External stat issue
Hi
I'm back after running the ASHP for 7 months now with a different topic.
The pump runs fine with a constant temp of 20 degrees inside. It does cycle. I think we decided it's too big at 9kw.
Anyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers. The mercury is nearer predicted temperatures by forecast.
I would consider this important but should I make a thing of this?
Thanks
Cliff
Is it reading high or low?
Measurement of the outside temperature will directly affect Weather Compensation where the target flow temps are determined by the outside temperature, but if it's out by a known margin (3-4C), you may be able to offset the WC curve by the same amount.
It may also affect functions such as anti-freezing (if your heat pump has such features), which may be set to trigger at temps below 5C, either meaning the do not trigger when intended or trigger too early depending if it's reading high or low.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @cliffhangerAnyway how important is the accuracy of the external stat? Mine is out by 3-4 degrees C when compared to two mercury thermometers.
Do you mean sensor rather than stat? If so, and we are talking about the OAT (outside air temperature) as reported by a heat pump, then this something that has cropped up a number of times, particularly when the sensor is inside the heat pump, and so samples air that is affected by the heat pump's own activity.
More generally, it may not matter too much if it is consistently inaccurate. In effect, the WCC settings will accommodate that consistent inaccuracy. But if it is inconsistent, then things may get more interesting. There's currently a discussion on what the real OAT is on this thread.
I mean OAT. I have an external stat facing north around 2m up
Posted by: @cliffhangerI mean OAT. I have an external stat facing north around 2m up
If it is measuring (and only measuring) the OAT, it is a sensor, if it measures the OAT and then does something like turn the heating on or off, then it is a (thermo)stat. It is difficult to answer your original question (how important is accuracy) if we don't know what you are talking about!
Midea 14kW (for now...) ASHP heating both building and DHW
Right. It's the outside weather sensor that's wrong compared to Mercury.
I'm running the pump on external weather compensation.
@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@cliffhanger - OK, that's clear. My earlier remark about if it is consistently inaccurate still applies. The weather compensation curve will in effect have the same error, but it will work, although be rather confusing.
Let's say the OAT sensor is consistently reads 4 degrees higher than the actual OAT, and you want a curve that has 50 @ -2 / 30 @ 15 actual end points, then to get that, you will have to set the curve to 54 @ -2 / 34 @ 15 (because when the OAT sensor says 54 OAT it is actually 50 OAT, if that makes sense. All a bit confusing, but no reason why it should not work.
If it is inconsistently inaccurate, then that won't work.
Are then any reasons why it might be inaccurate, apart from the sensor itself being faulty?
As mentioned earlier it is 2m up sand facing north.
Looks like I will have to make curve changes as it is consistently inaccurate. Still under guarantee incidentally. Are they as accurate normally as Mercury?
Posted by: @cliffhangerStill under guarantee incidentally.
That's probably the most important point, maybe see if you can get a replacement fitted?
Midea 14kW (for now...) ASHP heating both building and DHW
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 142 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 11 hours ago
-
RE: Help needed with Grant Aerona 3 issues
Noted. Its a pity you didnt capture the flow rate and ...
By JamesPa , 16 hours ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 16 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 23 hours ago
-
RE: Changing from 4-port buffer to volumizer
@andy1618 see the very sage advice from @editor above. ...
By JamesPa , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 1 day ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 2 days ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 2 days ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
Also, though they weren’t prepared to match the price t...
By Toodles , 2 days ago
-
RE: How long will your energy contract last?
My INTELLI-FIX-12M-25-08-29 has less than 12 months to ...
By Batpred , 2 days ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
Then, perhaps @toodles , you should've made a submissio...
By Transparent , 2 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I am wondering if anyone with an EV could find the 7p/k...
By Batpred , 2 days ago
-
Possibly, but it would also reduce DeltaT across the em...
By JamesPa , 2 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@cathoderay It was reminiscent of the BBC Open Universi...
By Toodles , 2 days ago
-
-
@morgan They are unsupervised these days, can’t get the...
By Toodles , 5 days ago