Distance from house...
 
Notifications
Clear all

Distance from house issue - Samsung 5kW ASHP

7 Posts
4 Users
0 Reactions
390 Views
(@jswhite)
Estimable Member Member
279 kWhs
Joined: 3 years ago
Posts: 31
Topic starter  

I can install a 5kW Samsung heat pump close to the house but the position is a frost hollow. It never gets a sight of the sun and the air it is drawing in is cold. Or I can position the unit about 3 or 4 metres away where it will get the winter sun so the coldest air may be a degree or two warmer.

The question is how much heat will be lost flowing through the 4 metres of pipe between the heat pump and the house? I intend to heavily insulate the pipes, i.e. much more than just the black wrappers.

This topic was modified 4 months ago by Mars

   
Quote
(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

Frost pockets are never a good idea!

What water flow temperature do you propose at what external air temperature? That us needed for the heat loss calculation.

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
ReplyQuote
(@jswhite)
Estimable Member Member
279 kWhs
Joined: 3 years ago
Posts: 31
Topic starter  

I will have to guess that it will be 45C in the depths of winter but it is more complicated than just a new install.
I intend to heat part of my house, 60sq meters, which has two ufh rooms and a large radiator, and that's it. The heat loss is about 4.5Kw.


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5002 kWhs
Joined: 3 years ago
Posts: 737
 

@jswhite

have a look at this if you are worried about the pipe distance 🙂

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@jswhite)
Estimable Member Member
279 kWhs
Joined: 3 years ago
Posts: 31
Topic starter  

Thanks for the video. The important sentence was that external pipework in the insulating tube loses 7watts of heat per linear metre. Making the loss on my pump 28 watts. Not a figure to lose sleep over. Thank you.


   
ReplyQuote
(@dorkypark)
Active Member Member
81 kWhs
Joined: 6 months ago
Posts: 9
 

The heat loss differs depending on the pipe diameter (and flow temperature, presumably). Here are some of the numbers I could find:

15mm 7.89 W/m
22mm 9.12 W/m
28mm 10.07 W/m
35mm 11.08 W/m

This will be on the flow and return pipes so if it is 4 metres away from the house it would be 8 linear metres - still relatively low.


   
ReplyQuote



(@jswhite)
Estimable Member Member
279 kWhs
Joined: 3 years ago
Posts: 31
Topic starter  

The advantage being that the unit is in the sun for most of the year (morning sun) so any chance of a bit of extra heat in the air might offset a bit of the heat loss through the pipes.  Thanks for your help.


   
ReplyQuote



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security