Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps

165 Posts
17 Users
29 Reactions
3,551 Views
(@bobtskutter)
Estimable Member Member
539 kWhs
Joined: 2 months ago
Posts: 86
 

Posted by: @transparent

I don't think that will work because compressors can't operate at very low speed.

Hummm....this depends on the type of compressor.

For a typical positive displacement compressor (think medical syringe moving backwards and forwards), they can operate a very low speeds.

Turbo compressors, think jet engines, can't operate at low speeds.  (look up compressor stall / surge / stonewall if you're interested).

Trouble is ASHP aren't using plunger compressors, they're either rotary or scroll type.  These compressors have internal leakage which means some gas gets "left behind" inside the compressor.  At low speeds there is more internal leakage than forward flow, so they stop pumping i.e. they don't work well at low speed.  These designs will also use the lubrication oil as a seal fluid to prevent internal leakage, which then allows the machine to operate a slow speeds - but with higher internal friction, therefore loosing out on overall efficiency.

Again, this illustrates nicely just how difficult it is to select a device purely based on "efficiency".

Any device should be selected so that it works well over the required operating range - this does not necessarily mean "the most efficient".

We've not even spoken about the initial cost of a larger heat pump vs a small heat pump. In the example above, assuming a 10year life, would the customer spend less money with the 8kW machine than they would with the 11kW machine?

Regards

Bob


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12949 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Posted by: @heatgeek

A UFH system with insulated floating screed floor, tog 1 carpet and 20cm pipe spacing has a fixed System Performance Factor (SPF) of 3 W/m2K.

Note for those who wish to follow this discussion but are wary of the maths...

There is a BEAMA Guide to underfloor heating which compares the SPF of different flooring materials.
it has illustrations and reference tables.

 

Beware that the letters SPF are also used to describe the Seasonal Performance Factor for a heat-pump.
The difference should be apparent if you check the context.

Save energy... recycle electrons!


   
ReplyQuote
(@stuartornum)
Trusted Member Member
160 kWhs
Joined: 1 year ago
Posts: 20
Topic starter  

Posted by: @bobtskutter

 

We've not even spoken about the initial cost of a larger heat pump vs a small heat pump. In the example above, assuming a 10year life, would the customer spend less money with the 8kW machine than they would with the 11kW machine?

This is a very valid point, one that could be modelled out quite easily 


   
ReplyQuote



(@uk_pete_2000)
Estimable Member Member
387 kWhs
Joined: 4 months ago
Posts: 69
 

Posted by: @heatgeek

@jamespa I have been quietly following all of this in amazement at some of the statements, especially about over-sized HP’s being more efficient. The comments by @jamespa are absolutely correct. Let me provide a parallel view. Imagine you are trying to heat a large metal cooking pot on a fire outside on a winter’s day and you want to keep a constant water temperature. With the right size fire the metal pot will heat up to the temperature at which balance is achieved between the heat input and the heat output from the pot which will be sustained for a constant outside temperature. If we only have a big on/off flame, we can overheat the pot by, say, 1C more and then let it cool -1C down before applying heat again. The bigger the flame the more on/offs. The average required temperature will be sustained (with hysteresis) but the actual heat energy applied to the pot will be the same regardless.
The same applies to a house. The flame is the floor in a UFH system and the pot is the room above with its internal air and its walls to the outside temperature. A UFH system with insulated floating screed floor, tog 1 carpet and 20cm pipe spacing has a fixed System Performance Factor (SPF) of 3 W/m2K. A certified Passivhaus must meet a space heating limit of 10W/m2 at peak demand. A 500 sqm Passivhaus will therefore lose 5kW at this limit. To supply constant 10W/m2 @ SPF 3 requires a delta-T of 3.33C (3 x 3.33 = 10) or MWT 23.3C for 20C room temperature (25.8C flow). If this 24 h heat load is concentrated over 12 hours and the room then left to cool for 12 hours, double the heat output is required for 12 hours, therefore the delta-T must be doubled (6.66C) with flow of 29.2C. The 24h heat loss @ 20C average room temperature is the same however you heat it. Therefore, assuming fixed outdoor temperature, you can heat constantly @ 26C flow or for 12 hours @ 29C flow with slightly worse COP. The size of the heat pump is irrelevant as long as it can supply peak 5kW load and cater for lower loads efficiently. However, a 13kW heat pump would need to demodulate down to 5kW before cycling. Below this peak demand, it will struggle. The situation with an average house losing 60W/m2 will be 6 times worse with wide COP difference. Furthermore, to say that heating constantly at 23C room temperature costs 3 times more than 12 hour concentrated heating at 20C, and therefore constant heating at 20C should not be used is frankly ridiculous.  And WC is useless......🤨

I enjoyed reading this response, it so follows our house, but we have different results.
 
Our house is 538m² and built to Passive standards and we have a 13kw HP, but running it 24hrs will cost us more than twice, as much running it by stop / starting.
 
For a couple of years we allowed the system to decide when to heat then turn itself off till it dropped 1°. At which time it would heat up and start again. This cost us 1300kwh each year (no DHW). 
 
We now control it a bit more and only run the HP during the day for 6 to 8 hrs. Then allow the house to cool down and restart the cycle again. So much the same as before but we are hoping it will save 100 to 200kwh. Next year we will make some more changes and hopefully reduce our power to less than 1000kwh.
 
We run the system with a flow temp of 26° (Not the 29 you list), no WC involved (which we did have for 2 years). If we do run it 24/7 (which we tried at the start of January), then the flow has to be reduced to around 23°. But the cost went up quite a bit, so much so that I will not be doing it again. It does cost 2 to 3 times as much.
 
Next year, after some changes, we hope to run the HP at 23°, but it will still be turned off over night and only run during the day. 
 
We could change the HP to a 4-6kw unit and run at say 20-21 flow temp, but i don't think we would save anything running it 24/7. Having a larger HP means we get less de-icing, slower fan and compressor speeds. Having a buffer means the HP does not cycle. When we tested 24/7 it started to introduce cycling, as the return temp increased over time to match the flow temp. The only way we could stop this was to go back to on / off operation

 


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10732 kWhs
Veteran
Joined: 2 years ago
Posts: 2023
 

@heatgeek  @uk_pete_2000

I think it's clear that the general conclusions that apply to the vast majority of UK housing stock, may not apply to the tiny minority which are low loss/eco houses with very low heating requirements.  Furthermore there are good theoretical reasons why this is the case.  Of course the latter probably, at least for now, represent a disproportionate subset of heat pump installations (although not necessarily the majority).

In any statement about 'best approach' it's therefore vital to distinguish which case the statement applies to and equally vital not to assume that it applies to the other case.  

Any statement I make is intended to apply to the vast majority of UK housing stock not the low loss/eco house special case, unless I say otherwise.  I will henceforth repeat this from time to time!

This post was modified 4 weeks ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@heatgeek)
Trusted Member Member
290 kWhs
Joined: 3 months ago
Posts: 39
 

@uk_pete_2000 Sorry, I forgot to say that in my second case of 12 hour heating period, a double size HP would be required i.e. 10kW to deliver double the load (120kWh in 12 hours). This is the only way you could operate with such a large HP (bigger flame). As pointed out before, if heating is continuous then it would cycle endlessly at <5kW output as it is too big and cost will be high. The flow temperature is a function of the efficiency of your heat emitters. For example, a 15cm pipe spacing would increase SPF to 3.3 and MWT would then be 26C in my example. When talking flow, one must distinguish between flow leaving the HP and the average flow temp in the floor with 5C delta-T. My figures are notional. The figure for Passivhaus is a minimum limit and actual heat loss will depend on your own level of insulation. Having said that, I am still trying to get my head around what you are saying is happening (when I get the time). Will get back.


   
👍
1
ReplyQuote
(@bobtskutter)
Estimable Member Member
539 kWhs
Joined: 2 months ago
Posts: 86
 

Posted by: @uk_pete_2000

We could change the HP to a 4-6kw unit and run at say 20-21 flow temp, but i don't think we would save anything running it 24/7. Having a larger HP means we get less de-icing, slower fan and compressor speeds. Having a buffer means the HP does not cycle. When we tested 24/7 it started to introduce cycling, as the return temp increased over time to match the flow temp. The only way we could stop this was to go back to on / off operation

Just a thought, do you have underfloor heating?

The comment "started cycling as the return temp increased" makes me think you're seeing a benefit of having a low return water temperature.

regards

bob


   
ReplyQuote
(@uk_pete_2000)
Estimable Member Member
387 kWhs
Joined: 4 months ago
Posts: 69
 

Posted by: @bobtskutter

Posted by: @uk_pete_2000

We could change the HP to a 4-6kw unit and run at say 20-21 flow temp, but i don't think we would save anything running it 24/7. Having a larger HP means we get less de-icing, slower fan and compressor speeds. Having a buffer means the HP does not cycle. When we tested 24/7 it started to introduce cycling, as the return temp increased over time to match the flow temp. The only way we could stop this was to go back to on / off operation

Just a thought, do you have underfloor heating?

The comment "started cycling as the return temp increased" makes me think you're seeing a benefit of having a low return water temperature.

regards

bob

Yes we have about 300m² on two manifolds, 16 loops. Another manifold is for upstairs rads

 


   
ReplyQuote
(@bobtskutter)
Estimable Member Member
539 kWhs
Joined: 2 months ago
Posts: 86
 

Here's a quick spreadsheet I put together that shows how compressor discharge temperature varies according to pressure ratio.

The data is based on Propane, R290 (because that's what was on the Air Liquide web site)

You must have the return water temperature to the ASHP less than the condensation temperature of Propane at the compressor discharge pressure.

If your return temperature is 27C, you can have a pressure ratio of 10

If your return temperature is 47C, you need a pressure ratio of 16

i.e. increasing the return water temperature from 27C to 47C will require 60% more compressor power (because compressor power is proportional to pressure ratio).

Regards

Bob

This post was modified 4 weeks ago 2 times by BobTSkutter

   
🤩
1
ReplyQuote



(@heatgeek)
Trusted Member Member
290 kWhs
Joined: 3 months ago
Posts: 39
 

@uk_pete_2000 I have perused your data again. As far as I can see there is no way that you can efficiently use such a large HP to directly heat your emitters. You are focussed on lowering temperature as a metric for direct heating. Temperature has no effect on heat delivery, it only slows down the delivery of heat from the emitter to the room. The heat delivered by 25/20C flow is exactly the same as 40/35C. Let’s look at flow instead. You need 37 l/min flow for 13kW (5C delta-T). The HP may be able to modulate down to 6kW or 17 l/min flow. If you need 3kW heat on a milder day, emitters will require 8.5 l/min flow. The HP can only deliver 17 l/min minimum so half the flow will go to emitters and half routed back to HP through the buffer tank. This cannot be good. Another problem is that reducing flow down to 23C screws up your radiators. They are non-linear unlike the UFH and cause distortion with the UFH. This is the same problem that I have. Therefore you should choose the minimum heat temperature for the radiators to operate efficiently at 12-15C outside temperature.

Therefore the only way I can see that you can use this HP efficiently is to change the buffer tank for a 300l thermal store and use a 5C hysteresis in the store. Add a mild form of WC e.g. 30/25C @ 15C and 35/30C at low end. If 30/25C works across the board with radiators then keep this. The HP will be decoupled from the emitters completely and will heat the store directly. With 13kW a 5C uplift from 25C to 30C will take around 1.5 hours (~20kWh charge) off the top of my head and HP operation will be continuous and efficient. Then the emitters will draw water at leisure over the next 7-8 hours before the HP kicks in again. Twice a day HP heating will probably be enough therefore you can make use of timed off-peak periods. As emitters are now independent of flow constraints, you can make liberal use of thermostats for individual temperature control and save more. A simple thermal store is a much cheaper option than a new smaller HP. Use 2 sensors in a latch to ensure HP heats the store down to the bottom. Emitters draw from the top. A vice now becomes a virtue.

Hope this gives some food for thought.


   
ReplyQuote
(@uk_pete_2000)
Estimable Member Member
387 kWhs
Joined: 4 months ago
Posts: 69
 

@heatgeek 

Thank you, yes this is quite a meal and I'll try to understand each part. 
 
--- "efficiently use such a large HP to directly heat your emitters" ---
 
Not sure what this is saying. If its about the size of the HP, then I agree it is far too large, but MCS figures said we need this size. It listed our heat lose around 23kwh. Our EPC (taken from SAP, new house build) showed 8,300kwh. One SAP showed just 3,500kwh, heatpunk showed 11,000kwh. Everyone is different and I suspect the SAP ones are much closer to the correct figures and falls inline with possible SCOP usage.
 
--- "The heat delivered by 25/20C flow is exactly the same as 40/35C" ---
 
I have no idea about how much heat is delivered (nor do you need to show the formula/explain) All I see is the higher the flow temp, the greater risk of de-icing and the house heating up too much etc.  What happened to "slow & low" ?
 
--- "it only slows down the delivery of heat from the emitter to the room" ---
 
Yes it does but any quicker and we would need to be off for longer, then we lose too much heat while it's off. My idea is to run it for so long, then allow house to drop 1° and turn HP back on. Normally it takes over 12hrs to lose this heat and sometime 16hrs, so I try to time the unit in on to this mark. Much the same as "setback", but ours take longer.
 
Your next part is figures that have gone over my head (sorry). Until I make some changes I have no idea what the flow speed is. The HP is set on its lowest setting, which is 15l/m, I suspect its a little higher than that and with our HP I can not go any slower without putting in restrictions.
 
--- "so half the flow will go to emitters and half routed back to HP through the buffer tank" ---
 
Possible not quite half, but yes some does go that way. That was my original reason for coming  to this site but answers didn't help, so I set about rebalancing the flow across the buffer to 2°. Could not get it lower, so looking at other options.
 
--- radiators ---
 
All where sized for max of 35° flow. As they are in the bedroom and we do not restrict flow they work fine. They are also on a separate manifold (we have 3, with 20 zones between them, all fully opened)
 
The idea of changing the buffer to a thermal store sounds and looks good. During December, we had a problem with our EP002 controller. It meant we could turn on the HP separately  from the CH and as I was working on the buffer at the time I ran it a little like a thermal store. The HP was on for about 6 hrs and the CH side was on for 8hrs, just to extract the most from the buffer. All worked fine, so I understand what you are getting at.
 
That is until I see the usage of 20kwh (this amount will cover all our house electricity per day) and if this was twice a day I might as well run it 24/7 at 23-25°. The usage would be about the same. If I can make this work on one charge etc then this is a good option.
 
Under normal conditions we are using about 6 to 8kwh per day, but this does increase the longer we run the system. To us it depends on how long we run the HP rather than what flow temp we have.
 
Now we could leave it all, as is, and as long as my changes have not introduce extra running cost, it will just cost us about £150 per year to run. So how much do you spend to save £50 per year ? 
 
To us, it has always about reducing our ongoing cost, so some work will take place. You are correct changing the HP is not really the option, but changes to the setup are.
 
The way I was looking at was to introduce valves on all 4 ports, bypass pipes / valve between ASHP out to CH in and another between CH return to HP return. As it will be drained we will also install a number of flow meters / inhibitors to help understanding.
 
Then over next winter I can go from a 4 port buffer, to a three port buffer, to a volumizer. We would even be able to test a form of thermal store.
 
The one I think will work better for us, is the 3 port buffer. This will push more heat from the HP into the CH and thus we can lower the flow temp even further and possible even run at 23°( which is the lowest we can go). It will also allow us to have different flow speeds
 
Whether we can go just a volumizer, we have the size,  is debatable as this would be better running 24/7 rather than the way we do it.
 
As the current OAT are low, I am re-checking how much we use against running it 24/7.  I just have to work with one 10kw battery, as the 2nd one is offline and waiting for replacement. This helps us keep all cost down to OE Cosy cheap rate
 
 
 
 

   
ReplyQuote
(@heatgeek)
Trusted Member Member
290 kWhs
Joined: 3 months ago
Posts: 39
 

@uk_pete_2000 I think we have some misunderstandings here. You previously indicated that you have a passive house (<10W/m2 or ~5kW peak loss) but it now seems that you actually have a previous standard new build. Your heat loss could therefore be nearer 20W/m2 or 10kW peak. Allowing a margin for DHW, etc implies that the sizing of your HP is in the right ballpark. This negates all my previous comments as I took it that your peak heat loss is less than the minimum output of your HP. You are focussed on your kWh electricity usage when you should be assessing your kW heat loss. When I mentioned 20kWh for the tank, this was for heat input from the HP. At a COP of 5, this equates to 4kWh electricity input. You cannot plan or change anything unless you have an understanding of your house heat loss in kWs, not kWhs of electricity. Regarding flows, you have 4 manifolds with a flow meter on each loop/radiator, don’t you? What are the l/min readings on these? Does each manifold have a pump/mixer or is there only one post-buffer pump for all? What is the model and speed setting on these pumps? Do you have u-values and dimensions for all walls, floor, roof and windows? What is the pipe spacing on your UFH, screed type and floor covering? You are also operating the heating intermittently which is distorting the value of real heat loss if you only look at the electricity consumed.

It is impossible to give you any suggestions without accurate information.


   
ReplyQuote
Page 5 / 14
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security