Hi All
I have a Samsung ashp and believe the flow and return to the external condenser are mixed up. When I go into the controller parameters - for those who may be familiar - specifically E901 (water inlet) and E902 (water outlet), I have a higher reading on the inlet. Even though I believe the house is performing ‘ok’ in terms of energy usage I’m wondering would I be loosing much efficiency the way it is? - should I have it changed?
From talking to maintenance providers it seems to be a common mistake in new developments!
Appreciate any comments.
Thanks
Are you heating in June? Or is it in cooling mode? Are the sensors on external pipework or inside the unit?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Yes, probably it does matter, depending on the rest of your system. If you have a heat exchanger, it's likely using it the wrong way around, which will cost around 5degC, dropping efficiency by around 10%. If you have radiators, there should be a magnetic trap before the heatexchanger - it will be less effective at protecting the complex heat exchanging structure from black crud if it is "after" it.
The refrigerant side of the ASHP plate heat exchanger is a condenser, superheated refrigerant gas in at the top, lower pressure sub-cooled liquid out at the other bottom. It is always piped counter flow to the return (RWT) and leaving (LWT) water side connections. So that means ASHP connections are usually return in at the bottom and flow out at the top.
The flow on the water side could be piped wrong, Samsungs don't have a built in primary circulating pump. Some knuckle scraping installer could have crossed the house side primary flow and return water connections. In heating, your LWT will always be higher than your RWT.
Surprised the ASHP sensors don't register RWT > LWT and throw an error code 'incorrect flow direction' when in heating mode, but Samsung might assume, not unreasonably, no installer would be that stupid and therefore no error code is required for this. Ah, how little they know about UK installation standards!!....
Thanks for the replies! The Samsung unit has the sensors built into it and yes it would make sense for the system to raise a fault code once it sees the return temp higher than the flow! Perhaps newer units would do this! 10% efficiency loss is 10% higher bills so I will get it changed. I don’t believe there is a filter either so when I swap pipes around I will put a filter on flow to stop any dirt that’s in the system going into heat pump. The system was poorly commissioned, stats were controlling wrong zones too but that was a simple fix by swapping over valve actuators. - there’s probably a good business in the making to go around optimising poorly installed heat pump systems 😂
Posted by: @clongwill- there’s probably a good business in the making to go around optimising poorly installed heat pump systems 😂
I am seriously considering having @heacool or a Heat Geek engineer to come and have a look at my recently commissioned install.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @clongwillthere’s probably a good business in the making to go around optimising poorly installed heat pump systems 😂
There sure is, but it's not the most rewarding work going round sorting out other folks' cock-ups. If there's one thing I've learned on my domestic ASHP journey over the last 1 year, and my 30+ year journey in building services; inefficiency is due to poor design and control. An A2W ASHP will do what it's designed to do, capture heat from the outside air and transfer it to a secondary medium. It'll perform reliably as per it's rated capacity and published performance data. But from the unit water connections, the variables are in the hands of the system designer and installer. How much of that heat gets transmitted into the heated space, and how efficiently, can vary enormously. The ASHP gets the blame as that's the bit the customer assumes 'doesn't work'. Almost always the ASHP isn't the problem.
In your case, it looks like the installers didn't even get the water connections to the ASHP right, so I would get an independent expert report prepared and it will be money well spent. If it's new build under NHBC, and major issues are identified, have you any redress with the developer? Have neighbours got similar systems with identical issues?
@allyfish Surely if the water circuit was plumbed incorrectly and water was pumped the wrong way, the flow switch in the heat pump would not be activated and the heat pump would be prevented from starting?
@iaack hi again. The flow sensor is external on the system hot water cylinder on Samsung Gen6, not internal to the monobloc, so it's possible to have correct flow at the cylinder but reversed flow and return connections at the ASHP. Monoblocs with internal primary pump and flow monitoring can't have reverse flow. I think you can with the Samsung because these items are external. Given the standard and quality of some new build installs, it's quite possible!
- 22 Forums
- 2,084 Topics
- 45.9 K Posts
- 29 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 3 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I think that QR code is to download the app SmartHome o...
By cathodeRay , 9 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 12 hours ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 1 day ago
-
A good start but I’m glad I didn’t need to learn someth...
By Judith , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 1 day ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 1 day ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 2 days ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 3 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 4 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 4 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 4 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 4 days ago