Ecodan 14kw - DHW COP
Hi all
I wondered what sort of DHW COP others are getting from their Ecodan's? We have the combined system with the pre-plumbed cylinder and over the summer have had the room heating switched off so only the DHW is working. In July and August we have only been getting a COP of c. 1.9 heating the water to 45-47 degrees. Does this seem right? Feels low to me?
Thx
Posted by: @hjdHi all
I wondered what sort of DHW COP others are getting from their Ecodan's? We have the combined system with the pre-plumbed cylinder and over the summer have had the room heating switched off so only the DHW is working. In July and August we have only been getting a COP of c. 1.9 heating the water to 45-47 degrees. Does this seem right? Feels low to me?
Thx
About 2.1-2.2 for me. 14kWh Ecodan and external HW tank.
I think it depends how you have it set up and your HW usage. If you heat your HW once a day at the warmest time of day and use a lot of HW the COP will be better because the ASHP will have a chance to get going and run for a while in steady state. If it's constantly topping up every time you wash your hands then it's going to be doing a lot of cold starts, which is inefficient. At least when you do this in the winter, the flow is already 40C or whatever, in the summer the flow starts at room temp. The ASHP uses a lot of power from a cold start, more when the flow is colder.
The other thing to be aware of is that even though your tank is set at 45C, the flow water will be hotter than this otherwise it would take too long to heat the tank. How much more and for how long depends on whether you use Eco or Normal settings.
Thanks Kev. That makes a lot of sense. I think part of our challenge is that we have a 300l tank but probably don't use lots of it. Thus it is always just running in top-up mode. I will try moving to once a day.
If you have a solar PV system, you should either install a power diverter to produce hot water, so that you do not need to run your heat pump at all. Alternatively run your heat pump to produce hot water when your solar PV is giving maximum generation. Whilst this will not actually change the recorded COP value, it will reduce your actual energy consumption, and is more environmentally friendly.
- 26 Forums
- 2,111 Topics
- 46.4 K Posts
- 42 Online
- 3,402 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
@benson It is a shame, I was looking at these when I wa...
By Grantmethestrength , 7 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 8 hours ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 8 hours ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 11 hours ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 13 hours ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 13 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
When i was looking I encountered one installer who does...
By JamesPa , 13 hours ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 3 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 4 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 5 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 5 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 5 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 5 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 5 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 6 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 6 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 1 week ago
Members Online
No online members at the moment