Daikin ASHP Installation Critique and upgrade suggestions
Hi All,
Looking for the community to comment on my ashp installation that came with the house. It is certainly unconventional in these parts in central Europe but I need to make the most of it and be comfortable in the winters.
The house is a 2 story concrete block construction with some level of insulation, about 170sqm. The last energy audit rated it as E/F on a scale of A to I. Newer triple pane windows/doors throughtout.
The professional installation is a Daikin mini split system with 2 External units (5MXS90E), ~9Kwh each, connected to 5 internal floor and ceiling mounted units each. The heated refrigerant is brought in via insulated copper tubes that wrap around the facade of the house. The whole setup is about 10 years old and has been maintained. The only issue I see is that the external unit facing the constantly windy side of the house produces about 7 liters of water condensation on humid days.
We like that in addition to heating we have cooling, fan functions, air filtration as well as individual room controls and that we are not burning any gas/oil.
I understand the house previously had electric radiators so there is no possibility of in wall water pipes etc. We also have cold floors because there is no cellar, only a 1 meter crawl space above bare ground.
The system can certainly get individual rooms comfortably up to 20c but we are not quite able to get a comfortable 20c throughout the house, specially the hallways. At the moment with temps around 2-3c the Daikin system alone is using 40-50 KWH per day at a rate of 18 euro cents per KWH. And this is with 30% of the rooms closed off / unheated.
We should test with different settings but I feel that this will take us towards 70kwh per day without still being properly comfortable.
In the short term I am focusing on hunting down air leaks and keeping the heat settings more constant (based on what I read on this forum) and keeping the pump working at a steady pace vs. up and down. I plan to get a thermal imager to find cold spots.
In the long term I plan to redo the roof and insulate it much better as well as install solar panels to take the pressure of the heating costs. Insulating the house further on the facade with hard foam insulation could also be an option. Another idea if necessary is a pellet oven to supplement the heating.
So what do you suggest for improvements? Is it time for new more efficient or larger units outside, should I replace/re-insulate the external copper tubes or do something else. Would welcome any ideas!
Hi Nick,
I would suggest that you initially concentrate on insulation and draft proofing, since if you don't need the energy in the first place, it is a win for both you and the environment.
Hi Nick and welcome to the forum. Most people here have wet central heating systems but I think one or two have similar to you. Have you done a heat loss calculation on your house and compared it to the output of your heating system? It would be useful to know how well the system matches the house.
What sort of floor do you have? From what you describe it's some sort of suspended concrete? Could you stick some insulation on the underside? I have a block and beam concrete floor and I have a layer of insulation on top. So it's ground/800mm gap/concrete block/insulation/chipboard/wood or tile. You can lose a lot of heat through an uninsulated floor.
A lot of folks on here have wood burners to help the ASHP when it's really cold.
How do you heat your water? Electricity?
Kev
Thanks Derek and Kev.
I will lookup the documents I have on heat efficiency calculations. I believe I can also contact the energy assessor or perhaps the installer for more information. In any case I will read up on heat loss calculations.
The ground floor is suspended concrete spanning the footings of the house. On top of the concrete we have a few cm's of screed and then tile and wood floors. We found some insulation when changing tiles however it did not look too intact and of insulation value. The cold floors confirm that. The idea for insulation from the underside sounds good. I can look for someone up to the job.
For hot water we have a 100 liter electric water heater with a C energy rating and annual usage of 2600KW per the label. Left on the eco 50c setting full time. We have thought about switching our baths and kitchen to instant heaters as we found this arrangement fairly efficient cost and space wise in our previous place. Showers aside, by the time the warm water arrives we are finished with the tap!
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
9 hours ago
-
Ecodan consuming 100kwh per day in new build!!!
1 week ago
-
Oversized Daikin 9kw
1 month ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
1 month ago
-
ASHP install contract and BUS grant money
1 month ago
- 22 Forums
- 2,033 Topics
- 44.3 K Posts
- 43 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
By trebor12345 , 25 minutes ago
-
The Great British Heat Pump Quiz
Whether you’re a homeowner, installer, retrofit nerd or...
By Mars , 2 hours ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
Hi @editor - thanks for your reply. A buffer tank was n...
By CBrenewable , 9 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 9 hours ago
-
RE: help sizing rads based on room by room heat loss
By JamesPa , 11 hours ago
-
Hi Thanks for the reply, the walls are being constru...
By Fingers , 12 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 13 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 17 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 17 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 17 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 18 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 22 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 1 day ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 1 day ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 1 day ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 2 days ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 2 days ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 3 days ago