Ecodan 8.5kW ASHP - 320L DHW Tank
Hello
I have a Ecodan 8.5kW ASHP with a 320L Water Tank. I have tried to set the water to heat for 120 minutes at 2.30am and it does reaching the target temp of 49 degrees. Wife had a shower at 6.30am (5-7 Minutes) and then I went for a shower at 7.30 and these was only luke warm water. Heated water again on demand and went for a shower. Tank temp showed 48 degrees after an hour. After dinner at 7pm we were washing the dishes and half way through we ran out of hot water.
Re-circulating pump was switch off a few days ago but this has made no difference.
What could be the cause of this. Im sure 320L should last for a day and im sure it should do more then a shower and washing up.
Currently running the ASHP to heat after a temp drop of 10 degrees so it heats as soon as we go for a shower.
I notice as soon as the shower turned on the temp drops within minutes on the hourly chart on the MELCloud App.
I have the same problem
i heat at night on cheap tariff but one shower and temp drop from 48 to 18
I suppose that the first thing would be to quantify how much electrical energy is being used during the DHW heating cycle, since this should provide a measure of how much thermal energy is being supplied.
If the electrical energy usage is low, then check the position of the temperature sensor fitted in the side of the hot water cylinder, also ensure that the sensor is making good thermal contact inside the sensor pocket.
If electrical energy usage is high, you will need to discover where the thermal energy is going.
Do you have a anti-stratification pump on your hot water cylinder? If so, is it running whilst the cylinder is being heated?
Where is your mains water supply pipe connected to the hot water cylinder? When you draw off hot water from the cylinder the outlet pipe should be at the top of the cylinder, with the mains supply being located near the base. Is this correct?
@derek-m attached a screen shot of what happens when someone goes for a shower. Takes about an 1 hour and 15 minutes to heat the tank on average from the heat pump. Not sure how much energy was used.
We have a Temp sensor in the lower part of the tank. There is only one place for this to go in. Goes in all the way and seems to be reading correctly.
Hot water comes out the top pipe and the cold water plus if on the recirculated water goes in the bottom of the cylinder.
The fact that the temperature sensor is located in the bottom section of the tank will be the reason why the reading plummets. There should still be plenty of hot water in the rest of the tank.
@ambaz79 You can query Melcloud under Energy Usage and specify just one day and see pie charts of the energy consumed and generated for heating and hot water. It only gives figures for consumed energy, though there are ways to see other figures using MelCloud in a browser window. 75 mins seems a reasonable time to complete a reheat, especially on a large tank.
Unless it is an optical distortion you seem to have a portion of the tank above the hot water draw, the hottest water you can never use! Try putting your hand on the various pipes entering the tank and see how warm they are - you have a number of uninsulated pieces of copper connected. A couple of hours after the HW cycle has finished you would hope those flow and return pipes would be cool as they are uninsulated but if they are still warm then this might show they are conducting heat back out of the tank.
Possibly check the cold supply pipe too, though in this case I wonder about the effect of the recirculation loop that joins it. Even though you are not now actively pumping the hot water round, which will destratify the tank and make it all increasingly (decreasingly?) tepid, it is still a loop through which the hot water within could cool and sink into the bottom of the tank drawing more hot water out of the top. I am not certain but I think the pump will still allow water to flow through even when it is not actively pumping.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Turns out my son was going for a shower for over 20 minutes after school. This was emptying the tank. I've kept the Circulating Pump off and might just remove it. I've set the tank to warn once at night and once in the day. Also districts my sons shower to less than 10 minutes. Not sure this is being fully followed though! We are getting through 24 hours with just 2 cylinder head ups. Thanks for all your help on this.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 139 Online
- 5,673 Members
Podcast Picks
Latest Posts
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 4 minutes ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 5 minutes ago
-
Engineer has been. Prob air locks....undid a few things...
By Profzarkov , 1 hour ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 3 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 5 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 6 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 8 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 18 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 3 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 3 days ago