Ecodan ASHP - How to optimise my set up?
Hi all,
I've recently purchased a new build property that came with an Ecodan ASHP set up (details below).
I have been reading / tinkering as much as possible, but given there is so much to learn I thought it would be best to ask a blanket question:
"Are there any suggestions for optimising my controls / settings, given my situation?"
Currently my COP averages around 2.2x, (Oct-23 to Jan-24), and to be frank - the overall consumption feels high
Yesterday heating alone consumed 30kwh, delivered 62kwh (outside temps were below 5c the entire day), I guess if the COP was above 3x, then the consumption would be easier to stomach.
Right so details on my set-up: (see schematic diagram below)
- 100% electric house
- Ecodan 6kW - PUZ-WM60VAA
- 283L Tank
- The roof has Solar PV (tiny 0.4kw) and Solar Thermal
- The property is a Semi-detached 3 story, 4 bedroom
- Zone 2 - (ground floor) - UFH (there are two Heatmiser room stats, 1x kitchen + 1x living room - all set to 18c) (I think the heatmisers are linked to the UFH manifold? See picture below)
- Zone 1 - (1st + 2nd floor) - rads (one Heatmiser stat located on the 1st floor - set to 17c) (all Rads set to fully open)
- Total floor space = 119m^2
- Total property volume = 319m^3
- EPC = A (92), with "very good insulation"
- Air permeability = 5.55 (
- Currently two people living in the property (one who loves opening the trickle vents, and one who loves closing them. 🤣 )
- Current settings:
- DHW Target Temp = 45c
- Weather compensation curve set to -10c = 43c & 20c = 25C (no idea if this is anywhere good??)
- Flow rate 9l/m (this was set at 3 in the Ecodan module, but there is also a Grundfos pump set to1? (see schematic diagram below)
- We don't have set back temps / timers
- A couple of observations so far:
- When we moved in all stats were set to 21c, the house was very warm and was consuming c. 55kwh a day for heating (outside temp c. 12c), we moved the stats down (although I am not sure if we shouldn't have just adjusted the weather compensation curve instead?)
- The hot water temp when taking a shower drops rapidly, like after three minutes even if I max out the mixer I can feel the temp dropping. (rain shower head, so consumption may be high?)
- The Ecodan seems to short cycle quite a bit (heatmisers are always switching between calling for heat / not calling for heat), this has gotten better since I flattened out the weather compensation curve. (see below pic of when it goes crazy)
Any suggestions / comments on how to improve the COP of my set up? 😀
Hi Jake
My previous house had very similar stats to yours and had a 5kW Ecodan. I would suggest that yours should be very easy to heat at a low cost in the same way mine was. Your weather compensation curve is reasonable but your COP is awful. Looking at your setup the thing that jumps out at me is the zoning and heatmiser stats. I think these may be the reason why your flow temperature is all over the place suggesting a lot of stopping and starting.
I dont have a great deal of experience with these but my understanding is both should be avoided if possible. Extrapolating from my current system I would guess that you should set your stats high and try and adjust room temperature by affecting flow. On rads this is done by adjusting the manual valves leaving any thermostatic valves fully open.
Im sure others will be able to give you more specific advice but Im confident that you should be able to arrive at a good efficient system given time 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks for the reply!
Yes, I had wondered whether if I should just crank up the heatmisers, to make sure they are not the limiters, and adjust adjust the weather compensation if it's too warm / cold. It is just baffling to me that an installation done from scratch, in 2023, would include what appears to be a completely redundant / obstructive layer of equipment (and have multiple of them). Does anyone know in what scenario it make sense to have the heatmisers? Or is there consensus that zoning and heatmiser stats when connected to an AHSP is a bit daft?
@jaket Welcome to the world of bodged installations Jake! You are absolutely correct in your thinking. Having given it a bit of thought, I would try the following
1. crank up your heatmisers to 23C
2. maximise the flow through the rad? in the room you want warmest
3. run the heating for 4 or more hours to get it up to temperature
4. if your main room is too warm adjust your weather compensation curve downwards and vice versa
5. when you have your main room right, adjust the flows to the other rooms using the manual valve on the rads, keep any thermostatic valves wide open.
6. keep tweaking until you have all the rooms as you want them
7. im not sure how you would tackle the UFH. presumably it wont have a thermostatic valve fitted (it shouldnt)
let me know how its goes 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jaket Hi I have an ecodan with ufh and rads and Heatmisers. You can get it working well. It will just take some tweaking.
What you will probably find is that you need to set the Heatmisers to limit the max temp. You said 21 was too hot so maybe that’s your max limit or 20.5.
From the hourly flow temps you posted your unit is cycling 4 times an hour this won’t be good for efficiency.
Ecodans don’t modulate down well so you find that flow temps in the 20’s will lead to cycling. I have found that the lowest flow temp I can go to is 32C then regardless of the outside temp it won’t cycle. So my curve is flat at 32C down to 3C then it ramps up 1C per 1C till it gets to 45C at -10C.
You want all your circuits open rads and ufh at the same time to maximise the water volume are heating this will reduce cycling and increase efficiency.
with regards to the Hot water how long are you heating it for? Mine is set to 48C and heats for 2 hours. This is long enough to get the entire tank up to temp from cold. I don’t reheat at all there is enough for 2 showers washing up and kids bath before the next nightly reheat. Check what your hot water settings are if it’s reheating after a shower its reheat temp is probably set too high. Will just take some trial and error do you need to reheat or will the tank last a full day or just reheat once in the evening.
In the recent cold snap I was using 30-40kwh a day for heating you should be able to beat that.
Here is my flow for an hour yesterday afternoon it ran like this all day.
just noticed you posted flow rate was that from the running information menu using code 540? If so it’s very low turn the pump speed up to 4 and 5 and see what values you get. This will also be causing cycling and poor efficiency
Posted by: @gary
-- Attachment is not available --Here is my flow for an hour yesterday afternoon it ran like this all day.
just noticed you posted flow rate was that from the running information menu using code 540? If so it’s very low turn the pump speed up to 4 and 5 and see what values you get. This will also be causing cycling and poor efficiency
Yes, that was using code 540, with the pump speed set at 3.
If I increase the pump speed to 5, the flow rate (using code 540) shows 19 - is this better / sufficient?
Maybe asked a better way, what flow rate is ideal?
Posted by: @gary@jaket Hi I have an ecodan with ufh and rads and Heatmisers. You can get it working well. It will just take some tweaking.
What you will probably find is that you need to set the Heatmisers to limit the max temp. You said 21 was too hot so maybe that’s your max limit or 20.5.
From the hourly flow temps you posted your unit is cycling 4 times an hour this won’t be good for efficiency.
Ecodans don’t modulate down well so you find that flow temps in the 20’s will lead to cycling. I have found that the lowest flow temp I can go to is 32C then regardless of the outside temp it won’t cycle. So my curve is flat at 32C down to 3C then it ramps up 1C per 1C till it gets to 45C at -10C.
You want all your circuits open rads and ufh at the same time to maximise the water volume are heating this will reduce cycling and increase efficiency.
with regards to the Hot water how long are you heating it for? Mine is set to 48C and heats for 2 hours. This is long enough to get the entire tank up to temp from cold. I don’t reheat at all there is enough for 2 showers washing up and kids bath before the next nightly reheat. Check what your hot water settings are if it’s reheating after a shower its reheat temp is probably set too high. Will just take some trial and error do you need to reheat or will the tank last a full day or just reheat once in the evening.
In the recent cold snap I was using 30-40kwh a day for heating you should be able to beat that.
On the hot water - I can literally feel the temp start to drop after 3 min of use.
I can only assume it is being caused by either:
- The rain shower head is pushing serious volume, resulting in cold water mixing within 3 minutes of use,
- The outlet pipe is connected to the bottom of the tank.
I think I will have to do a bit more research on this point, might have to see if this has been a common issue for other ecodan users?
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
2 hours ago
-
Ecodan with FTC7 - True Weather Compensation
22 hours ago
-
Ecodan unable to hit legionella target temp - what's the consensus?
1 week ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
4 weeks ago
-
Ecodan consuming 100kwh per day in new build!!!
6 months ago
Currently viewing this topic 4 guests.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 466 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
The costs, if any, are not that great - see my calculat...
By JamesPa , 31 minutes ago
-
RE: Weather compensation- why you should use it
I think we're starting to veer off topic again (probabl...
By Majordennisbloodnok , 40 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Only the manual The commissioning documents state which...
By JamesPa , 1 hour ago
-
RE: Electricity price predictions
As electricity prices continue to rise and specialist h...
By Mars , 2 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Your installer is probably right. The L9 error means l...
By JamesPa , 2 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Thank you. No-one did. You posted some links to ...
By Majordennisbloodnok , 2 hours ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 3 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 3 hours ago
-
RE: Running from backup generaor in powercut?
@batpred Thanks for the warning. definately a job for a...
By Pipcart , 3 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@editor Mars, First of all thank you for your enco...
By Wally , 4 hours ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 4 hours ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 9 hours ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 10 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 20 hours ago
-
RE: Air source heat pump circuit not operational
Welcome to the forums. If the thermostat shows it’s c...
By Mars , 20 hours ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 22 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
That makes plenty of sense. Perhaps more importantly, O...
By Majordennisbloodnok , 1 day ago