Do I need a bigger volumizer: 8kW Daikin Altherma R32 LT split
Posted by: @rgledhillThanks... I've wondered from day one why it's there.
To suck out energy largely, which it appears to be doing rather well
And to cope with the possibility all your rads are shut down.
I have heard on here and elsewhere of some poor setups, this takes the biscuit.
You will almost certainly be better off bypassing or removing the secondary pump, and bypassing the llh on the flow side so that it becomes a small volumiser in the return. If you do this you need to ensure at least one rad is guaranteed to be open, or fit a pressure activated bypass.
Then please do what @derek-m suggests to re-baseline how the system operates.
But also please note that this is not professional advice just ideas to be tried at your own risk, as we still don't have a system diagram so there may yet be hidden reasons to do things in a particular way.
That's my suspicion too. We do have two towel rails that are permanently on and there's always the 18l volumiser!
I've dropped Daikin a message as I had the ear of their senior heating engineers, asking if removing the LLH and Grundfos pump work be better. They seem completely redundant to me...
Apologies for not drawing out a system diagram, but it's literally what you see in the photo, presumably with a manifold behind the wall to drive multiple circuits to the radiators and towel rails. If there's anything else you need please let me know and I'll track it down.
the others have already said it. get rid of the pointless 1 foot long middle loop, and the LLH. you've been given a really bad design unfortunately. all its doing is adding complexity and energy loss. its impossible to diagnose and improve your system the way its currently built. don't fit a pressure activated bypass. Just make sure you have always on rads.
also, investigate whether daikin has the capability to report on flow rate and temperatures on the "right hand side" of the indoor units heat exchanger. Other daikin users on this forum may know. If not, fit a heat meter (flow rate and flow/return temp gauge) into the CH side loop. Ideally one that has real time logging. this will be invaluable when you try to balance and optimise the system behaviour between input and output sides of the indoor unit.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @rgledhillApologies for not drawing out a system diagram, but it's literally what you see in the photo, presumably with a manifold behind the wall to drive multiple circuits to the radiators and towel rails. If there's anything else you need please let me know and I'll track it down.
It's 'presumably' that worries me. Given how bad what we can see is, who knows what we can't see? Personally I would presume nothing given the evidence we have! Not your fault I know so no criticism of you!
A very fair point James! The trouble is that without taking up floorboards, I'm not able to see the exact pipework.
Ian, the unit has the flow rate for its internal pump to the LLH/CHW loop as well as leaving and return temperatures available from the user interface, which does help a lot.
I'm going to contact the installer to see if I can get them to come and remove the LLH and Grundfos pump.
Posted by: @rgledhillA very fair point James! The trouble is that without taking up floorboards, I'm not able to see the exact pipework.
Ian, the unit has the flow rate for its internal pump to the LLH/CHW loop as well as leaving and return temperatures available from the user interface, which does help a lot.
I'm going to contact the installer to see if I can get them to come and remove the LLH and Grundfos pump.
brilliant. so just double checking, you can you see flow rate and leaving + return temps, both sides of the HEX? if so you've got what you need to tune it once the LLH has been removed.
your installer may have put the LLH in because of concerns about evohome TRV's closing and dropping the flow rate too low. reassure them that you are aiming to run with almost all rads open all the time and that you therefore do not need an LLH and you definitely don't need a bypass valve either.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
I believe I can see all of those readings, yes. I've been using them to watch it establish and maintain the temperature differential, cycling up and down due to the overshoot setting of 4C.
Thanks for the advice for talking to the installer. I will keep this thread updated.
Thank you all!
Well, we had the low-less header and accompanying Grundfos pump removed a few weeks back. And the results... well, the system has stabilised somewhat and isn't prone to the freak COPs of <2 any more. It's more settled but we're still just getting high 2's, occasionally tipping over 3, with temperatures varying between 0-13C overall. My suspicion is that a lot of the problem is extremely poor energy measurements inside the system, such that rounding errors can cause a massive perceived swing in COP - not a lot I can do about that.
So overall at this point, I'm just going to accept that it is what it is. I've spent hours and hours on this and the bottom line is that the particular combination we have (Evohome + Daikin ASHP) is just not an efficient combination. If I effectively disable the Evohome system by setting all room temperatures to 25C and control it with the flow valves, it still doesn't help as the ASHP cycles in and out at the super-low flow temperatures needed to keep the house at a sensible temperature.
Thanks for the support and help everyone.
-
Daikin Error Code 7H05
2 weeks ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
2 months ago
-
Daikin COP / energy used measurement from MMI
8 months ago
-
Daikin problem
11 months ago
-
Dedicated heat meter and HP heat meter discrepency
2 years ago
- 21 Forums
- 1,751 Topics
- 37.5 K Posts
- 44 Online
- 2,040 Members
Join Us!
Latest Posts
-
RE: Samsung E911 intermittent issue
Will do and thanks for all the help!!
By NetDonkey , 4 hours ago
-
RE: Watch Where Your Installer Fits Motorised Valves
The irony of this entire situation isn’t lost on me @tr...
By Mars , 5 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
We've had our Homely for a couple of months now. Comple...
By benson , 6 hours ago
-
If all we cared about was cost per kwh of heat, we can ...
By Ringi , 7 hours ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@editor Hi, yes it does, thank you
By Potatoman , 8 hours ago
-
RE: Questions and comments about annual heat pump maintenance and servicing
@toodles mine went and it was cheaper to get another, i...
By David999 , 9 hours ago
-
RE: Agile: average import cost vs other tariffs?
I don't know if you've taken a look at all, @ianmk13, b...
By Majordennisbloodnok , 10 hours ago
-
RE: What is a considered a decent weather curve for running weather compensation?
So with a flow temp maxing at 42C, managed to get livin...
By Crimson , 11 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor I purchased both books from Amazon and read th...
By ASHP-BOBBA , 15 hours ago
-
RE: New Samsung 12KW Heat Pump Help
@mike-h Oh, I am not sure I can answer accurately, When...
By ASHP-BOBBA , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Received an email today from British Gas informing me t...
By Mike Patrick , 1 day ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
Maybe work out what brand they are and google the instr...
By Gary , 2 days ago
-
RE: The UK’s Heating Nightmare: Why Many Systems Fail Homeowners
"within a few years" is a pretty long timeframe within ...
By Transparent , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
@dunlorn Good shout that buddy will give it a go at ...
By Burtis , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@bromide Thanks for the advice, doing it once but prope...
By ChandyKris , 4 days ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I've created a separate thread to discuss WC settings a...
By Crimson , 4 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Thanks I will try that and look at results
By A E Deans , 4 days ago
-
RE: Excessive performance/system issues with GSHP
@johnr Thanks - the Buffer tank is in the integral gara...
By didjerama_uk , 4 days ago
-
RE: Do thick walls make for warm houses?
@robl Thanks, thats interesting 🙂
By bontwoody , 5 days ago
-
RE: Mitsubishi EcoDan ASHP Settings not saving.
@fez96 Who’d of thought.? 👍
By Westkent , 5 days ago
Latest Topics
-
Samsung E911 intermittent issue
By NetDonkey 3 days ago
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 7 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 1 week ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 1 week ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 2 weeks ago
-
By R0y124 2 weeks ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 2 weeks ago