@cathoderay ok, just when I think I’m getting there…..
I want to have a bath and temperature of the water is at 36°
I thought the DHW would kick in if the temperature fell 5°? Or is it 15°? Feel like I’m losing it 🤯
Posted by: @cathyem1I thought the DHW would kick in if the temperature fell 5°? Or is it 15°?
It took me a while to get my head round how it works - at least, how I think it works.
The default drop in temperature from the set DHW temperature that triggers DHW heating is 5 degrees. If your set DHW is 45 degrees, then a reheat will be triggered when the tank actual temp drops to 40 degrees (or maybe 39 - ie setting the drop to 5 degrees actually means 'when the drop is more than 5 degrees' - I say this based on my own observations of when my system will trigger a reheat).
If you have DHW heating on a timer, as you do, then a reheat triggered by a 5 or more degree drop in actual DHW temperature will only happen when the DHW is timed to be on. For example, if the DHW is timed to come on between 1300 and 1400 (as mine is, as I don't have a time of use tariff), and I have a set DHE temp of 50 degrees, and a drop trigger of 10 degrees (as I do), then if the DHW is say 38 degrees at 1200 nothing will happen (DHW is OFF), however, come 1300 the DHW will come on, and the tank will reheat. If however the tank was at 42 degrees at 1300, a reheat won't happen, because the drop isn't large enough, even though the DHW heating is nominally ON.
Now occasionally I might need to manually trigger a reheat eg I want to have a bath, but the tank actual temp is too cool. Let's say I want a bath at 0900 and the tank is at 32 degrees. This I think is the situation you were in, DHW too cool and outside the timed DHW reheat period. To get the DHW heating to come on, you have to turn it on manually on the wired controller home page: Unlock > right arrow to DHW temp (which will change from showing the actual to the set temp) > toggle on (top right hand button) and then finally OK. The small right hand panel tap icon should get squiggles by it, and the 'compressor' icon should move to the right hand panel, and a tap should appear in the middle panel - all indications that DHW heating is ON, and you should see the actual DHW temp start to rise to your set temp. You can if you want turn it off (same steps as above, only this time toggle off rather than on) when it is warm enough, which I typically do when it has got to 45 degrees, which is warm enough for a bath; no need to get to 50 degrees.
[This paragraph is of secondary importance, it covers a rare event, the preceding paragraph cover the much more common situation. Very occasionally, the above scenario happens, tank actual temp is a bit cool for a bath, but the actual DHW isn't cool enough to trigger a reheat. Let's say, on my settings (set DHW temp 50 degrees, drop trigger 10 degrees), the tank happens to be at 41 degrees and I want to have a bath. If I run a bath with it at 41 degrees, it will run cool before the bath has filled, so I need to get the water a little warmer, but the above manual routine won't work, because the DHW tank temperature drop isn't large enough. To get round that, I have to set the set DHW high enough (ie more than 10 degrees above the current actual temp - in this scenario I might set it to 55 degrees) to trigger a reheat, and then do the manual DHW turn as described in the preceding paragraph. Most importantly, if you do ever have to do this, watch the DHW temp as it rises, and turn the DHW heating off when it is warm enough, and reset the set DHW temp to your normal setting.]
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Of course! Thank you so much for your wisdom. I’m printing out your advice so i don’t forget. I have ADHD so a printed copy always helps.
While I’m here, do you have any issues with the clock on the wired controller? My clock keeps gaining time very quickly.
Posted by: @cathyem1While I’m here, do you have any issues with the clock on the wired controller? My clock keeps gaining time very quickly.
Not that I am aware of. Perhaps your wired controller is in a tardis?
Seriously though, of course it shouldn't gain time. I can't think of anything in the controller that would alter time keeping, which is after all a very basic and at the same time fundamental activity. Maybe take some readings to show how fast it is gaining time and then ask your supplier about it?
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay He’s going to love me 😉
I’ve just checked and it has gained 8 minutes since last night!
Posted by: @cathyem1He’s going to love me 😉
I’ve just checked and it has gained 8 minutes since last night!
I know, and these things are always awkward, but that doesn't mean you should have to put up with something that is clearly malfunctioning. If it can't keep time, what else is it getting wrong, either because the time keeping is out, or coincidentally?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathyem1I’ve just checked and it has gained 8 minutes since last night!
Hmm. That could just be down to relativity.
What orbit are you in?
Save energy... recycle electrons!
@transparent Oh! The Einstein effect!😉 Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@cathyem1 Many digital time-clocks have two sources of data in order to retain some level of synchronisation during a power-cut.
They can pick up time from a master source, such as the internet, which uses Coordinated Universalised Time (UTC)
and there's also a date/time clock chip within them, powered by a lithium disulphide cell which has about 10-years life.
Whether or not your heat-pump system was ever intended to be synchronised to UTC,
the symptom you describe suggests that it's actually operating from an internal chip.
Posted by: @cathoderayIf it can't keep time, what else is it getting wrong,
There's unlikely to be any other fault as a direct consequence.
The date/time clock chip uses a quartz crystal oscillator and is separate from the electronics which is running the programming software.
The software itself doesn't malfunction just because it's being fed an 'incorrect time'.
It has no frame of reference to 'know' what is correct.
Save energy... recycle electrons!
Posted by: @transparentThere's unlikely to be any other fault as a direct consequence.
I was aware at the time I was writing very concisely, perhaps too concisely.
What I was getting at was the possibility of:
(a) a direct consequence of the timer being out, eg something timed to happen at hh:mm will happen at hh:mm +/- the current error
and, quite separately
(b) if the timer is out of whack, might other things as yet unknown also be out of whack? Basically when one find error I can't help but wonder what other errors there might be.
Posted by: @transparentThe software itself doesn't malfunction just because it's being fed an 'incorrect time'.
Likely not, but it will give the wrong answer. But it, and very likely we unless there is an obvious error, just don't know it is giving the wrong answer. It becomes GIGO. That's why it is so important to cross check independent sources of data whenever possible.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay The supplier has agreed our control panel is defective and has agreed to seek a replacement from Baxi. He’ll swap it when he comes to add the glycol etc to the solar thermal water heating and add some extra insulation to the pipes in the airing cupboard 🥰
Posted by: @cathyem1The supplier has agreed our control panel is defective and has agreed to seek a replacement from Baxi.
Sounds like good progress!
Midea 14kW (for now...) ASHP heating both building and DHW
- 21 Forums
- 1,959 Topics
- 42.5 K Posts
- 20 Online
- 2,272 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
SolarPV tables / online calculator
Is there some table or an online calculator that I can ...
By MichelleC , 2 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
Same here @jamespa - we have a 12kW Samsung ASHP, solar...
By Old_Scientist , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 5 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 6 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 7 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 9 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 10 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 13 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 14 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 15 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 18 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 19 hours ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 1 day ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 1 day ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 1 day ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 1 day ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I’d be interested to hear the feedback and consensus on...
By Mars , 2 days ago
Latest Topics
-
SolarPV tables / online calculator
By MichelleC 2 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 14 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 17 hours ago
-
By Toodles 1 day ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago
-
By big_si 2 days ago