at temps below 5C, either meaning the do not trigger when intended or trigger too early depending if it's reading high or low.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
I mean OAT. I have an external stat facing north around 2m up
Posted by: @cliffhangerI mean OAT. I have an external stat facing north around 2m up
If it is measuring (and only measuring) the OAT, it is a sensor, if it measures the OAT and then does something like turn the heating on or off, then it is a (thermo)stat. It is difficult to answer your original question (how important is accuracy) if we don't know what you are talking about!
Midea 14kW (for now...) ASHP heating both building and DHW
Right. It's the outside weather sensor that's wrong compared to Mercury.
I'm running the pump on external weather compensation.
@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
As mentioned earlier it is 2m up sand facing north.
Looks like I will have to make curve changes as it is consistently inaccurate. Still under guarantee incidentally. Are they as accurate normally as Mercury?
Posted by: @cliffhangerStill under guarantee incidentally.
That's probably the most important point, maybe see if you can get a replacement fitted?
Midea 14kW (for now...) ASHP heating both building and DHW
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,338 Topics
- 52.8 K Posts
- 521 Online
- 5,994 Members
Join Us!
Podcast Picks
Latest Posts
-
-
RE: Home energy storage & battery register
Now the proud owner of: 4.1Kw peak Aiko Neostar solar...
By TechnoGeek , 57 minutes ago
-
RE: What a Bad Heat Pump Installation Looks Like
Shoot the b@stards? Simple, but effective. Seriously ...
By cathodeRay , 58 minutes ago
-
RE: The good, the bad and the not that great – my heat pump installation
I did, thanks, and thanks to for reminding me I should ...
By cathodeRay , 2 hours ago
-
RE: Latest NIBE model has known defect and no solution
@kings I don’t I’m afraid as I submitted it through my ...
By richardpool , 3 hours ago
-
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Aira called me back today, but not sure we got to the a...
By ChandyKris , 7 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
That level of cycling is normal and absolutely nothing ...
By JamesPa , 12 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Hello Henri. It is disappointing, but I must pres...
By DavidAlgarve , 1 day ago
-
RE: Experience with Mitsu Par 50/60 Wireless Controller
The 27°C request doesn't boost the weather compensation...
By Sheriff Fatman , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Oh and it was installed by Stevie Wonder!
By Grantmethestrength , 2 days ago
-
There seems to be plenty of evidence to support this. ...
By JamesPa , 2 days ago
-
RE: One Year Review: Grant 13kW ASHP - A Catalogue of Errors
@solenoid it sounds like you are making progress. No n...
By JamesPa , 2 days ago
-
RE: How good is the app support for your heat pump?
I think you are right about the ebus stick. It's cert...
By JamesPa , 3 days ago
-
RE: My DIY Heat Pump installation
@majordennisbloodnok Element-ary my Dear Major.
By Toodles , 3 days ago
-
Welcome to the forums @isaac. What you’re describing is...
By Mars , 3 days ago
-
Win an Eve Smart Home Bundle worth over £350!
Win an Eve Smart Home Bundle worth over £350! ...
By Mars , 3 days ago
-
RE: Is your heat pump insured?
I chose Tesco in the end. Unambiguously cover HP, PV an...
By Davesoa , 3 days ago