Distance from house issue - Samsung 5kW ASHP
I can install a 5kW Samsung heat pump close to the house but the position is a frost hollow. It never gets a sight of the sun and the air it is drawing in is cold. Or I can position the unit about 3 or 4 metres away where it will get the winter sun so the coldest air may be a degree or two warmer.
The question is how much heat will be lost flowing through the 4 metres of pipe between the heat pump and the house? I intend to heavily insulate the pipes, i.e. much more than just the black wrappers.
Frost pockets are never a good idea!
What water flow temperature do you propose at what external air temperature? That us needed for the heat loss calculation.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
I will have to guess that it will be 45C in the depths of winter but it is more complicated than just a new install.
I intend to heat part of my house, 60sq meters, which has two ufh rooms and a large radiator, and that's it. The heat loss is about 4.5Kw.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Thanks for the video. The important sentence was that external pipework in the insulating tube loses 7watts of heat per linear metre. Making the loss on my pump 28 watts. Not a figure to lose sleep over. Thank you.
The heat loss differs depending on the pipe diameter (and flow temperature, presumably). Here are some of the numbers I could find:
15mm 7.89 W/m
22mm 9.12 W/m
28mm 10.07 W/m
35mm 11.08 W/m
This will be on the flow and return pipes so if it is 4 metres away from the house it would be 8 linear metres - still relatively low.
The advantage being that the unit is in the sun for most of the year (morning sun) so any chance of a bit of extra heat in the air might offset a bit of the heat loss through the pipes. Thanks for your help.
- 26 Forums
 - 2,265 Topics
 - 50.6 K Posts
 - 528 Online
 - 5,924 Members
 
Join Us!
Podcast Picks
Latest Posts
- 
                        
RE: Oil Boiler & Heat Pump Hybrid System
thanks for your reply, tried to explain that tenants fo...
By paultheheating , 1 hour ago
 - 
                        
RE: Help me keep the faith with my air source heat pump installation
@jamespa I contacted the installer and asked them to ba...
By AdamK , 6 hours ago
 - 
                        
RE: UFH downstairs and radiators upstairs balancing question
@walnut-tree-cottage My bad, sorry I transpose while tr...
By ASHP-BOBBA , 7 hours ago
 - 
                        
RE: Who has a V2G EV installation
They certainly look stylish! But it seems that Ander...
By Batpred , 8 hours ago
 - 
                        
                                RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
And if MCS don’t have one on record that’s an issue bec...
By Mars , 8 hours ago
 - 
                        
                                RE: My DIY Heat Pump installation
@polar-bear, I take my hat off to you. I wish I had the...
By Mars , 8 hours ago
 - 
                        
                                RE: Electricity price predictions
One persons view In sync with the Nesta figures s...
By Jeff , 10 hours ago
 - 
                        
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 12 hours ago
 - 
                        
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 19 hours ago
 - 
                        
                                RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 22 hours ago
 - 
                        
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 1 day ago
 - 
                        
                                RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 2 days ago
 - 
                        
                                @old_scientist I dont monitor the tank temperature but ...
By bontwoody , 2 days ago
 - 
                        
                                RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 2 days ago
 - 
                        
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 2 days ago
 - 
                        
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 2 days ago
 - 
                        
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 3 days ago
 - 
                        
                                RE: Buying large amp bidirectional RCD and RCBO
The following diagram is taken from the Meter Operator'...
By Transparent , 3 days ago
 

 