Ecodan - optimal external installation?
I think this notion of an 'optimal' install is something of a chimera. Every installation is different, and the majority of forum users have experience of just the one installation. From what you have said (though images are worth a thousand words) your installation seems to be fine, the installers haven't done anything stupid.
If you are having vibration issues at the heat pump then it might be an equipment issue rather than a pipework issue. I have noise inside introduced by the circulation pumps, but only small amounts of occasional mechanical noise and the sound of the air being moved from the outside unit. The units weigh around 100kg so you wouldn't want any slight vibration to be converted into sound or transmitted to the rigid, fixed pipework, but they aren't going to move around like washing machines.
You ask a few questions:
28mm pipework should run as far as you can take it into the house - you need volume of water in the system to cover defrosts.
You protect the outside pipework and the pump either by having glycol so the water can just sit at very cold temperatures, or you circulate the warm water in the pipes to keep the outside parts from freezing – the anti-freeze valves are a fail-safe should you be unable to power the water circulation. You would not want to be dumping glycol.
Full bore valves are isolating valves...
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
I’d consider my system to be installed quite optimally… I have one anti freeze valve, no flexis, and over 20m of buried primary pipework.
I also don’t have any hydraulic separation, and I have 400mm clear to the rear of the evaporator.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @harriup28mm pipework should run as far as you can take it into the house - you need volume of water in the system to cover defrosts.
Yes. Where would the optimal position and method of stepping down? I assume nearest the unit, so at the unit's inlet/outlet - but not sure how.
You protect the outside pipework and the pump either by having glycol so the water can just sit at very cold temperatures, or you circulate the warm water in the pipes to keep the outside parts from freezing – the anti-freeze valves are a fail-safe should you be unable to power the water circulation. You would not want to be dumping glycol.
Thank you.
Full bore valves are isolating valves...
From the BES component diagram in the OP (relevant section below), it shows 'isolator valves' and 'full bore valves' - though, having just looked at it again, I've just noticed the isolator valves are inside the property:
The isolator valves I mentioned describing my install are Inta lever ball valves - I assume these should be full bore to maximise flow rate and be positioned as the primary pipework exits the brickwork outside? Is there any value in having a second set at the unit's inlet/outlet too?
Posted by: @rhh2348What's the optimal / minimum length and shape of flexihoses (and why, if not for best performance and least vibration)?
I'd appreciate anyone's thoughts on this, having read in one or two posts (I now can't find...) that longer hoses can reduce/eliminate vibrations travelling through the primary pipework elsewhere.
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
10 hours ago
-
Ecodan with FTC7 - True Weather Compensation
2 days ago
-
Ecodan unable to hit legionella target temp - what's the consensus?
2 weeks ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
4 weeks ago
-
Rate the quality of your heat pump design and installation
1 month ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 399 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
yes, the circuit needs the usual protection, mcb and ma...
By Batpred , 5 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
I agree and that’s why I don’t believe a lot o...
By SimonF , 2 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
I doubt that matters, ToU tariffs are for the benefit o...
By JamesPa , 3 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 6 hours ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 8 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 10 hours ago
-
RE: Setback savings - fact or fiction?
Never assume it makes an ass of u and me! You need the...
By JamesPa , 10 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Before I answer your specific questions just one more t...
By JamesPa , 10 hours ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 21 hours ago
-
RE: Running from backup generaor in powercut?
Definitely and professionals sometimes miss it. I had...
By Batpred , 21 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 1 day ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 1 day ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 1 day ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 1 day ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 1 day ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 1 day ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 2 days ago