Ecodan Minimum Run Time, Flow & COP
We have an 11.2KW Ecodan with an FTC6, installed 2022 with a 300l HW tank and 10 circuits of Wundasmart underfloor heating in around 120 sqm, installer (who was generally great) left every circuit thermostatically controlled.
We spent a lot of time learning about the system over the last year, and one quirk of the Ecodan is a minimum run time which it imposes on itself and the impact on flow temperatures. After conversations with Mitsubishi, this is called the Compressor On Guard Strategy, which enforces a 20 minute minimum runtime, unless the Superheat has been >10C for 10 minutes. It took us a long time to find out from Mitsubishi that this existed.
It doesn't matter a lot what the above means, but the effect - a minimum run time - is interesting. Normally if the pump's minimum heat delivery is higher than the demand, then during low flow conditions (e.g. only a few thermostats calling for heat) the flow temp rises and the pump will turn itself off when flow exceeds 5C above the compensation curve set temperature. In our case, with flow around 27C that might be when flow hits 32C, cunsuming around 1KW of energy.
However the Ecodan will prioritise the importance of keeping on running over halting when exceeding the flow temperature, and will keep trying to heat the water while it keeps running. The compressor runs harder and harder as the temp spirals and we were recording 55C flows at which point it turned off. This incurred very high energy consumption (3KW or more).
This had a huge impact on the COP, dropped below 3 during mild weather. During cold weather it's never a problem, there's always enough flow because so many circuits are calling for heat and minimum runtimes are over 20mins anyway.
We contemplated adding a buffer (cost around £1K installed) but instead trialled removing all thermostatic control in all rooms except the coldest one and using full system volume all the time with the compensation curve driving the system. The result in mild weather is dramatic: we can keep flow temps at 23C above 13C outside, the pump cycles twice an hour with max flow never exceeding 5C above set flow temp, Melcloud-reported COP is regularly over 5 and often over 6, it appears to be phenomenally efficient, borne out by much lower daily energy usage in mild weather.
We do have some small challenges with some warmer rooms getting a couple of degrees C above what we'd prefer but it is cheaper to just live with the extra heat, cost goes up if we re-introduce any thermostatically control rooms, because the volume reduced and pump works harder as above. Our Wundasmart manifolds use automatic balancing valves which set the circuit flow dependant on flow/return temps and can't be manually adjusted down, which is an unfortunate side-effect of an automated system.
The lesson learned is that Ecodans and lots of thermostats really don't work well in mild weather and it's much cheaper (and generally nicer) to go to the effort of working out the right compensation curve and running low flow temps against your full system volume.
Might be useful to anyone with an Ecodan, lots of thermostats and seeing big spikes in flow temps and energy consumption several times an hour during mild weather.
Rod
Posted by: @rodMight be useful to anyone with an Ecodan, lots of thermostats and seeing big spikes in flow temps and energy consumption several times an hour during mild weather.
Rod
Welcome to the forum and thank you for the detailed report. I must admit that I was not aware of the Compressor On Guard Strategy, which I don't believe is mentioned in the manual.
Your findings about thermostats is not only relevant to Ecodan owners, but probably all heat pump owners.
Very interesting. My (14kW) ASHP can definitely run the compressor in bursts of less than 20 minutes when in heating mode. It doesn't do it very often and only when in WC mode and mild conditions. It never heats to more than one or two degrees above WC set point though, although I have only two zones, which means the ASHP is heating at least half my house at any one time. Interestingly, although the compressor stops after less than 20 minutes, I don't think it is ever in heating mode for less than 20 minutes. That is, it spends some time in heating mode while delivering no energy.
This is heating you're talking about btw - the label on the graph on your attachment mentions DHW?
I've never heard of Compressor on guard or Superheat; it's not mentioned on the manuals afaik.
@derek-m if you skim through this Samsung doc, you will see details how a double compressor "heat pump"/AC works, some of this data is pointless to anyone but the engineers that need to look(improve/make a new model) at the machine beyond checking the refrigerant charge.
@kev-m Yes, it's in heating mode. For reasons I still don't understand the HP can spin up to do a DHW cycle when the tank temp is very close to setpoint and cut out immediately the set point is reached without entering the On Guard strategy, even if it's only a couple of mins long. Mitsubishi could not explain why the strategy is used for heating but not for water.
This stuff definitely isn't in the manual and isn't generally known to the support teams, it was only when I pressed them that this appeared.
Thanks fazel, much appreciated.
I suspect that the training manual is for industrial type units, since the smallest compressor of a twin compressor unit is rated at roughly 19kW, and each compressor in the main unit is rated at 25kW. I don't think that it would get planning permission. 😋
Nevertheless the manual appears to give a good description of the inner workings of a heat pump, which is very similar, if not exactly the same, as a domestic sized unit.
- 26 Forums
- 2,364 Topics
- 53.6 K Posts
- 168 Online
- 6,027 Members
Join Us!
Worth Watching
Latest Posts
-
Sadly, no, @agentgeorge. The inverter will handle 5kW t...
By Majordennisbloodnok , 10 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent The readings are 0 for amps, 0 ...
By Batpred , 10 hours ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 11 hours ago
-
RE: Speedcomfort radiator fans
I watched the video to see whether they'd potentially b...
By Sheriff Fatman , 11 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
@ecoste For what it's worth, this is my equivalent data...
By Sheriff Fatman , 12 hours ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 12 hours ago
-
RE: Setback savings - fact or fiction?
Will come back to the above points, but for now, I've j...
By cathodeRay , 12 hours ago
-
@jamespa I have found that it comes as a shock when we ...
By Toodles , 14 hours ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
I suspect a good chunk of the "losses" are power consum...
By Bash , 15 hours ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Hi @mickamills . Welcome to the forum. It sounds like...
By bontwoody , 16 hours ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 16 hours ago
-
RE: External pipework insulation
@transparent I hope you are not being admonished @trans...
By Toodles , 16 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
The FT levels off at either the set point OR the minimu...
By AndrewJ , 2 days ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent Thanks, this helps. Could it be that St...
By Batpred , 2 days ago
-
RE: Clivet ASHPs and weather compensation
Simon did share a lot of very helpful advice. On furthe...
By ambris , 2 days ago
-
-
RE: Advice on internal circulation pump noise
Extend the primary branch and make sure you have more t...
By ASHP-BOBBA , 3 days ago