Good morning all,
After months of problems and complaints, I finally have a formal report from LG categorically stating that our 9kw heat pump is undersized for our 2700 sqft home - which is why we cannot heat the rooms in weather with temperatures below 4° and why the pump is so horribly noisy in those conditions as it is under significant strain and working at full capacity 24/7 to try to do so.
This is fantastic progress, but what now? I'm about to approach the developer who built my new build property, but does anyone have any advice or knowledge of laws concerning sufficient heating systems? I need to make sure the builder and Omnie, who designed the underpowered system and have always maintained there's nothing wrong with it (although could never explain why my home wouldn't heat above 16.5° all winter) have no wriggle room and recognise their legal obligations.
Do I need to engage a solicitor? What should I do in the first instance?
Help!
Sam.
Sam,
do you know if RHI is being claimed by the developer (I assume it isn't by you)? If so they would have to have filled in an MCI calculation and submitted it to OFGEM. That should ensure the sizing is correct. It'd be worth asking them for this or anything else they used to size the system.
Kev
Have LG confirmed what size ASHP is suitable?
Do you have access to the system data showing flow rates/temps etc? It would be interesting to see the flow temp when the ambient temp is sub 4 degrees to see when every zone is calling for heat what it is actually flowing at.
If I switch on every single zone/radiator on our system it will only flow at 37-40 max. Is your property all radiators or a mix of UFH and radiators?
Mitsubishi Ecodan 14kw ASHP + 500l Cylinder
@kev-m, do you know if there's a way of searching the MCS database?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Sam,
As suggested previously, have you been in touch with trading standards or consumer protection? They would probably be able to point you in the correct direction.
You should also get in touch with MCS, their helpline number is 0333 103 8130.
Personally I would not go down the route of getting a solicitor just yet, keep that as a last resort.
Your local MP may also be of assistance, since the government want us all go 'green'.
Hope this helps.
Regards,
Derek.
@derek-m, I completely agree with you. The first point of attack would be MCS, but the only thing I'm unsure of (which I think Sam informed me of) is that the installers weren't MCS accredited. If they're not, there's not much recourse there. Sam can correct me if I've remembered this incorrectly. A phone call should clarify this. Also, if they were MCS accredited, there'll be insurance in play which Sam can use to get the matter resolved. Our MCS certificate states that we're insured by HEIS, and they'll put right any problems.
Trading standards and consumer protection is also a good course of action to pursue as a next step.
The solicitors play is a last resort in most cases, because of the money involved, but negligence and incompetence shouldn't be that difficult to prove, given that LG have now issued a formal report stating the incorrect size heat pump was installed.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
A quick looks suggests the MCS data is available but you need to ask for a login
https://certificate.microgenerationcertification.org/
Hi,
Mars, unfortunately you are correct. We do not have an MCS certificate. I've been advised to contact the builder with the report quoting the 2015 consumer rights act.
I suppose my main concern is that Omnie will simply write a report stating it is big enough.
Sam
I don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
@sam, I would demand the heat loss and emitter calculation from Omnie. If they say that the heat pump is the correct size, they must provide the evidence to back that up, and the only way to do that is to share the aforementioned calculations.
I can't remember if you told me this, but have you called MCS and verified from them that there isn't a MCS certificate for your property?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @samI don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
I missed this earlier comment. Is the calculation from the LG technician, not Omnie?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Rodents! A word of warning for heat pump owners
2 weeks ago
-
Surface mount or bury primaries for heat pump installation?
3 months ago
-
UFH and ASHPs
4 months ago
-
Installing your own ASHP - DIY
5 months ago
-
ASHP install contract and BUS grant money
6 months ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 31 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Damage on install - useable or dealbreaker?
They have already been dishonest by not telling you abo...
By GrahamF , 6 hours ago
-
Testing new controls/monitoring for Midea Clone ASHP
Hi all, I thought it might be of interest to others i...
By benson , 6 hours ago
-
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 8 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 9 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 10 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 11 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 13 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 14 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 15 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 16 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago