Do I need separate UFH pumps?
Does anyone have a view whether the pre-plumbed CH circuit pump on the Ecodan Cylinder could manage the full UFH circuits itself? At present we have pumps on the ufh manifolds on ground and first floor. They are activated from the room thermostats and run 24/7 at the moment regardless of whether the Auto Adaption has the system running or not. (Because the room thermostats are set to call for heat constantly). I am wondering whether I could a) get these pumps removed completely or b) get them rewired so that the Ecodan switches them on rather than the room thermostats.
Posted by: @hjdDoes anyone have a view whether the pre-plumbed CH circuit pump on the Ecodan Cylinder could manage the full UFH circuits itself? At present we have pumps on the ufh manifolds on ground and first floor. They are activated from the room thermostats and run 24/7 at the moment regardless of whether the Auto Adaption has the system running or not. (Because the room thermostats are set to call for heat constantly). I am wondering whether I could a) get these pumps removed completely or b) get them rewired so that the Ecodan switches them on rather than the room thermostats.
Do you have the FTC6 manual? Page 8 shows options for zones and pumps. It looks like you can run 2 zones without external pumps but only if both are at the same temperature.
I thought my pumps only ran when the room stats are calling for heat and the ASHP is below target flow temp. I.e. even though my stats are turned up to 30 deg, the pumps are not running 24x7. I think mine is set up a bit like this.
The pump only runs when the ASHP controller tells it to. All the room stats do is open and close the motorised valves. I do have 2 external pumps but I think they are common to my zones, i.e, one does flow for both zones and the other is return for both zones.
I'm still trying to work out how auto adaptation works in my 2 zones. I think I know now but I'm not sure ...
Sheesh - these instruction manuals are (too) complex. I've just looked at the FTC6 diagrams which @kev-m refers to. It's written to give you lots of possible options rather than explaining why each one might be preferable under particular circumstances.
It's like going to an Indian restaurant with no English translation on the menu, but a photo of each dish instead. Then you're trying to work out how 'hot' is each option 😓
@hjd may I ask some basic questions, the answers to which might better get us to the answer you're really seeking.
And I'll state up front, I'm driving two UFH manifolds from a thermal store rather than directly from a HP, as you are. But mine is a DIY installation which 'evolved' as I gradually understood the principles.
1: Did your manifolds each come in a package that included a pump? Or did the installer do some flow calculations and suggest that you needed a pump for each floor?
2: Does each UFH loop connected to a manifold have its own 'motorised' valve operated by a zone-thermostat for that room?
3: Are these pumps really running full-on 24/7 or do they alter speed (modulate) according to the number of ufh zone-valves which are open? Most modern pumps are modulated, using a sensor to measure the pressure on their output.
4: Why are your room thermostats set to call for heat constantly? Do they also have an inbuilt time-clock to ask for lower temperatures at night, for example?
5: The longer the floor-loop, the slower the water will pass through it. So my smaller loops will initially take more of the flow, but then switch off their zone-valve sooner when that room/zone reaches the set temp. Do you have a rough idea of the lengths of your UFH loops?
6: (referring to a comment from @kev-m) Are you happy that all your UFH circuits are receiving water at the same temperature? Mine do, despite the floor construction differing. Do have a read-out of what temperature the flow-pipe is running at?
7: Before considering whether to get the manifold pumps removed (or controlled by the Ecodan), are they possibly configured such that their operation also mixes return-water with flow-water in order to lower the temperature? This is a common feature of manifolds with combined pumps which are to feed water to wooden floors. The flow might be too hot which risks warping the wood, so some of the return-water is mixed back in.
You don't need to answer each question.
They're there so that you can think through what you want to achieve logically. Only then do we go to the instruction manual to see how it can be achieved.
Nor do we mind if your responses then alter your original question. This is a discussion forum. We're all free to change our mind as we think through a problem!
Save energy... recycle electrons!
Hey - thanks for the detailed reply and your questions, which I have tried to answer below. I've also done a bit more reading up about the Emmetti manifolds and wiring centre and it seems like they are configured by design for the pumps to be triggered by the manifold valve opening - so it probably is working correctly. Ultimately, I guess the impact over the 5 months a year when the heating is on, is relatively limited vs the cost of running the HP!
----------------------------------------------------
Sheesh - these instruction manuals are (too) complex. I've just looked at the FTC6 diagrams which @kev-m refers to. It's written to give you lots of possible options rather than explaining why each one might be preferable under particular circumstances.
It's like going to an Indian restaurant with no English translation on the menu, but a photo of each dish instead. Then you're trying to work out how 'hot' is each option 😓
@hjd may I ask some basic questions, the answers to which might better get us to the answer you're really seeking.
And I'll state up front, I'm driving two UFH manifolds from a thermal store rather than directly from a HP, as you are. But mine is a DIY installation which 'evolved' as I gradually understood the principles.
1: Did your manifolds each come in a package that included a pump? Or did the installer do some flow calculations and suggest that you needed a pump for each floor? They were packaged with the manifold as far as I know
2: Does each UFH loop connected to a manifold have its own 'motorised' valve operated by a zone-thermostat for that room? Yes - as soon as one activates, shortly afterwards it starts the pump and interlock's to the Ecodan cylinder
-- Attachment is not available --
3: Are these pumps really running full-on 24/7 or do they alter speed (modulate) according to the number of ufh zone-valves which are open? Most modern pumps are modulated, using a sensor to measure the pressure on their output. They are Grundfos UPMs - i think they must modulate to some extent as they go from very quiet to noisier dependent on the temp of the flow.
4: Why are your room thermostats set to call for heat constantly? Do they also have an inbuilt time-clock to ask for lower temperatures at night, for example? I turned them up to 23 degrees so that they are not overriding the auto adaption / WC managed by the Ecodan wireless contoller. I could introduce night set back.
-- Attachment is not available --
5: The longer the floor-loop, the slower the water will pass through it. So my smaller loops will initially take more of the flow, but then switch off their zone-valve sooner when that room/zone reaches the set temp. Do you have a rough idea of the lengths of your UFH loops? I don't really although I could probably estimate it based on room size and distance from manifold.
-- Attachment is not available --
6: (referring to a comment from @kev-m) Are you happy that all your UFH circuits are receiving water at the same temperature? Mine do, despite the floor construction differing. Do have a read-out of what temperature the flow-pipe is running at? I think they probably do. A couple of rooms are c. 1 degree colder than others (but I think the manifold flow rate adjusters are set slightly differently).
7: Before considering whether to get the manifold pumps removed (or controlled by the Ecodan), are they possibly configured such that their operation also mixes return-water with flow-water in order to lower the temperature? This is a common feature of manifolds with combined pumps which are to feed water to wooden floors. The flow might be too hot which risks warping the wood, so some of the return-water is mixed back in. I don't think there is any mixing going on as there is not a thermostatic valve on the manifold.
You don't need to answer each question.
They're there so that you can think through what you want to achieve logically. Only then do we go to the instruction manual to see how it can be achieved.
Nor do we mind if your responses then alter your original question. This is a discussion forum. We're all free to change our mind as we think through a problem!
Thanks @hjd - this is becoming a bit clearer now.
Posted by: @hjdDoes each UFH loop connected to a manifold have its own 'motorised' valve operated by a zone-thermostat for that room? Yes - as soon as one activates, shortly afterwards it starts the pump and interlock's to the Ecodan cylinder
I think that's the key point.
It seems that the UFH manifold, associated pump and the room thermostats are all operating as intended. I think they need to be left as at present.
That leaves the outstanding issue to be how the Ecodan and its WC should be configured. Leaving the room 'stats set to 23degC shouldn't be the answer!
It's possible that your system needs a buffer-tank (or store) to allow the heat-pump to continue operating within its design envelope. Alternatively, the 'interlock' back to the Ecodan controller might not be implemented as it should've been.
Those are points which are better picked up by those with experience of WC parameters. Have you read the ongoing discussion involving WC configuration and related matters over on the topic 12kW Samsung short cycling? The best HP experts on this forum are all piling in there!
Save energy... recycle electrons!
Posted by: @hjdDoes anyone have a view whether the pre-plumbed CH circuit pump on the Ecodan Cylinder could manage the full UFH circuits itself? At present we have pumps on the ufh manifolds on ground and first floor. They are activated from the room thermostats and run 24/7 at the moment regardless of whether the Auto Adaption has the system running or not. (Because the room thermostats are set to call for heat constantly). I am wondering whether I could a) get these pumps removed completely or b) get them rewired so that the Ecodan switches them on rather than the room thermostats.
Is your heating system totally UFH or do you have any radiators?
The fact that the additional water pumps came as part of the UFH package, would indicate that they are required for mixing the warm supply and cold return.
If you have radiators in one section of your home, then the Ecodan auto adaptation controller should be located in that area. The thermostats for the UFH should therefore be used to control the temperature in their sections of your home, so should be lowered from the present 23C setting.
Do you have zone valves and if so how many?
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 60 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 5 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 12 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 1 hour ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 3 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 14 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 17 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 18 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 21 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 22 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 23 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 3 hours ago
-
SolarPV tables / online calculator
By MichelleC 10 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 22 hours ago
-
By Toodles 2 days ago