Posted by: @notechknowhow

@derek-m Further to your suggestion of tracking down the 3 way valve I came across these three items on the journey and wondered what was the function of each? 

 

IMG 6152
IMG 6154
IMG 6155

 

The first photo is of the bypass valve. Bypass valves were installed in systems containing TRV's, to prevent the water pump actually pumping against a dead end if all the TRV's fully closed. In heat pump systems it is better if both TRV's and a bypass valve are not installed. Since the bypass valve has already been installed it should be set at the highest setting.

The system is pressurised hence the need for a pressure gauge. The required operating pressure is normally in the 1 bar to 2 bar range.

The third photo shows a filter. This should be checked periodically for particle build-up.

 


   
Mars reacted
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13609 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4153
 

@notechknowhow

If as you state the solar PV system was not installed until 2020, then it will not qualify for FIT payments.

There may be an electrical power meter installed in the cabling from the solar PV inverter to your consumer unit, but would only actually be required if the system had been registered for FIT payments.


   
Mars reacted
ReplyQuote
(@notechknowhow)
Trusted Member Member
130 kWhs
Joined: 4 weeks ago
Posts: 27
Topic starter  

@guthrie thank you - will check which pipe pressure gauge is on. The pressure release is as you say labelled Auto bypass.


   
ReplyQuote
(@notechknowhow)
Trusted Member Member
130 kWhs
Joined: 4 weeks ago
Posts: 27
Topic starter  

@derek-m Thank you all. As you've all pointed out given the date of installation it can't have been registered for the FIT scheme.


   
ReplyQuote
(@notechknowhow)
Trusted Member Member
130 kWhs
Joined: 4 weeks ago
Posts: 27
Topic starter  

@derek-m Thank you. Looking again at the photo the pressure release valve looks like it is set at 0.5 which also looks is the highest setting (?).


   
ReplyQuote
(@notechknowhow)
Trusted Member Member
130 kWhs
Joined: 4 weeks ago
Posts: 27
Topic starter  

@derek-m Jamespa, Derek-m, Bontwoody, Guthrie, Toodles, Mars, Majordennisbloodnok, thank you for your help to date.

The ASH is now up and running again. Does anyone know of 'An idiots Guide to PV / ASH / Thermal Solar' book that's out there?  

 

kind regards Andy @ NoTechKNowHow


   
ReplyQuote



(@bontwoody)
Prominent Member Contributor
2816 kWhs
Joined: 2 years ago
Posts: 402
 

@notechknowhow

I dont sorry Andy, but your order of priority would be to heat as much as your hot water via the solar thermal first, then the diverter or heat pump (depending on the export rate). The problem with solar thermal is that its not versatile like electricity and can only do one thing, plus its very heavily dependant on sun so not a lot of use in the winter. That said its the most efficient way of turning sunshine into heat!

However if its out of commision it might not be worth spending a lot of money getting it working again due to the very long return of investment.

You may find like me that the solar diverter isnt a lot of use either because I can heat more cheaply using my immersion at night and export surplus electricity at a higher rate during the day. (I have an EV and get a very low overnight rate)

Its often all very individual depending on circumstances and you may have to do some number crunching to see whats the best way forward for you. The good news is that you have all the kit to choose from! (Except a wind turbine-Im still doing the numbers on that!)

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@jamespa)
Noble Member Member
4162 kWhs
Joined: 1 year ago
Posts: 692
 

Posted by: @bontwoody

@notechknowhow

I dont sorry Andy, but your order of priority would be to heat as much as your hot water via the solar thermal first, then the diverter or heat pump (depending on the export rate). The problem with solar thermal is that its not versatile like electricity and can only do one thing, plus its very heavily dependant on sun so not a lot of use in the winter. That said its the most efficient way of turning sunshine into heat!

However if its out of commision it might not be worth spending a lot of money getting it working again due to the very long return of investment.

You may find like me that the solar diverter isnt a lot of use either because I can heat more cheaply using my immersion at night and export surplus electricity at a higher rate during the day. (I have an EV and get a very low overnight rate)

Its often all very individual depending on circumstances and you may have to do some number crunching to see whats the best way forward for you. The good news is that you have all the kit to choose from! (Except a wind turbine-Im still doing the numbers on that!)

Agreed.  I expanded on this and related matters a bit in an earlier post of mine.  You may want to re-read now the basics are done and I'm happy to answer questions.

https://renewableheatinghub.co.uk/forums/postid/29607

This post was modified 4 weeks ago 2 times by JamesPa

   
ReplyQuote
(@bontwoody)
Prominent Member Contributor
2816 kWhs
Joined: 2 years ago
Posts: 402
 

@jamespa apologises, I did virtually paraphase everything you said earlier 🤣 

@notechknowhow as James mentioned, it might be a good idea to contact the previous owners, certainly I couldnt tell my purchasers enough of what I had done and probably bored them senseless!

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@jamespa)
Noble Member Member
4162 kWhs
Joined: 1 year ago
Posts: 692
 

Posted by: @bontwoody

@jamespa apologises, I did virtually paraphase everything you said earlier 🤣 

@notechknowhow as James mentioned, it might be a good idea to contact the previous owners, certainly I couldnt tell my purchasers enough of what I had done and probably bored them senseless!

No I apologise.  I didn't mean to quote you I meant to quote OP (perils of working on a mobile phone!) - ie the comment was meant to help OP not as some sort of veiled criticism of you

 


   