@cathyem1 - this isn't exactly beginner's level stuff, but it may nonetheless help you get your head around some of this. This is my system running on weather compensation over a recent seven day period as shown on the bottom horizontal axis (I have fairly detailed monitoring that collects this data):
Now at first glance I am sure it makes no sense. However, lets look at certain elements:
In the upper (temperatures) chart
(1) the dark brown purple line stuck on around 20 - that's my room temperature. Fairly steady, weather compensation working as it should.
(2) the green line under the room temperature line - that's the outside air temperature (OAT). Ranges between zero and ten degrees.
(3) the partially obscured red/orange line - that's the SET (target) LWT, as set by the weather compensation curve, not by me). Note how it changes in response to the OAT. When it gets colder outside, the SET LWT goes up, when it's warmer outside, it goes down.
(4) The teal/turquoise line - that's the ACTUAL LWT. For now, just notice how most of the time it is pretty close to the SET LWT. The heat pump is doing its job, without any intervention from me, room stats, timers, magic controllers, woo crystals or anything else (apart from one adjustment control I have which fine tunes the weather compensation curve, but that's another subject for another day for more advanced use). The only thing I did was set the ends points of the weather compensation curve, the heat pump controls did the rest.
Also out of interest in the bottom energy chart note how variable the energy in (used) per hour is (green bars), depending on the OAT, without corresponding large increases in energy out (heat supplied to the house, the red bars). This reflects the extra effort needed in cold weather, the heat pump has to work much harder to produce heat, and as a result its performance (COP, the blue line) falls sharply. They key take away is just how variable the performance is: this is how we know that when it gets milder as spring approaches, our energy use (and bills) will go down.
Edit: I should add that in cold weather there is a double hit: not only does the COP plummet because it is cold, the demand also increases because it is cold. Result: big bills. But equally in mild weather, the COP (performance) increases greatly and the demand is far less. Result: tiny bills. Over a heating season, the two cancel each other out.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathyem1I'm keen to save some money
Cathy, once you've followed the instructions from @cathoderay to get the WC curve set correctly,
there comes a point where further investigation of System Optimisation is effort being spent with diminishing returns.
Let's look forward in time to see what else you could do to save money:
1: Spent a bit of time to better insulate those pipes, and the attached valves.
We haven't yet seen a photo of the external pipework.
That could be throwing away 20% of your heat energy before it even gets into the house!
2: Reduce the cost of the electricity you're using to run the heat-pump.
Even without having PV Solar Panels, there is still a strong argument in favour of battery storage.
With a Time of Use (ToU) tariff, you could then recharge the battery from the grid during cheap periods.
Better still, the inverter could be wired so as to continue running some equipment during a power cut
- the heat pump
- a kettle
- lights
Only you can decide those priorities.
But I'm suggesting these issues with your husband in mind.
Save energy... recycle electrons!
Thanks for the photos.
That's in the top 10% of external HP installations which I've seen. 🙂
But it still looks like rain could enter through the gaps in the insulation for the two anti-freeze valves and the isolator with the blue handle above them.
Any rain which goes between the insulation and the pipe will absorb precious heat,
and then dump it on the ground!
I also don't understand why you only appear to have one lever-valve to isolate the external unit.
Save energy... recycle electrons!
@transparent the installer is returning soon to replenish the glycol and sort out my solar thermal so i’ll mention these points to him then. Thank you again
Posted by: @cathyem1I’ve changed both ends of the curve by 1° today and i’ll see how we get on.
That's the way to go. Over time you will get closer and closer to the ideal setting for your home. Don't be thrown by days when external factors like wind chill (happens to homes as well as people), solar gain (sun's warmth also contributes to warming your home) and human activity eg lots of cooking push the room temp a bit this way or that, just let it happen. There are ways of dealing with these things but for most people they are not necessary. For now, I suggest just concentrate of getting the weather compensation curve right, and of course making progress with @transparent's suggestions.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathyem1the installer is returning soon to replenish the glycol
If you are to have glycol added to the system, then I question why have also had (relatively expensive) anti-freeze valves fitted. 🤔
The anti-freeze valve detects when the system fluid is on the point of forming ice, and then opens to empty your pipework into the gravel below the heat-pump.
It should only occur if the software-controlled de-frosting method has failed to remove ice from the compressor circuit and radiator grid of the external unit.
Your heat-pump then stops working (of course) but it does at least avoid damage occuring.
I wouldn't usually expect to see anti-freeze valves on a system with glycol, because they would be dumping that chemical into the soil.
Glycol also has a lower thermal capacity than water.
Adding it to your system will reduce its ability to move heat into the house.
Thus the heat-pump has to work slightly harder and is less efficient.
Everything you're learning about your heat pump is demonstrating that there are balances to be made between alternatives.
It's the role of your installer to explain these rather than just implementing their own personal preference.
Save energy... recycle electrons!
@transparent The glycol is for the separate solar thermal water heating system not the ashp.
🤣 🤣 🤣
@cathoderay I’ve just realised the date on the control panel is now correct but the time isn’t. Could you tell me how to change the time please. I have looked through the user information and cannot find it. Thank you.
- 26 Forums
- 2,129 Topics
- 46.8 K Posts
- 22 Online
- 5,654 Members
Join Us!
Podcast Picks
Latest Posts
-
@old_scientist yes, assumptions are crucial. For many p...
By Tim441 , 2 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
That's the sort of good design we would expect from Tes...
By Transparent , 30 minutes ago
-
RE: ASHP heat output monitoring
@carlo I have a 16kw LG Therma V. Installed 2020 so eve...
By Tim441 , 56 minutes ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@morgan They may be good but cannot service the heat pu...
By dgclimatecontrol , 1 hour ago
-
RE: Mitsu Wireless Controller and MelCloud
@davidalgarve If they are 'off' because of a timed s...
By Morgan , 3 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 2 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 3 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 3 days ago
-
RE: Who has a V2G EV installation
I agree, but a word of caution. V2X is also sometimes u...
By Majordennisbloodnok , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 1 week ago