Dedicated heat meter and HP heat meter discrepency
Hi all,
I have a Daikin Altherma 3 split, 16kW (EPGA16DV) which was installed back in 2020. Since then, I've been periodically keeping track of the energy usage, that it and the external heat / electricity meters report. I'm seeing a significant discrepancy in the results from the heat meter, and I'm wondering if anyone has seen anything similar or has any suggestions.
The original heat meter was showing around about half the heat produced compared to what the Daikin unit reports. I reported this issue to the installers and after a lot of back and forth, last year they installed a different heat meter. It is closer, but still there is a significant disparity. For example, over the last month the heat meter reports 1458kWh while the Daikin reports 2065kWh (diff compared to last month's readings). The electricity meters are much closer showing 839kWh (EM1) to 805kWh (Daikin). Which reading is used, significantly impacts SCoP: 1.74 if using the external meters and 2.57 if using the Daikin readings.
An SCoP of 2.57 seems low, but it was cold at the start of the month. 1.74 however seems terrible.
I don't know what to do now. I've asked the installers many times, but they just say that the flow calculations show it operating at 400%. That is not reflected in the SCoP at all.
Any ideas, thoughts, suggestions welcome!
Allan
Posted by: @theallanHi all,
I have a Daikin Altherma 3 split, 16kW (EPGA16DV) which was installed back in 2020. Since then, I've been periodically keeping track of the energy usage, that it and the external heat / electricity meters report. I'm seeing a significant discrepancy in the results from the heat meter, and I'm wondering if anyone has seen anything similar or has any suggestions.
The original heat meter was showing around about half the heat produced compared to what the Daikin unit reports. I reported this issue to the installers and after a lot of back and forth, last year they installed a different heat meter. It is closer, but still there is a significant disparity. For example, over the last month the heat meter reports 1458kWh while the Daikin reports 2065kWh (diff compared to last month's readings). The electricity meters are much closer showing 839kWh (EM1) to 805kWh (Daikin). Which reading is used, significantly impacts SCoP: 1.74 if using the external meters and 2.57 if using the Daikin readings.
An SCoP of 2.57 seems low, but it was cold at the start of the month. 1.74 however seems terrible.
I don't know what to do now. I've asked the installers many times, but they just say that the flow calculations show it operating at 400%. That is not reflected in the SCoP at all.
Any ideas, thoughts, suggestions welcome!
Allan
If correctly installed, I would expect the external heat meter to be the more accurate. Please provide photo's, both distance and closeup, of your installation.
Absolutely! One shot of the internal part of the split HP + buffer tank, close up of the heat meter, and one of the DHW tank.
I don't have a schematic of the piping, but I can draw one up if it would be useful.
I'd expect the external meters to be more accurate as well, which is what really bothers me about the SCoP.
Thanks,
Allan
Where are the temperature sensors associated with the heat meter, are they in pockets or clipped to the pipework? Are the temperature sensors making good thermal contact and are they and the pipework adequately insulated?
Where are the temperature sensors measuring the LWT and RWT, and flow meter connected to the heat pump controller?
Low COP can be caused by flow and return water mixing within the buffer tank. What are the temperatures on the pipes going in and out of the buffer?
Hi,
Thanks so much for your help and insight with this! Attached are photos showing the layout of the heat meter and close ups of its two temperature sensors in the pipes. They both appear to be firmly embedded and secure.
This morning I took some readings from the heat meter and the equivalent from the Daikin:
- Heat meter:
- Delta temp: 2.56C (leaving water: 40.6C, inlet 38.1C)
- Flow rate: 1.364 m^3/h
- Daikin:
- Delta temp: 3.9C (leaving water: 40.9C, inlet 37.0C) - the Daikin also has a Leaving water PHE which was 41.5C - I think that's the water temp on the heat exchanger plate?
- Flow rate: 1.332 (on screen as 22.2l/min)
- Analogue meters on manifold:
- Delta temp: 3C (flow: 36C, return 33C)
One thing I did find interesting is that while looking at the numbers on the heat meter over night, the delta went negative a number of times. Only about -0.5C, but I hadn't expected that. The largest delta I saw was +4.6C.
Allan
@theallan I'd definitely suggest you draw a schematic to help us understand, the overall layout and where the metering points are. that may start to give some clues why the meter readings are different.
negative DT will happen hen the circulation pump is running but the heat pump is not heating. RWT can be higher than LWT in that situation. that will happen during defrost, or at any point when the heatpump's compressor has shutdown, but its still keeping the circulation pump running, as part of its normal cycle of control.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@Dandee - No I hadn't thought of that - the readings above were while calling for space heating. Do you mean to just disable the call for heat and DHW production?
@iancalderbank - Thanks for the negative number explanation. I'll draw a schematic this weekend and upload it.
As the saying goes "a picture is worth a thousand words".
The heat meter temperature sensors are indeed in pockets, and if correctly installed will hopefully be making good thermal contact. Measuring temperature accurately is not as easy as many may think, since the type of sensor used will have a specified accuracy, then the electronics required to convert the sensor output into an actual reading will also have a specified accuracy. Accurate flow measurement is even more difficult to achieve.
If you were to install two identical heat meters on the same system, I am quite confident that they would not give the same reading, but the readings should be within the specified tolerance.
If you look at the data sheet for your heat meter it should give details of the specified accuracy, you could also ask Daikin what the expected accuracy of their measurements should be. If both heat energy output measuring systems are providing reasonably consistent measurements, the percentage difference between the two readings should be reasonably consistent over a period of time.
As I think has already been pointed out, the LWT and RWT readings can reverse when the heat pump performs a defrost cycle.
I suspect that the low SCOP is probably due to the way your system has been configured and is being operated. Do you have any thermostats or TRV's within your system? Are you operating the system in Weather Compensation (WC) mode or fixed LWT? If in WC mode what are the settings?
another thing to check is whether the heat meter is configured for glycol. A glycol mix has less heat energy than pure H20. My heat meter (which is similar to yours) is set to reduce output by (I think) 20% for this. Make sure you're comparing like with like. In fact my ASHP (Mitsubishi but others may be the same) has several sorts of manual adjustments and fudges you can make so it's worth checking this on yours.
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
3 months ago
-
Daikin Error Code 7H05
6 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
7 months ago
-
Daikin COP / energy used measurement from MMI
1 year ago
-
Do I need a bigger volumizer: 8kW Daikin Altherma R32 LT split
1 year ago
- 22 Forums
- 2,061 Topics
- 45.1 K Posts
- 14 Online
- 3,328 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
@editor Do you know what the current regulations are f...
By Old_Scientist , 60 minutes ago
-
RE: Say hello and introduce yourself
Yes but we have to deal for now with the world as it is...
By JamesPa , 7 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@editor Oh come on…. it’ll only take him 10 or 15 minut...
By Toodles , 20 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@westkent My present Cosy Tariff is as follows: NB....
By Toodles , 1 day ago
-
By the way, I also think our industry need to get on bo...
By ASHP-BOBBA , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
That's a curious conclusion with which I am struggling,...
By JamesPa , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
Cool sounds good
By Johnmo , 2 days ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
That's interesting, @grantmethestrength. I'm a little s...
By Majordennisbloodnok , 3 days ago
-
@allyfish That's impressive. We are on a similar journe...
By ChandyKris , 3 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Hi, good to hear. To be honest, I've given up with the ...
By Profzarkov , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
I feel like a record is on it's way this month. Scotlan...
By Andris , 4 days ago
-
RE: Discharging battery to grid whilst charging EV
@majordennisbloodnok Well, I tried it and nothing burne...
By AndrewJ , 4 days ago
-
RE: Using AI to optimise your system
@marvinator80 Two of the best resources on Youtube that...
By Grantmethestrength , 4 days ago
-
RE: Renewables & Heat Pumps in the News
@johnmo Ours is powered from solar energy (with grid ba...
By Toodles , 5 days ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
I'm curious who you think are the reluctant ears. Cert...
By JamesPa , 5 days ago
-
RE: Commencing on an ASHP Installation Process
If that is the case then I would add to my earlier post...
By JamesPa , 5 days ago
-
RE: Battery sizing - How low can you go!
The second 6.5 kWh Growatt battery was installed today....
By ChandyKris , 7 days ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Your system seems to be more modern than mine, mine was...
By abbote , 7 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 1 week ago