Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Comms and power cabling to outside unit

14 Posts
4 Users
6 Reactions
325 Views
(@papahuhu)
Reputable Member Member
Joined: 1 year ago
Posts: 370
Topic starter   [#3104]

Does anyone know if

1. The comms cable should be 50 mm from the power cable (mine isn’t, it’s been clipped to the power cable). The install manual says it should. 

2. Is it mandatory (MCS or electrical safety regs) for the power cable to be run inside trunking. Mine has just been clipped and runs on the outside of the brickwork. The reason I ask is that the install manual states it should be run in ducting of suitable IP rating to protect from water and possible shock.

I just had a service from BG and they indicated it was a problem/contrary to install manual. I approached the installer and they said it was not an issue.

Thanks

 



   
Quote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5245
 

Posted by: @papahuhu

1. The comms cable should be 50 mm from the power cable (mine isn’t, it’s been clipped to the power cable). The install manual says it should. 

If the instal manual says it should then yes it should.  As to whether it makes a difference that is another matter.

 

Posted by: @papahuhu

2. Is it mandatory (MCS or electrical safety regs) for the power cable to be run inside trunking. Mine has just been clipped and runs on the outside of the brickwork. The reason I ask is that the install manual states it should be run in ducting of suitable IP rating to protect from water and possible shock.

This is principally in the UK a matter for electrical regulations and on particular the electrician doing the installation.  The regs frequently put it in these terms, rather than absolute terms.

The electrician is, I believe, required to make an assessment of the risk.  This link references some specificregs which apply: https://professional-electrician.com/technical/external-installations-cables/.  

Of course different electricians will make different assessments.

FWIW mine is run in trunking for the fixed part (ie up to the breaker) but not thereafter, on the grounds that the last metre is mechanically protected by the body of the heat pump.

That said if the installation manual says it's mandatory (read the wording very carefully as a lawyer would) then it is arguably mandatory.

 

What exactly does the installation manual actually say about these cases, it's not unknown for them to be misquoted (for example it's frequently quoted that vaillant require a specific type of RCD.   This is true, but only if an RCD is fitted.  There is however no requirement to fit an RCD so a legitimate option is not to bother). 

One approach is to ask bg precisely which paragraphs in the installation manual or regs they are referring to, you can then look them up. If they don't know they are giving you BS.


This post was modified 3 weeks ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Famed Member Moderator
Joined: 5 years ago
Posts: 2054
 

I can’t comment on comms cabling as installed for heat pumps but I can say that network cabling (which, let’s face it, is a form of comms cable) needs to either be separated from power cabling or needs to be shielded cable. If not, there will be interference on the data cable as a result of its proximity to mains electrical current. It makes sense the same would hold true for any other comms cable but I’ve no idea if the effect would be as severe or, of course, sufficient to cause communication issues.


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
👍
1
ReplyQuote
(@papahuhu)
Reputable Member Member
Joined: 1 year ago
Posts: 370
Topic starter  

@jamespa Thanks, bottom left is the section from the install manual, it looks like a mandatory instruction to me.

IMG 0297

 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5245
 

In relation to the power cord it says 'should' not 'shall' or 'must'.  Should is often but not universally taken to mean that the instructions is to be complied with unless there are reasons to the contrary.  MCS use it this way.

I tend to agree that, unless there are reasons to the contrary or the meaning of should is defined elsewhere on the manual, this installation manual specifies to put the power courd in an appropriate duct.  Really it's absolutely no business of the hp manufacturer to specify how electrical safety should be approached, other than in relation to matters specific to their product, but it appears they have.

On this basis (but not on any technical basis) I would say bg do have a reasonable argument and your installer should respond with their rebuttal.

In relation to the Comms cable the instructions are clear and there is a technical underpinning for separation.  Ignore at your peril


This post was modified 3 weeks ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@papahuhu)
Reputable Member Member
Joined: 1 year ago
Posts: 370
Topic starter  

@majordennisbloodnok 

I was half earwigging, BG rang Samsung and asked him to check the shielding status. I don’t know the status but apparently they advised it does need to be at least 50mm away. BG was here for just under 4 hours for service, very thorough. Checked and cleaned every terminal, took fan blades off, spent 30 mins cleaning the fins and drain pan, straightened some fins, checked inhibitor and topped it up, cleaned mag filter. Spent another hour on the inside unit but I had to take a call so didn’t hang over his shoulder. I was impressed for a £180 service. 

I give the fins a quick hose down quarterly when I do the windows, but I was amazed at how much black crap the cleaner solution took off. I no longer think it’s an unnecessary gimmick as all that residue that must impact heat xfer. 



   
👍
2
ReplyQuote
(@papahuhu)
Reputable Member Member
Joined: 1 year ago
Posts: 370
Topic starter  

@jamespa 

Thanks James. I’ll see what they say. 
I always thought the purpose of trunking was largely to protect the cable against UV and mechanical damage, it’s quite hefty (on a 32A circuit) and runs at calf height on the wall. 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5245
 

Posted by: @papahuhu

always thought the purpose of trunking was largely to protect the cable against UV and mechanical damage

That's also my understanding.  Obviously outside mechanical damage (potentially exposing live wire hence the risk) is arguably more likely than indoors.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@old_scientist)
Honorable Member Member
Joined: 2 years ago
Posts: 503
 

@papahuhu do you have a link where you can sign up for that servicing deal with BG? 

Never mind - found it.


This post was modified 3 weeks ago by Old_Scientist

Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.


   
ReplyQuote
(@papahuhu)
Reputable Member Member
Joined: 1 year ago
Posts: 370
Topic starter  

@old_scientist 

this was the one I used (there are 3, but this is the one for warrantied items, non glycol soupy stems only.) They were here 4 hours. 

https://www.britishgas.co.uk/heating/heat-pump-service.html



   
👍
1
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 5245
 

Interesting, they will service but not cover systems with glycol.  That's a pointer to the future!


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@papahuhu)
Reputable Member Member
Joined: 1 year ago
Posts: 370
Topic starter  

@jamespa 

I can only guess the issue is with cost of disposal or refilling. I know they also limit it to certain manufacturers too, I assume to the ones that BG fit themselves. 
The pricing is a bit weird, it works out about £5 a month extra for break down cover above and beyond the service cost, for parts and labour I thought that was cheap as chips. 
But the same cover for non warrantied systems is nearly £600 a year and has limits on part costs.



   
ReplyQuote