Ecodan ASHP - How to optimise my set up?
Hi all,
I've recently purchased a new build property that came with an Ecodan ASHP set up (details below).
I have been reading / tinkering as much as possible, but given there is so much to learn I thought it would be best to ask a blanket question:
"Are there any suggestions for optimising my controls / settings, given my situation?"
Currently my COP averages around 2.2x, (Oct-23 to Jan-24), and to be frank - the overall consumption feels high
Yesterday heating alone consumed 30kwh, delivered 62kwh (outside temps were below 5c the entire day), I guess if the COP was above 3x, then the consumption would be easier to stomach.
Right so details on my set-up: (see schematic diagram below)
- 100% electric house
- Ecodan 6kW - PUZ-WM60VAA
- 283L Tank
- The roof has Solar PV (tiny 0.4kw) and Solar Thermal
- The property is a Semi-detached 3 story, 4 bedroom
- Zone 2 - (ground floor) - UFH (there are two Heatmiser room stats, 1x kitchen + 1x living room - all set to 18c) (I think the heatmisers are linked to the UFH manifold? See picture below)
- Zone 1 - (1st + 2nd floor) - rads (one Heatmiser stat located on the 1st floor - set to 17c) (all Rads set to fully open)
- Total floor space = 119m^2
- Total property volume = 319m^3
- EPC = A (92), with "very good insulation"
- Air permeability = 5.55 (
- Currently two people living in the property (one who loves opening the trickle vents, and one who loves closing them. 🤣 )
- Current settings:
- DHW Target Temp = 45c
- Weather compensation curve set to -10c = 43c & 20c = 25C (no idea if this is anywhere good??)
- Flow rate 9l/m (this was set at 3 in the Ecodan module, but there is also a Grundfos pump set to1? (see schematic diagram below)
- We don't have set back temps / timers
- A couple of observations so far:
- When we moved in all stats were set to 21c, the house was very warm and was consuming c. 55kwh a day for heating (outside temp c. 12c), we moved the stats down (although I am not sure if we shouldn't have just adjusted the weather compensation curve instead?)
- The hot water temp when taking a shower drops rapidly, like after three minutes even if I max out the mixer I can feel the temp dropping. (rain shower head, so consumption may be high?)
- The Ecodan seems to short cycle quite a bit (heatmisers are always switching between calling for heat / not calling for heat), this has gotten better since I flattened out the weather compensation curve. (see below pic of when it goes crazy)
Any suggestions / comments on how to improve the COP of my set up? 😀
Hi Jake
My previous house had very similar stats to yours and had a 5kW Ecodan. I would suggest that yours should be very easy to heat at a low cost in the same way mine was. Your weather compensation curve is reasonable but your COP is awful. Looking at your setup the thing that jumps out at me is the zoning and heatmiser stats. I think these may be the reason why your flow temperature is all over the place suggesting a lot of stopping and starting.
I dont have a great deal of experience with these but my understanding is both should be avoided if possible. Extrapolating from my current system I would guess that you should set your stats high and try and adjust room temperature by affecting flow. On rads this is done by adjusting the manual valves leaving any thermostatic valves fully open.
Im sure others will be able to give you more specific advice but Im confident that you should be able to arrive at a good efficient system given time 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks for the reply!
Yes, I had wondered whether if I should just crank up the heatmisers, to make sure they are not the limiters, and adjust adjust the weather compensation if it's too warm / cold. It is just baffling to me that an installation done from scratch, in 2023, would include what appears to be a completely redundant / obstructive layer of equipment (and have multiple of them). Does anyone know in what scenario it make sense to have the heatmisers? Or is there consensus that zoning and heatmiser stats when connected to an AHSP is a bit daft?
@jaket Welcome to the world of bodged installations Jake! You are absolutely correct in your thinking. Having given it a bit of thought, I would try the following
1. crank up your heatmisers to 23C
2. maximise the flow through the rad? in the room you want warmest
3. run the heating for 4 or more hours to get it up to temperature
4. if your main room is too warm adjust your weather compensation curve downwards and vice versa
5. when you have your main room right, adjust the flows to the other rooms using the manual valve on the rads, keep any thermostatic valves wide open.
6. keep tweaking until you have all the rooms as you want them
7. im not sure how you would tackle the UFH. presumably it wont have a thermostatic valve fitted (it shouldnt)
let me know how its goes 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jaket Hi I have an ecodan with ufh and rads and Heatmisers. You can get it working well. It will just take some tweaking.
What you will probably find is that you need to set the Heatmisers to limit the max temp. You said 21 was too hot so maybe that’s your max limit or 20.5.
From the hourly flow temps you posted your unit is cycling 4 times an hour this won’t be good for efficiency.
Ecodans don’t modulate down well so you find that flow temps in the 20’s will lead to cycling. I have found that the lowest flow temp I can go to is 32C then regardless of the outside temp it won’t cycle. So my curve is flat at 32C down to 3C then it ramps up 1C per 1C till it gets to 45C at -10C.
You want all your circuits open rads and ufh at the same time to maximise the water volume are heating this will reduce cycling and increase efficiency.
with regards to the Hot water how long are you heating it for? Mine is set to 48C and heats for 2 hours. This is long enough to get the entire tank up to temp from cold. I don’t reheat at all there is enough for 2 showers washing up and kids bath before the next nightly reheat. Check what your hot water settings are if it’s reheating after a shower its reheat temp is probably set too high. Will just take some trial and error do you need to reheat or will the tank last a full day or just reheat once in the evening.
In the recent cold snap I was using 30-40kwh a day for heating you should be able to beat that.
Here is my flow for an hour yesterday afternoon it ran like this all day.
just noticed you posted flow rate was that from the running information menu using code 540? If so it’s very low turn the pump speed up to 4 and 5 and see what values you get. This will also be causing cycling and poor efficiency
Posted by: @gary
-- Attachment is not available --Here is my flow for an hour yesterday afternoon it ran like this all day.
just noticed you posted flow rate was that from the running information menu using code 540? If so it’s very low turn the pump speed up to 4 and 5 and see what values you get. This will also be causing cycling and poor efficiency
Yes, that was using code 540, with the pump speed set at 3.
If I increase the pump speed to 5, the flow rate (using code 540) shows 19 - is this better / sufficient?
Maybe asked a better way, what flow rate is ideal?
Posted by: @gary@jaket Hi I have an ecodan with ufh and rads and Heatmisers. You can get it working well. It will just take some tweaking.
What you will probably find is that you need to set the Heatmisers to limit the max temp. You said 21 was too hot so maybe that’s your max limit or 20.5.
From the hourly flow temps you posted your unit is cycling 4 times an hour this won’t be good for efficiency.
Ecodans don’t modulate down well so you find that flow temps in the 20’s will lead to cycling. I have found that the lowest flow temp I can go to is 32C then regardless of the outside temp it won’t cycle. So my curve is flat at 32C down to 3C then it ramps up 1C per 1C till it gets to 45C at -10C.
You want all your circuits open rads and ufh at the same time to maximise the water volume are heating this will reduce cycling and increase efficiency.
with regards to the Hot water how long are you heating it for? Mine is set to 48C and heats for 2 hours. This is long enough to get the entire tank up to temp from cold. I don’t reheat at all there is enough for 2 showers washing up and kids bath before the next nightly reheat. Check what your hot water settings are if it’s reheating after a shower its reheat temp is probably set too high. Will just take some trial and error do you need to reheat or will the tank last a full day or just reheat once in the evening.
In the recent cold snap I was using 30-40kwh a day for heating you should be able to beat that.
On the hot water - I can literally feel the temp start to drop after 3 min of use.
I can only assume it is being caused by either:
- The rain shower head is pushing serious volume, resulting in cold water mixing within 3 minutes of use,
- The outlet pipe is connected to the bottom of the tank.
I think I will have to do a bit more research on this point, might have to see if this has been a common issue for other ecodan users?
-
Mitsubishi Ecodan 11kw Defrosting Issue.
6 days ago
-
Mitsubishi EcoDan ASHP Settings not saving.
1 week ago
-
Is my Ecodan well installed and setup?
4 weeks ago
-
Ecodan DHW Settings missing
9 months ago
-
Ecodan - optimal external installation?
10 months ago
- 21 Forums
- 1,744 Topics
- 37.3 K Posts
- 20 Online
- 2,035 Members
Join Us!
Latest Posts
-
RE: In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
A similar pattern happened again last night and into th...
By cathodeRay , 6 hours ago
-
RE: Do thick walls make for warm houses?
@bontwoody A lot of the reason the u value doesn’t s...
By robl , 7 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
@crimson A raise in flow temperature to 45 deg. C shoul...
By Toodles , 7 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@mikeh, thanks a lot for the video. I found them very i...
By trungdong , 8 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor I suspect I need both. We're still trying to ge...
By Odd_Lion , 1 day ago
-
RE: Samsung HP secondary pump wiring
Thanks for the reply. I have asked a couple of days ago...
By Chris-in-Kemnay , 1 day ago
-
RE: New Samsung 12KW Heat Pump Help
@mike-h It has been a few days since we’ve changed t...
By dinhp , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Two other things that greatly effect SCOP but havent be...
By bontwoody , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Hi All We have 2 ASHPs, Solar/Battery system and soon...
By AlanB , 1 day ago
-
@westkent OK , Interesting , Im surprised that Airsourc...
By Alfapat , 1 day ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@potatoman I raised this with Secon, and here's what th...
By Mars , 1 day ago
-
RE: Smart meter installation – seamless or a potential nightmare?
@transparent, now hosted on our site as attached.
By Mars , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
That's actually not too bad, or, to put it another way,...
By cathodeRay , 2 days ago
-
RE: Air source heat pump roll call
Ecodan PUZ-WM85VAA1.7 slimline Stelrad Softline Comp...
By Westkent , 2 days ago
-
RE: Baffled by heat pump size/ choice!
Try reducing the DHW hysteresis setting and schedule th...
By JohnR , 3 days ago
-
RE: Vaillant ASHP Weather Compensation with Octopus Cosy
Your Sensocomfort is the thermostat and it does work as...
By Judith , 3 days ago
-
@raiph I apologise for my incorrect assumption. A PWM p...
By Mike H , 3 days ago
-
RE: Should We Rethink the Name “Heat Pump” for Homeowners?
Not sure you need the "re". Caleferator sounds fine to...
By downfield , 3 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
Thanks for this Mars. I've actually found out the issue...
By dnagre , 4 days ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
The ASHP, just like a boiler, can supply water at only ...
By JamesPa , 4 days ago
Latest Topics
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 2 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 2 days ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 5 days ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 6 days ago
-
By R0y124 6 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 7 days ago
-
By TheHolyHeatPump 1 week ago
-
Flow temperature- At what point?
By Westkent 1 week ago
-
Excessive performance/system issues with GSHP
By didjerama_uk 1 week ago