Ecodan 6kW - is it "cycling", or normal operation?
Posted by: @transparentWhat do you think @jamespa ?
It does sound like the house has a large thermal lag. Bear in mind that the thermal lag of the house can be long even if the radiators can cool quickly, this is as much (actually more) about the house as it is about the emitters.
I can see how any whole-house control loop can realistically deal both with solar gain (which @clockworks mentions) and a house with long thermal lag, unless it has a model of the house and individual control over each emitter (and even then it might be impossible). I also dont know what thermal lag/range of thermal lags autoadapt control loops assume to be honest.
I disabled room influence/autoadapt on my Vaillant a few days after it was installed, and have it running on pure, open loop, WC. The result is much more stable than with room influence enabled and much, much more stable than my boiler ever was. I have one room where solar gain is a 'problem' (is free energy ever a problem?), the radiator in that room happens to be a fancoil so it turns off the fan of its own accord, if it weren't a fancoil I would probably fit a TRC acting as a limiter.
I haven't followed this thread in full but I understand that the tweaking is principally designed to reduce cycling. The problem with that is simple, if the house loss at any given temperature is less than the minimum output of the heat pump, the heat pump has to cycle whatever you do with it. You can 'tweak' the frequency by playing with controls, but not the duty ratio. Looking at the plot posted upthread this appears to show a time when the loss only just exceeds the minimum output; the duty cycle isn't that much less than 100%.
If the house has a long thermal lag then part time heating might turn out to be more efficient when it would otherwise cycle. Otherwise Id personally leave it to do its thing without trying to bend the control algorithms built into the machine. There is probably an adjustable 'min cycle time' parameter which could be turned up if short cycling is common and personally I would change that rather than trying to get some external controller/thermostat to do the job. Best generally to keep these things as simple as possible.
There is a setting for "room temp control interval", but I'm not sure if this just applies in AA mode for reading the wireless sensor, or whether it applies in all modes for any thermostat switching.
It's been running along steadily in AA mode since about 7am, basically tracking the outdoor temp as it steadily rose. It's still cycling just as much as it did in WC mode though - once the OAT is steady.
It really does look like my cycling issue is just down to the relatively high minimum output of the heatpump being over the heat requirement of my house.
I think I'll go back to WC mode. Hopefully I can leave the wireless remote connected so that it can be used to nudge the operating temperature up or down with the buttons, but it'll be out of the feedback loop, and not try switching off the heatpump?
In WC mode, I could just set the curve a couple of degrees higher than necessary, and use the Evohome controller to limit the rooms and drop the call for heat if the rooms are all too warm. The Evohome seems to operate at +/- 0.5 hysteresis, so finer control than the Mitsubishi wireless remote. It's also limited to a maximum of 3 cycles per hour, and will respond by switching on when just one room drops 0.5 degrees below target.
I've currently got 2 big rads open all the time, and could increase that to 3 without compromising the way the Evohome works. Still the danger of cycling as the heatpump hits target temp - hence turning it up higher than necessary.
I know this is not how it's supposed to operate, but it might be the most economical way to get stable temperatures and the least amount of cycling. Run harder, 50% duty cycle, and a startup every hour or two, rather than every 20 minutes.
Posted by: @clockworksI know this is not how it's supposed to operate, but it might be the most economical way to get stable temperatures and the least amount of cycling. Run harder, 50% duty cycle, and a startup every hour or two, rather than every 20 minutes
The plot you posted was more like 80% duty cycle, unless you also increase flow temperature (compromising efficiency) then you cant, at the outdoor temperature of the plot, achieve 50%. Whatever you do duty cycle has to be able to vary from 0% to 100% to match the load.
I hope I wont offend if I ask - are you sure you arent over-thinking this and that you wouldn't be better just letting the heat pump controller do what it should be good at? Do you actually have any evidence its a problem? All heat pumps cycle at least some of the time and, given that they have a modulation ratio of 3:1 at best, even one that is perfectly matched to the load will only not cycle between about 4C (below that it cycles due to defrost) and about 12C.
@clockworks @transparent wrt thermal inertia - the control parameter I mentioned which I have been tweeking for my own installation (see previous post in this thread) is specifically relevant to this.
Ref: fine tuning heat pumps See 'Kelvin minutes'. In case that's useful.
I appreciate this is Stiebel Eltron, not Mitsubishi, but do you have access to Mitsubishi technical support? To see how they do this?
I would very much agree that less is more wtr controls. I only use WC. No room controls. All zones / TRVs etc are fully open. My kitchen has high solar gain and is one of best insulated rooms in the house - so I compensate for that through balancing the system, ie, reduced flow rate for the kitchen UFH which effectively reduces the heat output.
I'm pretty sure that I am overthinking it. It's just that so many people say " low and slow, cycling is bad", etc.
If by that, they actually mean "leave it alone, don't keep switching it on and off with the thermostat " then I've got the wrong end of the stick. I do tend towards fixating a little.
If the heatpump is designed to tolerate cycling every 20 minutes unless it's cold outside, then I'll be quite happy to leave it to get on with it.
I'm happy with how evenly warm the house is, and with how much it's costing to run. Better than my old oil boiler, and not costing much more.
Basically, I'm looking for reassurance that it's all OK, and there's nothing to worry about.
Posted by: @clockworksI'm pretty sure that I am overthinking it. It's just that so many people say " low and slow, cycling is bad", etc.
If by that, they actually mean "leave it alone, don't keep switching it on and off with the thermostat " then I've got the wrong end of the stick. I do tend towards fixating a little.
If the heatpump is designed to tolerate cycling every 20 minutes unless it's cold outside, then I'll be quite happy to leave it to get on with it.
I'm happy with how evenly warm the house is, and with how much it's costing to run. Better than my old oil boiler, and not costing much more.
Basically, I'm looking for reassurance that it's all OK, and there's nothing to worry about.
All heat pumps cycle, in fact the 'non-cycling' temperature window is quite small even if the heat pump is perfectly matched to the house. Because the typical modulation ration is at best 1 in 3 and below 4C cycling will occur due to defrost, running without cycling between say 4C and say 12C is about as much as you can realistically expect and I would be willing to bet the window is smaller than that for a majority of installations.
Listen to your fridge, its on and off all day. Same technology. How often do fridges fail?
Obviously Im not in a position to make promises but I genuinely don't think you have much to worry about!
Count me reassured .
I'll switch back to WC mode, and remove the wireless remote if necessary.
I'm reasonably confident that once I've replaced one slightly undersized radiator, got the hallway radiator replumbed the right way round with new valves, and topped up the insulation over the bathroom and lounge, the rooms will be reasonably close in rate of heatloss.
As it stands, I'm having to run a little hotter to keep the worst rooms up to temperature.
I left it in AA mode overnight, with the wireless remote set to a target temperature of 19.5, and with the Evohome TRVs limiting the temperature in most rooms.
Wireless remote in the hallway, and the hallway radiator "open".
Heating schedule set to "off" between 20:00 and 23:30.
OAT dipped to 9 degrees, back up at 10 degrees before dawn.
When the heating came on, the flow temp started off 5 degrees above the WC curve. That's fine, it "knew" the house needed more heat to make up for the "off" period. This is what I want it to do - run a bit harder during the 7p hours, after being off for 3.5 hours when it's 27p kWH.
By the time I got up just before 7, all the rooms were within 0.5 degrees of the setpoint, and everything was stable.
The graphs posted show that AA mode is actually working - as long as the target temp is very close to the actual temp, and the OAT is stable. The flow temp is up and down a little, and it looks like it's being controlled by the compressor duty cycle - same 20 minute cycles, but with much longer "off" periods than when in pure WC mode (a fixed 4 minutes)
Interesting little "blips" on the power consumption graph. Looks
like it fires up the pumps after being idle for a few minutes, checks the temps, and then starts the compressor.
I'll leave it alone for a few days, and see how it copes with swings in OAT. I'm not sure if it went crazy yesterday morning because the OAT dropped rapidly, or because I had the target temp set at 20 degrees - a temperature the hallway was realistically never going to reach.
I'm seriously impressed with the cost so far today - 80p and 6.26kWH since midnight, and that includes DHW up to 49 degrees.
- 21 Forums
- 1,875 Topics
- 40.9 K Posts
- 26 Online
- 2,196 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Rob is here to help!
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
Latest Posts
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
I didn’t hear any problem with that noise it was less t...
By Judith , 7 hours ago
-
RE: New Project! ASHP, Solar PV + Battery, MVHR!
@editor yes please Mars, that would be fantastic.
By nickmorgan , 8 hours ago
-
Struggling to Find a Top Heat Pump Installer? We Can Connect You With the Best Installers in the UK
We know from homeowner’s posts and emails how stressful...
By Mars , 9 hours ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathoderay Our 01.00 to 06.00 electricity tariff is go...
By Cathyem1 , 9 hours ago
-
-
RE: Recommendation for Consultants in West Yorkshire for 1850's House Installation
Welcome to the forums. I’ll connect you some recommende...
By Mars , 10 hours ago
-
RE: Large ASHP recommendations for listed house
I’ll connect you via email (using the email address you...
By Mars , 10 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
An update - got through to a helpful Octopus employee, ...
By samiebon1 , 11 hours ago
-
There should be no significant change in the load on th...
By JohnR , 12 hours ago
-
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
@ajbevster If it's fully pushed in yes, better if it...
By JamesPa , 12 hours ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
@heatgeek Thank you, yes this is quite a meal and I'...
By Uk_pete_2000 , 13 hours ago
-
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Its the actual flow rate, after you have bypassed the b...
By JamesPa , 16 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@lokisam Thank you for reply. I have posted here bef...
By Dwynwen , 18 hours ago
-
RE: Is My Midea Heat Pump Inherently Defective?
Absolutely, I am very aware of that! Moving to a fan co...
By cathodeRay , 20 hours ago
-
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@odynsfee Hi, I only just saw your post. Sorry to hear ...
By Lokisam , 1 day ago
-
RE: Best way to heat and store hot water with ASHP and Solar - am I being stupid?
@nickmorgan you’re absolutely spot on with your thinkin...
By Mars , 1 day ago
-
RE: Grant Aerona3 with Octopus Cosy tariff
Unless I completely misunderstood you (in which case ap...
By JamesPa , 2 days ago
Latest Topics
-
By bretix 15 hours ago
-
Large ASHP recommendations for listed house
By Greenlover75 17 hours ago
-
VisitaHeatPump Participants - Guidance Please
By Toodles 2 days ago
-
By KundK 2 days ago
-
Pipes and cables exposed on roof
By MichelleC 2 days ago
-
By Silverkop 3 days ago
-
Baxi Air Source Heat Pump tips and tricks please
By Cathyem1 3 days ago