E121 error code on Samsung 12kw gen 6
Hi Craig,
First of all you will be using more electrical energy, since it is now colder outside. You should also be aware that electrical energy use by a heat pump is not linear with change in outside air temperature, but increases exponentially as the outside air temperature reduces. How much energy did you use?
I am assuming that the heat pump is no longer switching off for only 20 seconds?
One further interesting point is that the 'Inverter Pump' reading is now showing as 25%, which if you had a PWM controlled pump would mean that it would be running much slower. Don't change anything at the moment, but later it may be possible to try the pump on a slower speed setting.
What I don't understand is that the descriptions on the 'Master Indoor Zone Information' screen refer to an 'Indoor Unit', which you don't have in your system. I suppose it could just be that Samsung forgot to change the text in the software for the Monobloc heat pump.
Keep carrying out your tests, which I feel certain both you and others will find of use. One important thing to remember is that no two days are exactly the same, so making like for like comparisons may not always be possible.
@derek-m I had also noticed the reduction in pump speed. It also dropped to 45 when we turned of WC a few days ago.
What KW we were using is a little irrelevant as we didn't have the heating on much and it was much milder at over 10 degrees. We were using as little as 8.6 up to 15kw. Now yesterday was 20 but the outside temp has dropped again and we are on 3.6 outside temp.
The indoor unit bit threw me off aswell. I assumed it was something to do with the box on the front of the UVC.
Yes, we are no longer short cycling. Hooray. Just trying to get it to run as efficiently as possible now. I'll see tomorrow if the 2091, 2 and 3 at #3 is better or worse.
One of the difficulties I have is that we were on LPG before and on auto fill so had no real idea how much we used. We also rarely ran the boiler apart from a few hours a day when it got cold. So I've no comparison for electric Vs previous gas use.
@derek-m I've just read this article on this site
In your situation the simple answer is no.
Because your controller is showing a value of 0.0 at the moment, this indicates that your controller is solely in WC mode, and takes no account of the indoor air temperature. The thermostats can switch the heat pump on and off, but the controller will only vary the LWT dependent upon the outside air temperature.
I'm back now and having checked the energy use it seemed to run for longer and use more energy on #3 on all three settings although this could be down to outside temps as you said. I've put all three back to #2
I'm not sure if 2093 remote controller, room temp control should be the same as the others but that's what I've done so far.
@craig1980 it’s been two years since you posted on this topic. Curious to know what happened.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 23 Forums
- 2,098 Topics
- 46.2 K Posts
- 63 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Heating coming on when not required
@editor Thats correct. Its not particularly cold but th...
By bontwoody , 2 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 4 hours ago
-
RE: Pressure drop Primary circuit
Just to update you all. I made up my own fill loop as...
By ohdearism , 5 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Hmm Before doing that I would want to be certain that...
By JamesPa , 9 hours ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 9 hours ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 20 hours ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 1 day ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 1 day ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 3 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 3 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 4 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 5 days ago