Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
ASHP choice help - 55C flow temperature required
apologies if others have covered...
is your total heat loss really 43kW? That's huge; the biggest domestic ASHP I've seen is 16kW.
55 degrees is high for any ASHP; most will do it but the COP isn't going to be a lot better than 2, even with the ones touted as HT. I think (don't know for sure) that while these units can do high temperatures, the COP is not necessarily better than 'normal' units. My ASHP (14kW Ecodan) will output 55 degrees all day at -2 but the COP will be around 2. One thing you rightly pointed out is to be careful with defrosts, which will lose you at least 10-15% of capacity below 2-3 degrees ambient. Also be careful with the rated outputs; they are often lower than the badged value at low ambients.
Remember an ASHP can only output at one LWT at a time. If the upstairs doesn't need 55 degrees LWT then you might be better with one for the downstairs and another for everything else. If your heat loss really is 43kW you're going to need multiple (or commercial grade) ASHPs anyway.
Finally, I don't know much about ufh but you do have to make sure it can emit enough heat at the flow rates an ASHP needs, which are normally higher than gas/oil systems.
Hi – I have a 16kW Daikin HT ASHP – system details below – which we’ve been running since August 2020. We have a combination of UFH and radiators. The system we have can only be used with a basic Daikin controller which gives no information on consumption or COP. I’ve managed by a process of elimination to work out consumption data and to date the heating consumption (not incl. DHW) is as below. Heating has been off since the start of April, and I’ve used this past winter’s figures for this next winter:
During 2021 and early 2022 we were using the system as if it was a gas boiler, doing everything wrong – room stats and zoning, running at high temperatures (there’s a blending valve on the UFH), no weather comp. It coped and was happy producing LWTs up to 70 or so for the radiators (!) but was obviously very thirsty in terms of consumption. This past winter with the help of the folks on this forum I’ve corrected these errors and obviously seen a big difference in consumption. I’m not actually running the HT capabilities of the system now but the house is quite comfortable; we possibly didn’t need a HT system but that’s what was recommended and we are just trying to run it as efficiently as possible.
I realise this doesn’t help much with the topic specifically but just wanted to add some insight into my Daikin HT journey particularly in respect of consumption. I’m more than happy to answer any queries about our experiences with the Daikin HT system.
System details:
- An outside unit - Daikin ERRQ016AAV1
- An inside unit - Daikin EKHBRD016ADV17
- A 500L thermal store - Daikin EKHWP500PB (no immersion heater installed)
- A very basic Daikin controller EKRUAHTB
- Manufacturer stated COP’s are 2.11 at -7, 3.01 at 2, 4.26 at 7, and 4.67 at 12C
- We have a 6.1kWp PV installation with 20 SW-facing panels and a SolarEdge SE6000H 6kw inverter, which produces around 8MWh pa, 3MWh of which goes back to the grid
Many thanks for the helpful responses.
@marzipan71 I'm still struggling to get figures out of Daikan. It's mystifying to me that suppliers aren't more transparant as to the key performance parameters of their products. Do you know what the LWT is for those COP figures?
@kev-m apologies - that heat loss figure was not quite right. The total heat loss in the rooms we use (!) is 18,000. But 5 of those are bedrooms, which are in practice scarcely heated, and even then only for a short time in the morning and evening.
For anyone interested, this is the result of my researches to date:
I am slightly surprised that there isn't a closer relationship between these COPs and the MCS SCOP figures, but of course they only cover a small part of the device characterisitics.
My current plan (it changes daily) is to go with a pair of Arotherm Plus 7kW pumps - one dedicated to the UFH and the other for rads around the house. I will post separately about my slightly eccentric DHW plans, because it would be great to get some input on those.
Stiebel Eltron WPLA07 7kW ASHP. 26 x 400W PV. 10kW Sunsynk 3-phase inverter. 6 x 4.8kWh Pylontech US5000C batteries.
@wintergreen here's what I have - apologies if it's too small to read. I was left two sheets by the installers - with completely different COP figures for the same pieces of kit! First file has the figures I quoted above. Agree about difficulty getting data - I have no way of monitoring COP via my controller as other users are able to do with their kit.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 387 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 3 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 4 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 6 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 7 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 9 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 9 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 10 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 10 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 13 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 13 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 14 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 15 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 15 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 16 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago