Anyone taken a thermal image of their ASHP condenser unit?

16 Posts
4 Users
5 Reactions
2,520 Views
(@heat-pump-newbie)
Reputable Member Member
1458 kWhs
Joined: 3 years ago
Posts: 166
Topic starter  

No, it's R32. A split system so it's pumped from the outdoor unit up the outside wall to the indoor unit in the loft.


   
ReplyQuote
(@saenergy)
Trusted Member Member
126 kWhs
Expert
Joined: 3 years ago
Posts: 17
 

if you have witnessed a refrigerant leak then the system will need to be thoroughly checked.  The joints are flared and should seat perfectly.  If they don’t and it leaks you have a dead system. 

These units a preloaded for a run of up to 15m (generally).  So in a short run you might be ok in terms of refrigerant load.  

however, and this is the important bit.  If refrigerant got out, then it is highly likely that moisture and or air got in.  These are non compressible and will cause a fault.

the best course of action is to have a proper fridge engineer come out and follow the service procedure to recover the refrigerant, fully nitrogen load and vac test the system.  Then add the correct amount of refrigerant for the system.  The preload amount should suffice unless it’s a long run. 

the risk of not doing this are not just reduced COP but total compressor failure.  

That banding is not a good thing. 

Internationally recognised award winning installer of heat pumps and stuff


   
👍
1
ReplyQuote
(@heat-pump-newbie)
Reputable Member Member
1458 kWhs
Joined: 3 years ago
Posts: 166
Topic starter  

Ooh @seaenergy that's a bit worrying !!! I'll have another go at my installer then. Thanks very much for you advise. It's been running like that for over a year now - is it in trouble ?

I've sent an email to my installer to remind them that I asked about this at the service last April.


   
ReplyQuote



(@saenergy)
Trusted Member Member
126 kWhs
Expert
Joined: 3 years ago
Posts: 17
 

@heat-pump-newbie I would want it properly checked out.  If there is a refrigerant leak it’s rarely a good thing.  You could be very lucky and it’s all good.  

The banding can happen for a number of reasons, the bottom coils for example sometimes use a base heater to heat them as that’s the part of the coils that gets the least heat recovery in defrost cycle.  

I expect having it properly checked is cheaper than a new unit   A lot of installers are not AC guys, when I do split units I bring in a specialist company to do the refrigerant pipework.  They may need to get someone in to do the job properly.  

 

Internationally recognised award winning installer of heat pumps and stuff


   
👍
1
ReplyQuote
Page 2 / 2
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security