Mitsubishi PUHZ-SW120 ASHP & Buffer Tank
Ok well in that case I defer to the more detailed comment by @johnmo above.
There are ways to fix the pump capacity (if it's actually a problem).
If the buffer tank is unbalanced then it is reducing efficiency, roughly 3% per degree C measured between flow in from the heat pump, and flow out to the radiators, that's just a fact.
I would measure the difference above (mid season) and then decide whether the cost matters to you. If it does then insist on a change.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@johnmo
That is a different concept to that I was trying to get across in my broken Portugese sprinkled with English. I was hoping to ditch the secondary pump because:
1 It is a PWM pump without the variable speed facility. The local Grundfoss agent says it should not have been used, but I think because it is old rather than necessarily it's performance curves
2 It is using power, so presumably wasteful
Just to confirm - I have no house thermostat and work entirely on weather compensation
I cannot check until we get to colder temperatures, but I seem to recall that the secondary pump is not controlled by the Hydrobox, i.e. runs all the time.
I will check its electrical connection tomorrow
Posted by: @davidalgarve@johnmo
That is a different concept to that I was trying to get across in my broken Portugese sprinkled with English. I was hoping to ditch the secondary pump because:
1 It is a PWM pump without the variable speed facility. The local Grundfoss agent says it should not have been used, but I think because it is old rather than necessarily it's performance curves
2 It is using power, so presumably wasteful
Just to confirm - I have no house thermostat and work entirely on weather compensation
In addition to any response from @johnmo please read my post above which gives you some way to determine how much it matters . If the power consumption of the second pump is a concern so the arithmetic to see if it's significant. Central heating pumps are usually 50W or less.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I was almost using your piece above as my script to explain what I wanted to do. I had even done a translation into Portuguese, but I had no answer to the possible inadequacy of the inbuilt Mitsubishi pump
Posted by: @davidalgarve@jamespa I was almost using your piece above as my script to explain what I wanted to do. I had even done a translation into Portuguese, but I had no answer to the possible inadequacy of the inbuilt Mitsubishi pump
Unfortunately the plumber may be right, or he may not. Without doing the calculations (or the experiment) it's impossible to tell.
However more or less any plumber should be able to do these calculations and show you the answer. If the Mitsubishi pump isn't adequate then it needs to be supplemented or replaced.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Comparing your heat pump, circulation pump and the secondary pump curves they are very similar. So assuming the heat pump isn't 10s of metres away there should be no issues deleting the secondary pump and buffer.
@johnmo I have checked the connection of the secondary pump and it is on "Out 2" which is designated for "Pump 2 - Zone 1". Strangely "Out 1" designated for "Heating and DHW" has no connections.
I am a little uncertain how you are comparing the EHSC pump, (for which I previously provided the curves), with the secondary, Grundfos UPM@ 25-70 180.
I am attaching the curves I have found for the latter and if I do one comparison on the max speed curve at 40kPa on the EHSC and 4.07mH on the Grundfos (which I believe are the same), the EHSC pump delivers 22l/min and the Grundfos delivers 38l/min.
However, my 87 year old brain doesn't cope well with more modern units so perhaps I am entirely wrong.
I dont know what speed the secondary pump runs at because the PWM control is missing, but it is not so noisy so I suspect not at maximum. If I were to go ahead and accept the lower flow rate from the EHSC pump, would that be a disaster?
Posted by: @davidalgarveEHSC pump delivers 22l/min
No that is 2.2 m³/h, so 2200L/60 mins, is 36.66L/min. So the head flow curve is just about identical on speed 5 and max flow on the secondary pump.
If you need to operate at 4 bar head loss you have major issues.
Posted by: @davidalgarvedont know what speed the secondary pump runs at because the PWM control is missing,
Should be full speed i.e. top running curve.
Posted by: @davidalgarveStrangely "Out 1" designated for "Heating and DHW" has no connections.
You have a diverter valve upstream of the buffer which takes care of the DHW heating flow.
@johnmo Thanks for the correction and it sounds promising. I have no idea what head loss I am working at and don't know what the flow rate is, so would it be useful to measure the current drawn by the pump? I don't have a current vs head graph for the EHSC pump, but could, perhaps, use the Grundfos graph as an indicator.
Posted by: @davidalgarvedon't have a current vs head graph for the EHSC pump, but could, perhaps, use the Grundfos graph as an indicator.
Think looking at the two curves, you will be near enough using the Grundfos one.
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 145 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@mosibi — I, and I suspect others, am interested to kno...
By cathodeRay , 18 minutes ago
-
RE: Electricity price predictions
Is the distance between those new farms and where the e...
By Batpred , 9 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa hopefully after the rad balancing it will perf...
By AdamK , 9 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
@davidnolan22 Hi, ok first of all it very hard to truly...
By ASHP-BOBBA , 12 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Installers coming tomorrow. One has messaged messaging ...
By Crimson , 12 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
11.2kW Ecodan Manufacturer: Misubishi Model: PUZ-WM...
By DRB01 , 12 hours ago
-
RE: Homely asking about Solar Panels.
@majordennisbloodnok I will report back with any develo...
By Toodles , 15 hours ago
-
RE: Mediation with RECC, what's your experience?
@editor Thank you, I really appreciate it! I've made ...
By TreeWizard , 17 hours ago
-
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Are you able to post a photo of that 180-litre cylinder...
By Transparent , 19 hours ago
-
Agreed. It doesn't take all that much maintenance to ke...
By Majordennisbloodnok , 21 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 22 hours ago
-
RE: My DIY Heat Pump installation
@pollar-bear Top job, I installed my own too and even t...
By bontwoody , 23 hours ago
-
RE: Who has a V2G EV installation
Not sure how you got that information, @batpred. As of ...
By Majordennisbloodnok , 24 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 2 days ago
-
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 2 days ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 2 days ago
-
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 2 days ago