Mitsubishi PUHZ-SW120 ASHP & Buffer Tank
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Ok well in that case I defer to the more detailed comment by @johnmo above.
There are ways to fix the pump capacity (if it's actually a problem).
If the buffer tank is unbalanced then it is reducing efficiency, roughly 3% per degree C measured between flow in from the heat pump, and flow out to the radiators, that's just a fact.
I would measure the difference above (mid season) and then decide whether the cost matters to you. If it does then insist on a change.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@johnmo
That is a different concept to that I was trying to get across in my broken Portugese sprinkled with English. I was hoping to ditch the secondary pump because:
1 It is a PWM pump without the variable speed facility. The local Grundfoss agent says it should not have been used, but I think because it is old rather than necessarily it's performance curves
2 It is using power, so presumably wasteful
Just to confirm - I have no house thermostat and work entirely on weather compensation
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
I cannot check until we get to colder temperatures, but I seem to recall that the secondary pump is not controlled by the Hydrobox, i.e. runs all the time.
I will check its electrical connection tomorrow
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @davidalgarve@johnmo
That is a different concept to that I was trying to get across in my broken Portugese sprinkled with English. I was hoping to ditch the secondary pump because:
1 It is a PWM pump without the variable speed facility. The local Grundfoss agent says it should not have been used, but I think because it is old rather than necessarily it's performance curves
2 It is using power, so presumably wasteful
Just to confirm - I have no house thermostat and work entirely on weather compensation
In addition to any response from @johnmo please read my post above which gives you some way to determine how much it matters . If the power consumption of the second pump is a concern so the arithmetic to see if it's significant. Central heating pumps are usually 50W or less.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I was almost using your piece above as my script to explain what I wanted to do. I had even done a translation into Portuguese, but I had no answer to the possible inadequacy of the inbuilt Mitsubishi pump
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @davidalgarve@jamespa I was almost using your piece above as my script to explain what I wanted to do. I had even done a translation into Portuguese, but I had no answer to the possible inadequacy of the inbuilt Mitsubishi pump
Unfortunately the plumber may be right, or he may not. Without doing the calculations (or the experiment) it's impossible to tell.
However more or less any plumber should be able to do these calculations and show you the answer. If the Mitsubishi pump isn't adequate then it needs to be supplemented or replaced.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Comparing your heat pump, circulation pump and the secondary pump curves they are very similar. So assuming the heat pump isn't 10s of metres away there should be no issues deleting the secondary pump and buffer.
@johnmo I have checked the connection of the secondary pump and it is on "Out 2" which is designated for "Pump 2 - Zone 1". Strangely "Out 1" designated for "Heating and DHW" has no connections.
I am a little uncertain how you are comparing the EHSC pump, (for which I previously provided the curves), with the secondary, Grundfos UPM@ 25-70 180.
I am attaching the curves I have found for the latter and if I do one comparison on the max speed curve at 40kPa on the EHSC and 4.07mH on the Grundfos (which I believe are the same), the EHSC pump delivers 22l/min and the Grundfos delivers 38l/min.
However, my 87 year old brain doesn't cope well with more modern units so perhaps I am entirely wrong.
I dont know what speed the secondary pump runs at because the PWM control is missing, but it is not so noisy so I suspect not at maximum. If I were to go ahead and accept the lower flow rate from the EHSC pump, would that be a disaster?
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @davidalgarveEHSC pump delivers 22l/min
No that is 2.2 m³/h, so 2200L/60 mins, is 36.66L/min. So the head flow curve is just about identical on speed 5 and max flow on the secondary pump.
If you need to operate at 4 bar head loss you have major issues.
Posted by: @davidalgarvedont know what speed the secondary pump runs at because the PWM control is missing,
Should be full speed i.e. top running curve.
Posted by: @davidalgarveStrangely "Out 1" designated for "Heating and DHW" has no connections.
You have a diverter valve upstream of the buffer which takes care of the DHW heating flow.
@johnmo Thanks for the correction and it sounds promising. I have no idea what head loss I am working at and don't know what the flow rate is, so would it be useful to measure the current drawn by the pump? I don't have a current vs head graph for the EHSC pump, but could, perhaps, use the Grundfos graph as an indicator.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @davidalgarvedon't have a current vs head graph for the EHSC pump, but could, perhaps, use the Grundfos graph as an indicator.
Think looking at the two curves, you will be near enough using the Grundfos one.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 280 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Power outages and storms: A surprisingly good DNO experience
@majordennisbloodnok honestly, it was genuinely refresh...
By Mars , 2 minutes ago
-
RE: Setback savings - fact or fiction?
As far as I am aware, the majority, if not all, of the ...
By cathodeRay , 7 minutes ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Fair point. The highest frequency of defrosts I'd seen...
By Sheriff Fatman , 11 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 11 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick interesting update - thanks.I've been thr...
By Tim441 , 12 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I remember reading in some inverters. They mandate a se...
By Batpred , 13 hours ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 14 hours ago
-
RE: Running from backup generaor in powercut?
@majordennisbloodnok Back in the 80’ or 90’ we had a te...
By Toodles , 14 hours ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 15 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 16 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Great to hear! I just figured this out a day or tw...
By anotherdaveuk , 17 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 22 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 2 days ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 2 days ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 3 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 3 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 3 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 3 days ago