[Solved] Effect of Mitsu PAR WT60 Wireless Controller
I believe hat I have correctly installed the PAR WT60 on my FTC60 which was previosly (and is still) set up for Weather compensation, as attachment and which performed reasonably well last year.
Conditions are currently marginal in the Algarve with night & evening/ time temperatures of 17-18C. I am experimenting with the wireless controller to give a comfortable living room temperature in the evening of say 23C, but I find I have set the wireless controller 2-3 degrees higher than that and I can then only achieve the desired 23C by setting the FTC6 at +5
It seems a bit extreme, but should I reset the weather compensation to, say 30C at OAT 18C?
All Tado's are set open
Hi David,
If your Mitsi is still on weather compensation then the WT60 should act as an internal temperature limiter. The temperature it's set to is the switch on temp and the set temp + 1C is the switch off temperature. So if you want the internal temperature to be 23C set it to 22.5C.
As your WC curve has 47C at - 1C I guess you have radiators? I ask because it is unlikely that your (or any) radiators can dissipate much heat with a flow temp of 25C and internal temp of 23C. This explains the need for your FTC +5 setting. The FTC +5 will have increased the WC curve by 5C, so the equivalent of 30C at 18C (and 52C at -1C). If 47C at -1C works for your house, then yes set the WC curve to 30C at 18C.
Hi Rob.
Thanks for your comments and I am relieved that I appear to be on the right track. I had to step in and do the PAR WT60 installation myself after my contractor failed to do so and I was rather anxious to prove that the system was working satisfactorily before the winter.
I will see how it performs when the weather changes but it was 20C last night and I have never known temperatures as high as this, almost into November.
Once again, thank you.
@davidalgarve I was wondering how your home performs (loses or retains heat) in these milder conditions? Since, if it’s only 17c outside at the moment what would be the indoor temperature if there was no heating operating at all?
I also seem to recall you have a large HP so my question is are you intending to raise the temperature with a higher water flow temperature to prevent cycling. And putting up with longer OFF times? Or are you planning to operate your heat pump at the low flow temperature shown on your weather compensation curve which might cause faster on/off cycling?
perhaps I’m missing some detail like a buffer tank or some other heat store in your system?
I’ve attached a graph from our MELCloud system which shows our monthly report on internal room temperature compared to our outdoor temperature. We only turned on the heating on 3rd October where you can see the jump in indoor temperature.
What is interesting is how the indoor temperature remained 3 or 5c higher than the outdoor temperature even though there was no occupancy. So the only heat gain was from solar energy through windows and roof and wall insulation.
Our heat pump is only 8.5 kw with radiators only, but we have to operate the weather compensation curve at a minimum of 34c if we want to avoid rapid cycling. At 17 c ambient our HP operates for 2 hours max then idles for 4 hours.
@sunandair We were not present to do a tidy changeover from summer to winter due to family and health problems and it was mid October before I could complete the PAR 60 installation and "switch on" so to speak.
These were also new conditions following re-piping of the buffer tank as a return leg volumiser in a radiator system, with only the one Ecodan pump, so it was very much a case of into the unknown. I don't think I can rely on any data at the moment, because the temperatures even at night, have only dropped below 17C on a couple of occasions.
It is a largish house and the temperature would not normally drop below 20-21C with OAT's of 16-17C, although that is a generalisation because there is significant heat gain in our upstairs south facing lounge and conversely, nothing on the downstairs bedroom & sitting room. (We do have solar, but this is used for topping up DHW temperature and charging the car at this time. However, this is being limited by the lower sun).
We will collect more data as the OAT drops, but I am favouring a lower flow temperature if I can get away with it. I still have to experiment with the pump flow, (currently on 3 for CH and 2 for DHW) and the consequential flow and return temperatures. (The previously fitted secondary pump had no facility for changing the speed)
I realise that this must all seem something of a nightmare in comparison with some of the carefully calculated installations described on the forum, but I have to play the hand that I am given with no reliable technical backup from Mitsubishi.
I am in touch with Havenwise and may hand over to them once I have made a little more sense of it.
Thank you for your interest and I am sorry that I could not provide more precise answers at this time.
- 26 Forums
- 2,283 Topics
- 51.1 K Posts
- 138 Online
- 5,944 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Renewables & Heat Pumps in the News
Our average cost of the retrofit part of the work is ar...
By ASHP-BOBBA , 5 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Pressure will be same either side of llh. Llh gives so...
By JamesPa , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@agentgeorge it has got 2, the other bleed screw is the...
By AdamK , 6 hours ago
-
-
RE: Maximising Home Automation: Integrating Octopus Energy & More
Of course, @transparent; you're right. In fact, it's a ...
By Majordennisbloodnok , 7 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hi Only joined the forum today and have found this t...
By Pwils , 8 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@transparent Would that mean they were rubbishing your ...
By Toodles , 9 hours ago
-
I too felt the podcast was useful but think it could do...
By AndrewJ , 10 hours ago
-
@adamk apologies but did not understand what exactly yo...
By Eliuccio , 10 hours ago
-
Putting a 30 cm. radio controlled wall clock on Freegle...
By Toodles , 10 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I’m with octopus, best tariff for heat pump and battery...
By AgentGeorge , 11 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
I assume you are referring to this postand yes indeed y...
By JamesPa , 11 hours ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey Welcome to the Homely control club! Toodles...
By Toodles , 14 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@nickhorne Unfortunately not. We take the "normal" IOG ...
By HCas , 1 day ago
-
RE: Mixture of copper and plastic CH pipework. Will it be ok, or need changing?
In principle yes. Some heat pumps (I think including D...
By JamesPa , 1 day ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Some of the circuits in my home are not protected by RC...
By Batpred , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Aqara sells some inexpensive hubs (usb dongle size) tha...
By Batpred , 1 day ago
-
RE: Extend the colder range of the weather compensation curve?
@thebinman In answer to this and personal...
By TechnoGeek , 1 day ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard That's probably fine, provided as you say...
By GrahamF , 2 days ago