Daikin Altherma 3M in Buckinghamshire - Snoring Noise
@bridgetjohn Do you mean single- pipe like the link: https://www.buildingservicesindex.co.uk/entry/136545/AEL-Heating-Solutions-Ltd/Single-or-two-pipe-central-heating-system/
Like that?
@cycleneil Hi, yes, that's what I understand. Ours is apparently single pipe and that is what is potentially causing the rushing water noise in the towel rail which links directly off the pipes in the airing cupboard before they disappear into the floorboards and service the rest of the radiators.
@bridgetjohn Oh dear. I’m surprised that the installer didn’t convert to a 2-pipe system as a routine measure, the 1-pipe systems date back to the early days of central heating and never really worked well even then.
Installer has proposed
"We have discussed your system and feel it would help if we separated the heat pump from the existing system by reconfiguring the buffer vessel to a low loss header and installing a secondary pump to the heating system. This will mean we can control the pump speed around the existing system which should in turn reduce the noise issues. "
Any thoughts?
also see above about suspected Single Pipe system. The house was built in the 70's and extended late 70's.
Thanks in advance.
@bridgetjohn that is the solution I have - see Worcestershire ASHP.
The purests would say this adds complexity and reduces efficiency. Which is probably true. Ideally you’d change radiators and reduce flow temperature.
I’m getting SCOP of 3.3 controlled via a Nest. I will change to weather compensation from end of April (after 1year ownership) to compare and hopefully improve SCOP. And my bungalow is warm with no radiator changes
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and new Hyundai Ioniq 5 N electric vehicles with Myenergi Zappi mk1 charger
Update on this. The bathroom towel rail plumbing was re-routed so that stopped that noise. The low loss header added and that reduced the flow noise in the airing cupboard.
apparently if we want to add underfloor heating downstairs we’d have had to do that anyway?
we’ve also added a bit of soundproof board to the adjacent bedroom wall but don’t know if that works yet as heating is off for summer.
just left with very large electricity bill for the two months when first installed with faulty PCB board so we had to use Booster all the time and run on leaving water temp thermostat. Really bad that Daikin supplied faulty kit and didn’t compensate us for the consequences. It’d be like buying a faulty car and getting a huge fuel bill because it was running inefficiency and then refusing to rectify it or compensate.
I don't know if this helps, but you can change the pump limitation parameter to restrict the top end pump speed. It's in Installer Settings, so you'll need to change the user profile to Installer. From there, it's under Installer Settings > Field settings table > 9-0D. Change the value from whatever it is (probably 0) to 4. This will cause the pump speed to run at a maximum of 21lpm on start up. I found the default 30lpm much too loud and found no downsides to dropping this to 21lpm (which is 60%). Since my radiators were happily warm enough at the reduced 11lpm after initial 20 minutes or so, I was fairly sure it'd be fine at 21lpm as well. Sure enough, all rads warm up nicely and maintain their heat. Virtually silent running now.
It's all in the Installer Reference Guide.
- 22 Forums
- 2,090 Topics
- 46.1 K Posts
- 22 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 7 hours ago
-
RE: Adding battery storage to SolarEdge PV system
That's concerning. I am currently looking again at the...
By JamesPa , 9 hours ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 13 hours ago
-
RE: Commencing on an ASHP Installation Process
@jamespa Your post reminded me of an interesting intera...
By Sheriff Fatman , 14 hours ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 16 hours ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 19 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
What you run the cable through will affect its current ...
By Transparent , 1 day ago
-
I don't know how to enable cooling on Daikin and @major...
By JamesPa , 2 days ago
-
My advice is reject unless they will delete the buffer ...
By JamesPa , 2 days ago
-
RE: Battery storage to run Heat Pump.
I would be surprised if the battery chemistry is going ...
By Transparent , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@dowallydrifter OK. I would recommend you read t...
By JamesPa , 2 days ago
-
RE: Solar to power Heat Pump for DHW
Wow, how big is your heat pump that it is pulling 6kW d...
By Old_Scientist , 3 days ago
-
There are DHW tanks with a built in heat pump that take...
By JamesPa , 3 days ago
-
RE: Vaillant AroTherm Plus 7kW
If the thermostat is connected to the call for heat ter...
By JamesPa , 4 days ago
-
RE: Renewables & Heat Pumps in the News
Yes I realise I'm picking this up a week late...... but...
By Transparent , 5 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay how did you get a script to run for that- d...
By benson , 5 days ago