Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@cathoderay ok, just when I think I’m getting there…..
I want to have a bath and temperature of the water is at 36°
I thought the DHW would kick in if the temperature fell 5°? Or is it 15°? Feel like I’m losing it 🤯
Posted by: @cathyem1I thought the DHW would kick in if the temperature fell 5°? Or is it 15°?
It took me a while to get my head round how it works - at least, how I think it works.
The default drop in temperature from the set DHW temperature that triggers DHW heating is 5 degrees. If your set DHW is 45 degrees, then a reheat will be triggered when the tank actual temp drops to 40 degrees (or maybe 39 - ie setting the drop to 5 degrees actually means 'when the drop is more than 5 degrees' - I say this based on my own observations of when my system will trigger a reheat).
If you have DHW heating on a timer, as you do, then a reheat triggered by a 5 or more degree drop in actual DHW temperature will only happen when the DHW is timed to be on. For example, if the DHW is timed to come on between 1300 and 1400 (as mine is, as I don't have a time of use tariff), and I have a set DHE temp of 50 degrees, and a drop trigger of 10 degrees (as I do), then if the DHW is say 38 degrees at 1200 nothing will happen (DHW is OFF), however, come 1300 the DHW will come on, and the tank will reheat. If however the tank was at 42 degrees at 1300, a reheat won't happen, because the drop isn't large enough, even though the DHW heating is nominally ON.
Now occasionally I might need to manually trigger a reheat eg I want to have a bath, but the tank actual temp is too cool. Let's say I want a bath at 0900 and the tank is at 32 degrees. This I think is the situation you were in, DHW too cool and outside the timed DHW reheat period. To get the DHW heating to come on, you have to turn it on manually on the wired controller home page: Unlock > right arrow to DHW temp (which will change from showing the actual to the set temp) > toggle on (top right hand button) and then finally OK. The small right hand panel tap icon should get squiggles by it, and the 'compressor' icon should move to the right hand panel, and a tap should appear in the middle panel - all indications that DHW heating is ON, and you should see the actual DHW temp start to rise to your set temp. You can if you want turn it off (same steps as above, only this time toggle off rather than on) when it is warm enough, which I typically do when it has got to 45 degrees, which is warm enough for a bath; no need to get to 50 degrees.
[This paragraph is of secondary importance, it covers a rare event, the preceding paragraph cover the much more common situation. Very occasionally, the above scenario happens, tank actual temp is a bit cool for a bath, but the actual DHW isn't cool enough to trigger a reheat. Let's say, on my settings (set DHW temp 50 degrees, drop trigger 10 degrees), the tank happens to be at 41 degrees and I want to have a bath. If I run a bath with it at 41 degrees, it will run cool before the bath has filled, so I need to get the water a little warmer, but the above manual routine won't work, because the DHW tank temperature drop isn't large enough. To get round that, I have to set the set DHW high enough (ie more than 10 degrees above the current actual temp - in this scenario I might set it to 55 degrees) to trigger a reheat, and then do the manual DHW turn as described in the preceding paragraph. Most importantly, if you do ever have to do this, watch the DHW temp as it rises, and turn the DHW heating off when it is warm enough, and reset the set DHW temp to your normal setting.]
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Of course! Thank you so much for your wisdom. I’m printing out your advice so i don’t forget. I have ADHD so a printed copy always helps.
While I’m here, do you have any issues with the clock on the wired controller? My clock keeps gaining time very quickly.
Posted by: @cathyem1While I’m here, do you have any issues with the clock on the wired controller? My clock keeps gaining time very quickly.
Not that I am aware of. Perhaps your wired controller is in a tardis?
Seriously though, of course it shouldn't gain time. I can't think of anything in the controller that would alter time keeping, which is after all a very basic and at the same time fundamental activity. Maybe take some readings to show how fast it is gaining time and then ask your supplier about it?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathyem1He’s going to love me 😉
I’ve just checked and it has gained 8 minutes since last night!
I know, and these things are always awkward, but that doesn't mean you should have to put up with something that is clearly malfunctioning. If it can't keep time, what else is it getting wrong, either because the time keeping is out, or coincidentally?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathyem1I’ve just checked and it has gained 8 minutes since last night!
Hmm. That could just be down to relativity.
What orbit are you in?
Save energy... recycle electrons!
@transparent Oh! The Einstein effect!😉 Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
@cathyem1 Many digital time-clocks have two sources of data in order to retain some level of synchronisation during a power-cut.
They can pick up time from a master source, such as the internet, which uses Coordinated Universalised Time (UTC)
and there's also a date/time clock chip within them, powered by a lithium disulphide cell which has about 10-years life.
Whether or not your heat-pump system was ever intended to be synchronised to UTC,
the symptom you describe suggests that it's actually operating from an internal chip.
Posted by: @cathoderayIf it can't keep time, what else is it getting wrong,
There's unlikely to be any other fault as a direct consequence.
The date/time clock chip uses a quartz crystal oscillator and is separate from the electronics which is running the programming software.
The software itself doesn't malfunction just because it's being fed an 'incorrect time'.
It has no frame of reference to 'know' what is correct.
Save energy... recycle electrons!
Posted by: @transparentThere's unlikely to be any other fault as a direct consequence.
I was aware at the time I was writing very concisely, perhaps too concisely.
What I was getting at was the possibility of:
(a) a direct consequence of the timer being out, eg something timed to happen at hh:mm will happen at hh:mm +/- the current error
and, quite separately
(b) if the timer is out of whack, might other things as yet unknown also be out of whack? Basically when one find error I can't help but wonder what other errors there might be.
Posted by: @transparentThe software itself doesn't malfunction just because it's being fed an 'incorrect time'.
Likely not, but it will give the wrong answer. But it, and very likely we unless there is an obvious error, just don't know it is giving the wrong answer. It becomes GIGO. That's why it is so important to cross check independent sources of data whenever possible.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay The supplier has agreed our control panel is defective and has agreed to seek a replacement from Baxi. He’ll swap it when he comes to add the glycol etc to the solar thermal water heating and add some extra insulation to the pipes in the airing cupboard 🥰
Posted by: @cathyem1The supplier has agreed our control panel is defective and has agreed to seek a replacement from Baxi.
Sounds like good progress!
Midea 14kW (for now...) ASHP heating both building and DHW
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 459 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles If I ever catch myself feeling hubristic I ...
By Papahuhu , 3 hours ago
-
Why? Factor in 85% efficiency for that oil boiler and...
By Old_Scientist , 3 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
I've been watching this with interest as I would like s...
By JohnnyB , 4 hours ago
-
RE: Aerotherm 12+12kw cascade huge power utilisation
What the hell. There is exactly one reason to use a h...
By bobflux , 4 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Thanks for such a comprehensive response!!! ...
By errmm , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 9 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 15 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 16 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 1 day ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 2 days ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 2 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 2 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 3 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 3 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago