Do I need a bigger volumizer: 8kW Daikin Altherma R32 LT split
Posted by: @rgledhillThanks... I've wondered from day one why it's there.
To suck out energy largely, which it appears to be doing rather well
And to cope with the possibility all your rads are shut down.
I have heard on here and elsewhere of some poor setups, this takes the biscuit.
You will almost certainly be better off bypassing or removing the secondary pump, and bypassing the llh on the flow side so that it becomes a small volumiser in the return. If you do this you need to ensure at least one rad is guaranteed to be open, or fit a pressure activated bypass.
Then please do what @derek-m suggests to re-baseline how the system operates.
But also please note that this is not professional advice just ideas to be tried at your own risk, as we still don't have a system diagram so there may yet be hidden reasons to do things in a particular way.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
That's my suspicion too. We do have two towel rails that are permanently on and there's always the 18l volumiser!
I've dropped Daikin a message as I had the ear of their senior heating engineers, asking if removing the LLH and Grundfos pump work be better. They seem completely redundant to me...
Apologies for not drawing out a system diagram, but it's literally what you see in the photo, presumably with a manifold behind the wall to drive multiple circuits to the radiators and towel rails. If there's anything else you need please let me know and I'll track it down.
the others have already said it. get rid of the pointless 1 foot long middle loop, and the LLH. you've been given a really bad design unfortunately. all its doing is adding complexity and energy loss. its impossible to diagnose and improve your system the way its currently built. don't fit a pressure activated bypass. Just make sure you have always on rads.
also, investigate whether daikin has the capability to report on flow rate and temperatures on the "right hand side" of the indoor units heat exchanger. Other daikin users on this forum may know. If not, fit a heat meter (flow rate and flow/return temp gauge) into the CH side loop. Ideally one that has real time logging. this will be invaluable when you try to balance and optimise the system behaviour between input and output sides of the indoor unit.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @rgledhillApologies for not drawing out a system diagram, but it's literally what you see in the photo, presumably with a manifold behind the wall to drive multiple circuits to the radiators and towel rails. If there's anything else you need please let me know and I'll track it down.
It's 'presumably' that worries me. Given how bad what we can see is, who knows what we can't see? Personally I would presume nothing given the evidence we have! Not your fault I know so no criticism of you!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A very fair point James! The trouble is that without taking up floorboards, I'm not able to see the exact pipework.
Ian, the unit has the flow rate for its internal pump to the LLH/CHW loop as well as leaving and return temperatures available from the user interface, which does help a lot.
I'm going to contact the installer to see if I can get them to come and remove the LLH and Grundfos pump.
Posted by: @rgledhillA very fair point James! The trouble is that without taking up floorboards, I'm not able to see the exact pipework.
Ian, the unit has the flow rate for its internal pump to the LLH/CHW loop as well as leaving and return temperatures available from the user interface, which does help a lot.
I'm going to contact the installer to see if I can get them to come and remove the LLH and Grundfos pump.
brilliant. so just double checking, you can you see flow rate and leaving + return temps, both sides of the HEX? if so you've got what you need to tune it once the LLH has been removed.
your installer may have put the LLH in because of concerns about evohome TRV's closing and dropping the flow rate too low. reassure them that you are aiming to run with almost all rads open all the time and that you therefore do not need an LLH and you definitely don't need a bypass valve either.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
I believe I can see all of those readings, yes. I've been using them to watch it establish and maintain the temperature differential, cycling up and down due to the overshoot setting of 4C.
Thanks for the advice for talking to the installer. I will keep this thread updated.
Thank you all!
Well, we had the low-less header and accompanying Grundfos pump removed a few weeks back. And the results... well, the system has stabilised somewhat and isn't prone to the freak COPs of <2 any more. It's more settled but we're still just getting high 2's, occasionally tipping over 3, with temperatures varying between 0-13C overall. My suspicion is that a lot of the problem is extremely poor energy measurements inside the system, such that rounding errors can cause a massive perceived swing in COP - not a lot I can do about that.
So overall at this point, I'm just going to accept that it is what it is. I've spent hours and hours on this and the bottom line is that the particular combination we have (Evohome + Daikin ASHP) is just not an efficient combination. If I effectively disable the Evohome system by setting all room temperatures to 25C and control it with the flow valves, it still doesn't help as the ASHP cycles in and out at the super-low flow temperatures needed to keep the house at a sensible temperature.
Thanks for the support and help everyone.
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
3 months ago
-
Daikin Error Code 7H05
1 year ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
1 year ago
-
Daikin COP / energy used measurement from MMI
2 years ago
-
Daikin problem
2 years ago
- 26 Forums
- 2,406 Topics
- 54.6 K Posts
- 240 Online
- 6,092 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
🤣 Well, I never managed to get the HA solis "...
By Batpred , 59 minutes ago
-
RE: Experience - New Build / Complete New Heating System
Your sap clculations should give you a heat loss figure...
By JohnnyB , 1 hour ago
-
RE: Vaillant aroTherm not heating with many faults
@editor hmmm, our engineers Rae, Craig, Naz, Rob and Ry...
By ASHP-BOBBA , 2 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
@editor Hi Mars. I totally agree with your comments. ...
By Richard24738 , 2 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Indeed! And my apologies, I should have expected you...
By Batpred , 2 hours ago
-
RE: I’m glad the cold spell is over!
@editor as a reply for this date the 6th of Jan in o...
By Nursethescreens , 3 hours ago
-
RE: Heat loss based on gas usage
@jamespa Thanks. The numbers posted above were jus...
By Bash , 4 hours ago
-
RE: Heat pump not reaching flow temperature
I would describe this as either a fault or a configurat...
By JamesPa , 4 hours ago
-
RE: Please help with the settings ecodan
@sheriff-fatman when I increase it to number 3, the ...
By nose1972 , 6 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
I forgot to mention: Octopus measured our heat loss at ...
By Toodles , 7 hours ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
Thanks Mars and thank you for reaching out to so many p...
By iotum , 8 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @davec Manufacturer: Peak Energy Mode...
By DaveC , 8 hours ago
-
RE: Rate the quality of your heat pump design and installation
Well, the guy came out, turned the heat pump to max, we...
By razz , 8 hours ago
-
Midea R32 setup and bizarre running with lengthy off periods?
Hi I am new to the world of ASHP and have just had a re...
By Countryman Helmsley , 8 hours ago
-
RE: Setback savings - fact or fiction?
Given the weather has been relatively stable, the empir...
By Batpred , 9 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor That is very kind! Thank you so much.
By johnbroome , 10 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hi I am not sure how large your house is b...
By TechnoGeek , 11 hours ago
-
RE: Predicted Heat Loss & Needs from MCS calcs vs EPC vs actual
I've been thinking along similar lines to @tim441 from ...
By Sheriff Fatman , 11 hours ago
-
Thanks, @technogeek. Good to hear about the accuracy. ...
By Majordennisbloodnok , 12 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In my case it was a very specific pattern of behaviour ...
By Sheriff Fatman , 12 hours ago