No, it's R32. A split system so it's pumped from the outdoor unit up the outside wall to the indoor unit in the loft.
if you have witnessed a refrigerant leak then the system will need to be thoroughly checked. The joints are flared and should seat perfectly. If they don’t and it leaks you have a dead system.
These units a preloaded for a run of up to 15m (generally). So in a short run you might be ok in terms of refrigerant load.
however, and this is the important bit. If refrigerant got out, then it is highly likely that moisture and or air got in. These are non compressible and will cause a fault.
the best course of action is to have a proper fridge engineer come out and follow the service procedure to recover the refrigerant, fully nitrogen load and vac test the system. Then add the correct amount of refrigerant for the system. The preload amount should suffice unless it’s a long run.
the risk of not doing this are not just reduced COP but total compressor failure.
That banding is not a good thing.
Internationally recognised award winning installer of heat pumps and stuff
Ooh @seaenergy that's a bit worrying !!! I'll have another go at my installer then. Thanks very much for you advise. It's been running like that for over a year now - is it in trouble ?
I've sent an email to my installer to remind them that I asked about this at the service last April.
@heat-pump-newbie I would want it properly checked out. If there is a refrigerant leak it’s rarely a good thing. You could be very lucky and it’s all good.
The banding can happen for a number of reasons, the bottom coils for example sometimes use a base heater to heat them as that’s the part of the coils that gets the least heat recovery in defrost cycle.
I expect having it properly checked is cheaper than a new unit A lot of installers are not AC guys, when I do split units I bring in a specialist company to do the refrigerant pipework. They may need to get someone in to do the job properly.
Internationally recognised award winning installer of heat pumps and stuff
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 60 Online
- 2,276 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 8 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 35 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 57 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 1 hour ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 3 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 22 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 24 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago