A new install (Ecodan?) with solar thermal
Hi all
I considered installing a heat pump 10 years ago, but didn’t go through with it as the information I could find was rather mixed – but am now considering it again with the help of all the additional years’ worth of internet opinionating, which is still mixed!! I have found myself on a considerable learning curve in order to understand what the end result should perform like, though not entirely confident of applying what I read here and elsewhere to my own situation and making suitable critical assessment of the input from potential installers.
So far I have managed to get one quote and am waiting on another, but who knows if that will appear. ( I am not really counting the one that was a pretty much a pro forma quote done via email). The quote I do have came with some work on heat loss figures that tell me that at -2.5C the value is 7.3kW, I have had a stab at my own heat loss figures via a couple of websites, particularly the EST one, and they seem to concur. On this basis they have recommended an 8.5kW Ecodan. This size of heat pump seems to be just about capable enough, but I see others on here would oversize the pump further – and have just read the interesting front-page piece that explains why the nominal rated value is not the achieved value.
I have seen a couple of posters whose houses seem to be only a bit bigger then mine who do have higher-rated pumps, so I think I need to question the choice hard.
We are in an early 1970s 3-bed detached house, a one-off build and it seems pretty well constructed, 125sqm total area, and is now well-insulated (filled cavity walls; double glazing - some of which was replaced about 4 years ago; plenty of loft and ceiling insulation; and about half the ground floor has insulation). Rads only, and about four of these will need to be upsized according to the heat loss calcs. The house is currently heated by gas boiler at a usage of about 13000kWh per year. I believe this is an average size gas bill but presumably on the low side considering it is a detached house. I am not expecting an ASHP to be cheaper to run (certainly not with the current tariff we are stuck with at the moment) but it needs to be effective and efficient to be the environmentally worthy investment we are looking for.
Winter months can see 2000kWh + used so theoretically that should be achievable with around 800kWh of electric input – I am trying to not get too spooked by reading about usages of 75kWh+ per day, not to mention the other issues that some have with their setups.
We also have solar PV and thermal to throw into the mix. The solar thermal currently feeds a 250l heat store with gas boiler backup. I don’t know how much heat the thermal generates, I have been disappointed that it only fully heats the entire store to 55 on a handful of days so I can see a PV diverter to the tank immersion is perhaps overdue. In theory with both solar thermal and PV the less efficient HW generation by the ASHP *should* be relatively small.
But I have not got very far with understanding how the thermal generation will integrate with control and timings of the heat pump. The company that have provided the quote have not been clear on this – indeed the tank that they have referred to does not even have a solar coil! I have been reading instructions as part of my education and though the Ecodan/MELcloud application seems very accessible and well-endowed it is very much heat pump specific. The Vaillant controls on the other hand also cover solar thermal systems.
I would be interested to know of others’ experiences with running both heat pump and solar thermal together.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Welcome to the forum.
This is a simple straightforward check of your present heat demand utilising your present system. If possible gradually turn down the water flow temperature of your gas boiler and see how low you can get the temperature before the indoor temperature cannot achieve the setpoint. Also record the daily gas consumption and weather conditions to see how the heat demand varies. If you find that you need quite a high water flow temperature to supply the heat demand, this would indicate that some of your heat emitters may need to be upgraded.
I do believe that hot water tanks are available with twin heating coils and an immersion heater, so you could probably provide the vast majority of your hot water, using solar PV via a diverter unit, solar thermal to one of the heating coils and a feed from your ASHP to the second heating coil.
I have attached a spreadsheet, which although for a 14kW Ecodan, can provide you with some idea of how the heat demand and heat pump efficiency with varying ambient air temperatures. You can also see the effect of adding more insulation, upgrading the heat emitters and varying the desired indoor air temperature.
Posted by: @harriupHi all
I considered installing a heat pump 10 years ago, but didn’t go through with it as the information I could find was rather mixed – but am now considering it again with the help of all the additional years’ worth of internet opinionating, which is still mixed!! I have found myself on a considerable learning curve in order to understand what the end result should perform like, though not entirely confident of applying what I read here and elsewhere to my own situation and making suitable critical assessment of the input from potential installers.So far I have managed to get one quote and am waiting on another, but who knows if that will appear. ( I am not really counting the one that was a pretty much a pro forma quote done via email). The quote I do have came with some work on heat loss figures that tell me that at -2.5C the value is 7.3kW, I have had a stab at my own heat loss figures via a couple of websites, particularly the EST one, and they seem to concur. On this basis they have recommended an 8.5kW Ecodan. This size of heat pump seems to be just about capable enough, but I see others on here would oversize the pump further – and have just read the interesting front-page piece that explains why the nominal rated value is not the achieved value.
I have seen a couple of posters whose houses seem to be only a bit bigger then mine who do have higher-rated pumps, so I think I need to question the choice hard.
We are in an early 1970s 3-bed detached house, a one-off build and it seems pretty well constructed, 125sqm total area, and is now well-insulated (filled cavity walls; double glazing - some of which was replaced about 4 years ago; plenty of loft and ceiling insulation; and about half the ground floor has insulation). Rads only, and about four of these will need to be upsized according to the heat loss calcs. The house is currently heated by gas boiler at a usage of about 13000kWh per year. I believe this is an average size gas bill but presumably on the low side considering it is a detached house. I am not expecting an ASHP to be cheaper to run (certainly not with the current tariff we are stuck with at the moment) but it needs to be effective and efficient to be the environmentally worthy investment we are looking for.
Winter months can see 2000kWh + used so theoretically that should be achievable with around 800kWh of electric input – I am trying to not get too spooked by reading about usages of 75kWh+ per day, not to mention the other issues that some have with their setups.
We also have solar PV and thermal to throw into the mix. The solar thermal currently feeds a 250l heat store with gas boiler backup. I don’t know how much heat the thermal generates, I have been disappointed that it only fully heats the entire store to 55 on a handful of days so I can see a PV diverter to the tank immersion is perhaps overdue. In theory with both solar thermal and PV the less efficient HW generation by the ASHP *should* be relatively small.
But I have not got very far with understanding how the thermal generation will integrate with control and timings of the heat pump. The company that have provided the quote have not been clear on this – indeed the tank that they have referred to does not even have a solar coil! I have been reading instructions as part of my education and though the Ecodan/MELcloud application seems very accessible and well-endowed it is very much heat pump specific. The Vaillant controls on the other hand also cover solar thermal systems.
I would be interested to know of others’ experiences with running both heat pump and solar thermal together.
Hi Harry,
You may find the attached video of interest, since the LG controller can accommodate the inclusion of solar thermal.
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
3 weeks ago
-
Ecodan 11.2kw Wireless thermostat drop outs
1 month ago
-
Ecodan consuming 100kwh per day in new build!!!
1 month ago
-
Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
1 month ago
-
Transforming a Derbyshire Property into an Energy-Efficient Haven
2 months ago
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 63 Online
- 3,310 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@heatgeek Nibe also promote the two pipe buffer, I use ...
By Damon Blakemore , 17 minutes ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Well my switch from eon is tomorrow/Monday so I’ll soon...
By Westkent , 3 hours ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
So is that with external air supply?
By Johnmo , 5 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 6 hours ago
-
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I have been looking at the daily Agile rates fo...
By Toodles , 10 hours ago
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 10 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 20 hours ago
-
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 2 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 2 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 3 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 4 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 4 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 5 days ago