Sorry not to reply before, have been offline for a few days.
Grant sent an engineer to check out our system.
No leaks found although some aspects of our installation could not be inspected (such as the conduit running from the ASHP to the house).
Pressure at the heating expansion tank was checked and found to be OK (and I was told the expansion tank pressure gauge is indeed not working).
Hot water problem fixed. Timing of heating and water has to be aligned as ASHP can't heat both at once (this is normal). Engineer set heating to go off when water is on. But he did this by setting the heating timer to off. This cuts power to the room thermostats so they no longer show the correct date and time. I think I need to cut the call for heat by leaving the heating timer always on but setting the room thermostats to a low level during periods when the water is timed to go on. I will leave for now but need to change the timing and temperature sequence on each individual room thermostat - which is a pain.
I showed engineer photos of our system being installed. He questioned the spacing (not close enough) of the heating loops in the floor. Not conclusive but even if wrong clearly cannot be changed.
He confirmed that the ASHP itself is working correctly.
Action for me:
- Find another engineer to do regular servicing and maintenance. Grant's own man was the best yet but this was a one off and I think they normally only outsource.
- Fix faulty gauge and a relief valve which did leak but is screwed down. Grant suggested to contact my installer but as documented before they are no longer MCS registered or do heat pump systems.
- Get an electrician to replace the ASHP supply cable which is not external grade wiring. Also to install a meter on that supply so I can see how much power the pump alone is drawing. At present I can only measure total household usage.
- Try and get the bathroom radiators to heat all the time (this has been the least of my problems).
Overall power usage this month has been similar to last year (about 25% more than May 2019) but it has been an unseasonally cold May. Now the weather is finally warming I see usage dropping to about 23kWh per day which is in line with May 2019. But the big savings from getting the system right come between October and March. Our rolling 12 month total usage is still distorted by the horrendous January figures. But now down to 15,300kWh from 15,900kWh in January. But at this point in 2019 it was only 11,800kWh. With a 150 sqm house we are at roughly 100kWh per sqm p.a. As an aside I just saw some figures for a Passivhaus suggesting as little as 27kWh per sqm p.a. Scarcely believeable - must exclude power and lighting.
Mike
Grant Aerona HPID10 10kWh ASHP
Hi @Mike
Did I read that right, your avg. daily kWh for May is 23kWh? If you don't mind me asking, how many people are living at home?
Whilst May has been a bit of a damp squid for us, in our house which is approx. 130 square meters we're averaging 7.3kWh per day for May - we're due in October and no doubt will see our winter usage increase vs last year.
I was unaware that ASHP’s are incapable of heating water and radiators simultaneously. Really?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Since our ASHP installation on 21st April we’ve used 234kWh or 6.69kWh per day. Hot water is heated via solar PV and electric diverter. There have been a few cooler nights when the Daikin has kicked in for heating, but otherwise the ASHP is effectively off now until, I would guess September.
Against the MCS estimates, I’ve used double the electric prediction, so perhaps April/May were colder than I thought? Or the Estimates wrong 😳🤞
@mike-patrick I’m glad you had Grant engineer out to review your system. Can’t Grant suggest a reputable trained engineer through their network? Did you take out or do Grant offer a support contract? One of the reasons I picked Daikin is their annual support contract, fixed for 10 years. £234 includes annual service and all spares and labour per year.
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and new Hyundai Ioniq 5 N electric vehicles with Myenergi Zappi mk1 charger
Yes that's right.
The best figure we have ever had was avg 16kWh per day in July 2019.
That is total power usage for 2 people. So includes cooker, washing machine , tumble drier, everything.
We don't have PV just the heat pump.
Mike
Grant Aerona HPID10 10kWh ASHP
I don't believe there is a support contract with Grant.
Our installer ( 4 years ago) didn't even register the system with Grant and I've been playing catch up.
Mike
Grant Aerona HPID10 10kWh ASHP
@dant if it’s a dark or overcast day, then no, I have run the ASHP overnight on our cheap Octopus Go tariff (it is set up as such to heat to 80% if the cylinder drops below 30%). Or if my wife or daughter have a 3hr shower 🤪
But 90% of the hot water is via PV (same as before the ASHP).
Solar thermal would be slightly more efficient at heating water on overcast days, but I’ve read previously that when they fail, it’s difficult to get parts or maintenance. One connector fused on my solar PV in 9 years and my regular electrician diagnosed and sorted it for £50.
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and new Hyundai Ioniq 5 N electric vehicles with Myenergi Zappi mk1 charger
@julianc, that's a very low usage. Our heating is about 17kWh per day over the same period. What sort of temperature do you have your house? Our ASHP has been on in the morning and evening every day so far. Are you saying your MCS estimate was only 3-4 kWh per day for April/May. That seems extremely low.
We have a Nest thermostat in the hallway. Set at 17.5 in mornings. Goes to 18 to 19.5 in the evening. We have tweaked it to 20 a couple of times. And adjusted the TRVs in the dining room up when ate in there.
The radiators haven’t got as hot as the old oil boiler days, but the Nest switches off as it has reached temperature.
We do wear wool jumpers in the home 😉
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and new Hyundai Ioniq 5 N electric vehicles with Myenergi Zappi mk1 charger
@kev-m for the same period, so the 21st April - 25th May, we have used 275kWh, an average of 7.8kWh per day.
The heating hasn't been on really, maybe one or two days. The house is usually between 18-20, the odd day when the heating did come on it had dropped to 17.5 degrees in the living room.
-
ASHP install contract and BUS grant money
6 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Heat Pump starting current
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 56 Online
- 2,276 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 7 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 34 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 57 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 1 hour ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 3 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 22 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 24 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago