Ecodan ASHP low flow rate 6L
Hi I've been trying to setup my ASHP in wc mode recently as been running it just like a gas boiler recently found out that was stupid and was why the cost of electricity was sky high
Been on a mission to learn as much as possible about the ftc5 to get this sorted I've got the WC setup but pump just kept cycling through reading and learning I've found out the flow rate is 6l my unit PUZ-WM85 should be around 15l the pump speed is at 5 dhw is also at 5 but speed is still 6L I drained the tf1 filter nothing much came out and the prrssure in the system is at 1.5bar
Anyhelp would be appreciated
How old are your radiators? Might they have a build up of sludge? Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
They were installed same time as the heating they are the thicker radiators aswel when trying to bleed through radiators just the clean antifreeze that comes out they do heat up evenly also
@davidm Maybe there is a restriction caused by a partially open/shut valve? It sounds as though, though the pumps are working hard, there is an obstruction to a free flow of water through the system. A partially open or shut valve would cause a restriction, turbulence and probably additional noise.
Other than that might there be some obstruction from ‘gunk’ that was dislodged during the plumbing work that has lodge itself in a pipe (possibly at a joint). A lot to check I know but if pump is working its’ socks off and the water isn’t flowing fast enough - it is almost bound to be an obstruction or restriction - or (shudder) a kinked pipe! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Yeah that's what I seems like to me if you up the pump speed on the actual pump the flow still doesn't change, unfortunately I'm not equipped to take apart any of that
it was a company that fitted the system and my housing association plumbers ain't clued up on the ASHP at all, they sent someone round before when I moved in to help me setup didn't have a clue what to do, taken it upon myself to learn and I enjoy tinkering but at a loss what to do now
@davidm welcome to the forums.
It sounds like your Ecodan system could benefit from some adjustments to optimise both flow rates and pump sizing. With pre-plumbed Ecodan cylinders, the internal pumps are often undersized for anything but the best-designed systems, and they may not provide the 12–14 L/min flow rate recommended for an 8 kW unit like yours. This kind of consistent flow is critical for efficient heating and to reduce unnecessary cycling, especially in weather compensation (WC) mode.
If you have system separation, such as a buffer tank, it might be worth considering removing it. By eliminating it, your system can circulate more freely and reach the needed flow rates more consistently.
Also, controlling valves across all rooms can reduce flow efficiency. Instead, consider limiting smart TRVs to just bedroom zones if a cooler environment is desired overnight. For the best results, aim to keep all other valves open, allowing the system to circulate freely without restriction. This should help the heat pump function more smoothly in WC mode, minimise cycling and improve efficiency – keeping those energy bills in check.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
All my trv valves are full open around the whole house removing anything wouldn't be a option as it doesn't belong to me (housing association)
You say reaching needed flow rates consistently it doesn't reach them at all it's just 6l on pump speed 5 if I turn it to 3 flow rate goes to 0
Kind of looking for information to pass onto the h/a to maybe actually get somewhere with it as their own plumbers ain't clued with these as most houses around are gas but the small village I'm in doesn't have gas most are oil heating or electric here
- 22 Forums
- 2,086 Topics
- 46 K Posts
- 15 Online
- 3,377 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness bold choice on the Kronoterm. Nice! Wi...
By Mars , 5 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
It took me more than a few goes as well, plus some help...
By cathodeRay , 21 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 1 day ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 2 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 3 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 3 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 3 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 5 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 6 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 6 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 6 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 6 days ago