Adding Dedicated Immersion Heater Element
Vaillant AroTherm ASHP with VRC 700 controller. We have the cheap overnight tariff (5hours). During the winter the system works best if heating is separated from DHW. Therefore I time the UFH and upstairs to operate during the low tariff schedule. The DHW is timed to operate during the dearer period.
I am thinking of replacing the current immersion with the T-smart immersion and run it independently (i.e during the low tariff). At present the wiring to the immersion is obviously controlled and operated by the VRC700.
My question, what will be the outcome if a) an electrician disconnects the wiring into the immersion (currently supplied by VRC700) and replaces with dedicated immersion spur to operate the T-smart or b) he connects both cables (doubles up) thereby having a dual supply to the immersion (although only the T smart will actually be used. I don’t want to purchase the T-smart if this is a non starter, i.e could throw the VRC 700 into fault mode or something else.
Our DHW is normally 39deg and heated to 50 deg so the T-smart should, I assume easily cope with the temp increase during the 5 hours and of course the Legionella run.
Thanks.
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 121 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 2 hours ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 3 hours ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 15 hours ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 2 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 3 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 5 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 6 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 6 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 6 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 6 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago