Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Creative trials on Night-time Setbacks to @ faster recovery, improved comfort and even greater energy reductions.

48 Posts
10 Users
15 Reactions
18.6 K Views
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5774
Your energy: 166 kWh
 

Posted by: @sunandair
↑

If only this WC Curve setback was available as a scheduled setting as a night time setback.

For what it is worth, the way the Vaillant heat pump control works in pure wc mode (where actual room temperature is not part of the control loop) is that, when you adjust 'desired room temperature' it shifts the wc curve.  Since desired room temperature can be time programmed, this means it does exactly what you want.  

I'm actually rather surprised that mitsubishi doesn't offer a similar function, as it's generally a pretty sophisticated controller so far as i have read.  Are you certain that it doesn't in one of its modes?


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 4 years ago
Posts: 569
Your energy: 0 kWh
Topic starter  

Hi @jamespa  

There are other modes as you have queried within the Ecodan scope of operation. You may be aware of the Auto Adaptive setup. This does however use a target room temperature and a version of its own weather compensation. We have used this mode quite a lot in the past but have found it often overcompensates when recovering from a setback.  

 

Following certain shutdowns and setbacks the recovery can be quite extreme and becomes fixed as a learned recovery process. 

For us we just find AA a bit temperamental. We are currently preferring to use full weather compensation and use it’s more predictable behaviour. 

My previous  post outlined useful and efficient ways to use setbacks. But these efficiencies are only available in Weather Compensation Mode. These particular efficiencies are not available in Auto Adaptive Mode.

So, while it might be just a pipe dream, if ever a new operating system for Ecodan  was to be considered then we would certainly find scheduled Flow Temperature adjustment a useful energy saving tool. 



   
ReplyQuote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 4 years ago
Posts: 569
Your energy: 0 kWh
Topic starter  

Posted by: @sunandair
↑

Picking up this thread from last year 

Following discussion on what is missing in the controls of heat pumps I've done a trial on a different kind of setback for overnight operation which might be more efficient than simply dropping the target room temperature. 

On the Ecodan controls the only way to operate a scheduled setback is to program a temperature drop on the set temperature control. On the current system there  is no way, in weather compensation of making a setback FLOW TEMPERATURE.

Im suggesting that there is already a theoretical advantage of making a setback using flow temperature drop of say 5c and based on the widely quoted benefit of a 3% energy saving for every 1c reduction in flow temperature. This would mean a potential 15% saving on just a room temperature setback of say 2c.

But there would appear to be a second big saving which only revealed itself during the test responses from the heat pump. 

The first thing to notice in the reheat graph is the large ramp up when the room stat setback temperature is reached. This is because the HP is following the NORMAL WEATHER COMPENSATION CURVE. However this is night time. Do we need a heavy duty ramp up?

EF46B2B2 299C 4133 B4A7 1C26ACCEA975

Another costly activity of the heat pump is the defrost cycle which only takes about 5 minutes to complete but induces another ramp up and the return flow temperature takes around 25 minutes to reach its pre-defrost temperature.

E08526A3 367A 4657 B0B3 E75E8B925E14

 

The Ecodan controller has an on screen flow temp adjustment option. This simply adjusts the weather compensation curve  flow temperature up or down. So we have induced a low reaction setback by manually adjusting downwards the flow temperature to -5c.

image

The resulting lower flow resulted in a gentler start during the overnight setback. It was lowered in 2 stages from 40c down to 38c and then finally to 35c flow temp. The first graph shows the step change at 3.35am.

75E11670 850E 4906 A813 CC5D919BC5A0
D7CCA4B6 E9E7 4F50 8A8D 5C23CB7E7872
40A40080 3C8D 4815 B296 5613EE96B5A0

The last graph shows the flow temperature returned to the normal WC Curve setting. You might notice it goes straight into defrost mode when the flow temp is raised back to normal.

Here is the hidden result... 

the outside ambient temperature was 2c so we were operating with hourly defrosts.

However, by reducing the Flow Temperature the system appeared to operate below the rapid output which induces the defrost cycle.

This low flow temp adjustment of 5c off the WC Curve appears to have saved 8 defrosts. In addition to have reduced the consumption by as much as 10 to 15%. 

If only this WC Curve setback was available as a scheduled setting as a night time setback.

(resultant temp drop at 6am showed a room temp of 18.5c. This raised to 20c during normal operation by 9am)

 

 

 

Update: it looks like Daikin do exactly what I’m looking for in this post.

I’ve just seen this video done by Heat Geek… over 2 years ago. It’s at 8mins 46 seconds.

D1B5CCB1 D731 48F8 8579 A3D407C67613

To recap what I was looking for was : *While operating our Ecodan in Weather Compensation, a scheduled setback which sets the flow temperature lower rather than the room temperature lower. Reason being a room temperature setback will result in the temperature dropping then reheating at ‘full’ weather curve output until the lower room temperature is passed again. 

The Daikin system has the option of setting up a schedule for night time (or any time) where a cooler more comfortable night time is preferred. And by lowering the flow temperature say 5c this would also produce an improved energy saving over just lowering the room temperature. Even better- the room target could stay the same but by lowering the flow temperature the target room temperature will simply never be reached.

I guess you would need to play around with the flow temp drop so that the room temp only drops by 2c but it seems it can be done.

I wonder if there are any Daikin owners reading this post who use this setback feature who might shed some light on its effectiveness?

So now wondering if Mitsubishi have any plans on introducing such a control?

I’ll try and post the video.

the topic comes up at 8mins46.

 



   
ReplyQuote
 NJT
(@njt)
Trusted Member Member
Joined: 2 years ago
Posts: 59
Your energy: 0 kWh
 

@sunandair 

I've just recently started using pure weather compensation which is what you seen to be looking for. 

It's building the same weather curve, but removes the thermostat and just works on leaving water temperature that can be offset in the daily/weekly planner or via the app.

I've near enough set up right for us, with a -2 Deg offset at 9pm and reverting back to 0 at 5am



   
ReplyQuote

SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 4 years ago
Posts: 569
Your energy: 0 kWh
Topic starter  

Posted by: @njt
↑

@sunandair 

I've just recently started using pure weather compensation which is what you seen to be looking for. 

It's building the same weather curve, but removes the thermostat and just works on leaving water temperature that can be offset in the daily/weekly planner or via the app.

I've near enough set up right for us, with a -2 Deg offset at 9pm and reverting back to 0 at 5am

yes I’m already using weather compensation on our Mitsubishi but, as stated above, there isn’t a scheduled LWT setback option available. The trial I have done was by manually adjusting the flow temperature just to see how the system responded. And the graphs shown above were the results.

But I’m using an Ecodan system which doesn’t appear to have a programmable schedule for the flow temperature the schedule only appears to adjust the room set temperature.

Is your system a Daikin model or is it another make? How have you found the setback operates? Have you seen any benefits using the LWT setback? And just to clarify;  when you state -2c setback that means your schedule takes 2c off the LEaving Water temperature during the setback period? Is that right?

 

 

 

 



   
ReplyQuote
 NJT
(@njt)
Trusted Member Member
Joined: 2 years ago
Posts: 59
Your energy: 0 kWh
 

@sunandair 

Yes the -2 takes it off the LWT, and I have the Daikin 8kw

Using offset, obviously keeps the heat pump running as opposed to stop/start thermostat control, saving the 20 ish mins start up  boost that Daikin do every time it restarts before settling back to set LWT.

 

I initially tried thermostat control overnight but that's not accurate enough with Daikin (0.5 to 1.5 deg variation that can't be adjusted) 

So far so good 👍



   
Bang on
1
ReplyQuote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 4 years ago
Posts: 569
Your energy: 0 kWh
Topic starter  

That’s great to here….

im curious, If you’re putting a 2c drop on the flow temp what’s your room temperature drop at the end of the setback? (Of course this might vary from day to day)

I’ve been very impressed with the Daikin MMI controller. I’ve been helping a neighbour set up their WC curve and found it looks good and is easy to navigate.

 



   
ReplyQuote
 NJT
(@njt)
Trusted Member Member
Joined: 2 years ago
Posts: 59
Your energy: 0 kWh
 

@sunandair 

Like you say it varies dependant on OAT, but room temperature over the last week it averages 1 around 1.5 Deg drop.

This is till 4am when we heat the water cylinder that takes 45 to 60 mins to get to 48 deg and central heating obviously turns off during that period.



   
Like
1
ReplyQuote

SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 4 years ago
Posts: 569
Your energy: 0 kWh
Topic starter  

Here is an update of the setback we operate on our system.

We have created a simple schedule which copes with different night time outside temperatures. This is worth considering because if the outside temperature is particularly cold the indoor temperature will also drop lower than you might expect. So this means the morning reheat would need to start earlier in the morning to achieve a comfortable room temperature by a targeted time in the morning. 

the attached graph shows the times our schedule changes and the degree of setback. The room temperature line is the black line and in this illustration the room temperature doesn’t drop to 17C. But the temperature is below 18C at 4.30am so the HP will,start to heat at 4.30am.

IMG 0329

Conversely,  if the night time temperature was above 18C there needs to be an automated way, built into the schedule, to delay the start of the reheat of the house. This means you are not wasting energy bringing on the heating too early. So in a milder night the heating would be delayed until 6am which is the next scheduled start targeting 19C. 

The heating on our system operates in weather compensation mode which would typically overshoot the target temperature by 1C before switching into standby mode. However our weather curve is set to operate at a gentle output and only slowly attains 20C in about 3 hours.

We usually manually adjust the temperature up to 20C or 21C around mid afternoon. 

This works for us in our particular house but I think it’s fair to say differences in property characteristics, insulation influences and Heat Pump performance will vary from one property to another.

Perhaps the attached pie chart helps to show how energy can be saved during a setback. The yellow section shows how much time the HP was in freeze stat mode (in this case only activating the circulation pump to prevent the outside piped water dropping below 15C) it did this to protect the system for 4.5 hours. The red portion of the pie chart shows the heating when it was switched on at 4.30 am and  operating for the next 5 hours until the graph was created.

I hope some people will find this useful.

 

IMG 0343


   
ReplyQuote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 4 years ago
Posts: 569
Your energy: 0 kWh
Topic starter  

Here is an update of the setback we operate on our system.

We have created a simple schedule which copes with different night time outside temperatures. This is worth considering because if the outside temperature is particularly cold the indoor temperature will also drop lower than you might expect. So this means the morning reheat would need to start earlier in the morning to achieve a comfortable room temperature by a targeted time in the morning. 

the attached graph shows the times our schedule changes and the degree of setback. The room temperature line is the black line and in this illustration the room temperature doesn’t drop to 17C. But the temperature is below 18C at 4.30am so the HP will,start to heat at 4.30am.

IMG 0329

Conversely,  if the night time temperature was above 18C there needs to be an automated way, built into the schedule, to delay the start of the reheat of the house. This means you are not wasting energy bringing on the heating too early. So in a milder night the heating would be delayed until 6am which is the next scheduled start targeting 19C. 

The heating on our system operates in weather compensation mode which would typically overshoot the target temperature by 1C before switching into standby mode. However our weather curve is set to operate at a gentle output and only slowly attains 20C in about 3 hours.

We usually manually adjust the temperature up to 20C or 21C around mid afternoon. 

This works for us in our particular house but I think it’s fair to say differences in property characteristics, insulation influences and Heat Pump performance will vary from one property to another.

Perhaps the attached pie chart helps to show how energy can be saved during a setback. The yellow section shows how much time the HP was in freeze stat mode (in this case only activating the circulation pump to prevent the outside piped water dropping below 15C) it did this to protect the system for 4.5 hours. The red portion of the pie chart shows the heating when it was switched on at 4.30 am and  operating for the next 4.5 hours until the graph was created at 8.55am.

I hope some people will find this useful.

 

IMG 0343


   
ReplyQuote
(@old_scientist)
Samsung
Prominent Member Member
Joined: 2 years ago
Posts: 586
Your energy: 40 kWh
 

@sunandair we operate a very similar overnight setback with our Samsung ASHP using a 3rd party wireless programmable room thermostat.

The heat pump is oversized, and even at minimum output will output too much heat overnight unless it's below freezing outside, so a setback or switch off is almost mandatory for overnight comfort.

We have no way to schedule changes in LWT (other than WC), so that must be done manually. The room thermostat allows us to program start/stop times and set room temperatures so we can achieve similar results to yourself.

During milder weather, we simply turn off overnight and turn back on in the morning when we get up and find the house soon reheats to an acceptable minimum temperature.

During winter (below 5C) we schedule a 4am restart. We are on the Cosy tariff, and although we have a battery it makes sense to try to schedule any reheats from the grid rather than from the battery, so we normally schedule the heating to go off at midnight and to restart at 4am, although we could schedule a later start time based on room temp as you do (e.g, 4am if <17C, 5am if <18C etc) - good idea, thank you! I also manually turn the flow temps down to 30C when we go to bed and then turn them back up to 32-33C (or as required) when we get up. This has the desired effect of maintaining house temp at ~17-18C overnight and allows us to reheat to 19C in the morning. We then target 20C for the evening when we become more sedentary and require a little more heat. 

The overall effect is the indoor temp is oscillating between 17C and 20C over a 24h period in a fashion that suits our lifestyle and heat requirements. After a cooling period to 17C, we are gently reheating back to 20C throughout the day. Much of this is dictated by the fact we have an oversized heat pump that isn't capable of maintaining a steady state of 19C in anything other than the very coldest of weather. Our SCOP is in the region of 4.0 which I am more than happy with.

 


Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero


   
ReplyQuote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 4 years ago
Posts: 569
Your energy: 0 kWh
Topic starter  

Posted by: @old_scientist
↑

The heat pump is oversized, and even at minimum output will output too much heat overnight unless it's below freezing outside, so a setback or switch off is almost mandatory for overnight comfort.

Thanks for your comments @old_scientist. It sounds like you’ve managed to get the room temperatures you want albeit by manually adjusting the flow temperatures. 

We have had similar problems with finding the lowest flow temperatures but perhaps not as extreme as yours. We have found the 36C flow temperature is about as low as our Ecodan 8.5kw model will modulate down to before it starts to cycle. So at warmer nights above 10c we might have to let it run to a higher set temperature and switch off using the thermostat. 

 

Posted by: @old_scientist
↑

The overall effect is the indoor temp is oscillating between 17C and 20C over a 24h period in a fashion that suits our lifestyle and heat requirements. After a cooling period to 17C, we are gently reheating back to 20C throughout the day. Much of this is dictated by the fact we have an oversized heat pump that isn't capable of maintaining a steady state of 19C in anything other than the very coldest of weather. Our SCOP is in the region of 4.0 which I am more than happy with.

 

It’s good you’re getting a SCOP of 4 and you have a convenient way of adjusting the thermostat.

 

 


This post was modified 11 months ago by SUNandAIR

   