Ecodan Cascade system conflicting views
Hi All
Great content and reading so far.
We have 2 x 14kw R32 single phase Ecodan's on their own phase with a 500l HW tank and a 500l buffer.
The house is 5200 square feet but 2/3 of it are double height ceilings. Its very well insulated as was completely modernised/extended 10 years ago and the guy really went to town on insulation - even the dry lining is insulated plasterboard. We have since the heat-loss calc changed 3/4 of the windows to triple glazed so improved still further from the 22mm double glazed units.
I have loads of questions but will start with this that had divided opinion:
Should the heating for the buffer tank be set to temperature compensation?
Currently its at 45 degrees with hot water priority (10 degree drop)
They only went live just before Christmas so quite early in ownership/experience
Thoughts?
Hi JPST21. delighted to see another Ecodan Cascade system on the RHH. I was beginning to think I was the only one! I have 2X 11.2KW R32s with Mitsi FTC controllers and the wireless room stat. Also switched on December 9th just before the temperature dropped and scared the pants off me watching the power meters spin.
Have you worked out how to get a COP figure out of this system? Mine says that the energy monitors are not installed?
Happy to compare notes.
Best regards
Tom
Hi Tom
We’re having the Wi-Fi link installed to be able to use the app rather than go to the plant room to make setting changes.
The energy usage parts are missing which may not be a bad thing although the new supply meter was at zero it’s now reading almost 1900 in 12 days. That did include the end of the cold snap and heating 1000 litres from 11 degrees.
There must be a way to see the usage v generation
The units were supplied as a kit but one terminal block was missing and support told the installers it could be done with the dip switches but this was incorrect and we lost 10 days waiting for the part!
It’s been a bit of a bumpy road so far to say the least
Jez
Hi Jez Very few on this forum seem to be bump free. The wireless kit is good though my software writer son was very rude about the limited functionality of the app interface. It certainly does allow one to control the setup remotely. Though I keep reading threads here that suggest that if we only get the weather compensation process right it will not need to be touched! I have not worked out how to do that yet.
Between December 10th startup and Monday January 2nd (23 days) my system consumed 1140 KWh. ( but in a much smaller house 281m2, heat loss estimate 16.5KW)
Posted by: @tommclHi Jez Very few on this forum seem to be bump free. The wireless kit is good though my software writer son was very rude about the limited functionality of the app interface. It certainly does allow one to control the setup remotely. Though I keep reading threads here that suggest that if we only get the weather compensation process right it will not need to be touched! I have not worked out how to do that yet.
Between December 10th startup and Monday January 2nd (23 days) my system consumed 1140 KWh. ( but in a much smaller house 281m2, heat loss estimate 16.5KW)
I have not looked in detail at a cascade system, since the necessity has only just arisen. I have attached a copy of the very comprehensive manual that Kev posted some time ago, it may throw some light of the subject.
There are also various YouTube videos giving details of how to set up and adjust the parameters for weather compensation. I think that many on the forum would be interested in details of what your son found.
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 71 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 hours ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 6 hours ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 18 hours ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 2 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 3 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 5 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 6 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 6 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 6 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 6 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago