Comparing COP (coefficient of performance)
I ran an experiment this week to see what our COP and electricity consumption would be like by varying flow rates (45C and 40C):Â https://myhomefarm.co.uk/air-source-heat-pump-cop
As the winter comes to an end, please share your COP figures for your systems. It should make for some interesting reading.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Mars,
I suspect that the method being used to calculate COP in your system is not that accurate. I do believe that the MMSP system, even when correctly installed, is of the order of +/- 5% accurate. I don't think that any heat pump manufacturers system will come close to that.
Whilst electrical energy consumption can be measured with reasonable accuracy, to accurately measure the heat energy produced would require not only accurate temperature measurements, but also reasonably accurate mass flow measurement, which is not that easy to do.
Your tests proved what I think most people already know, that lowering the water flow temperature improves efficiency and reduces running costs. By using weather compensation this should be achieved automatically, without continual user intervention.
@derek-m, good points. Because we have a bivalent system, we've had to install two separate metres that are exclusively connected to our heat pump so that we can submit these readings to RHI on a quarterly basis to get our payments. I would therefore assume that the two metres provide us with two accurate data points: ASHP electricity consumption and ASHP heat generated. If it's of interest, I'll provide the names of both metres later this evening.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@derek-m, good points. Because we have a bivalent system, we've had to install two separate metres that are exclusively connected to our heat pump so that we can submit these readings to RHI on a quarterly basis to get our payments. I would therefore assume that the two metres provide us with two accurate data points: ASHP electricity consumption and ASHP heat generated. If it's of interest, I'll provide the names of both metres later this evening.
Hi Mars,
I am assuming that an electrical energy meter was installed along with a heat energy meter. Did the installers provide any form of calibration certificates?
@derek-m, you always give me some very useful homework to do 😀. I have no idea whether they were calibrated and I don't think I have any certificates to this effect, but I'll rummage through the paperwork tomorrow. Failing that, I'll contact the installers and enquire. I'll also post some photos in the morning of the two metres. The one that registers heat generated is extremely helpful as it also keeps tabs on physical flow of water through the pipes, which I use regularly. We're now averaging 30 litres/minute on the ASHP which is good. When that drops, it's time to give the mesh filter a clean, but thankfully we've been running very clean of late.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Rodents! A word of warning for heat pump owners
2 weeks ago
-
Surface mount or bury primaries for heat pump installation?
3 months ago
-
UFH and ASHPs
4 months ago
-
Installing your own ASHP - DIY
5 months ago
-
ASHP install contract and BUS grant money
6 months ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 58 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay yes there is the modbus register list at th...
By benson , 44 seconds ago
-
RE: Big Changes Coming to Our Heat Pump System
@scalextrix Yup Sadly consumerism, the foundation o...
By JamesPa , 7 minutes ago
-
RE: Heat Pump Damage on install - useable or dealbreaker?
@benson I imagine that this may well be a Daikin unit a...
By Toodles , 12 minutes ago
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 13 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 15 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 15 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 16 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 18 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 20 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 21 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago