4 port buffer tank connections

80 Posts
9 Users
31 Reactions
1,743 Views
(@uk_pete_2000)
Estimable Member Member
387 kWhs
Joined: 4 months ago
Posts: 69
 

Posted by: @jamespa

Viessman pre-heat a specific defrost

Grant have much to same and can even be placed outside, next to the HP.

Yes when defrosting the heat has to come from some where and by changing to the 3 port buffer it will still come from the house loop and need to be replace. So it will still work the same as your open loop.

Its the anti-freeze cycle that just keeps water flowing through the heat pump for 12hrs when it's below 4c, that will draw heat from the house with no buffer. And as the CH pumps are off at this time it confines the water flow to just the buffer. 

When the HP starts up and flow temp goes up it will not worry about what's in the 3 port buffer and if the flow is still greater from the HP, it will heat up the buffer and help reduce the defrost


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10773 kWhs
Veteran
Joined: 2 years ago
Posts: 2031
 

Posted by: @heacol

I don't believe the installation of a buffer tank, complies with the building regulations.

 

 

Nice one!

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@uk_pete_2000)
Estimable Member Member
387 kWhs
Joined: 4 months ago
Posts: 69
 

Posted by: @jamespa

Just thinking about this measuring the temperatures on all 4 ports

That's how we start, 4 temps on the 4 ports. It showed we had a imbalance of 5° across the top, which I wanted to reduce having looked at the various videos on the subject.

And YES it is hard adjusting everything, leaving it 24 hrs and rechecking. If I had installed flow meters both side it might have been quick.

Learnt a great deal about my system doing this and quite happy to spend £200 this summer to put 4 valves, 2 flow meters and bypass pipes in, so once again I can check various combinations to see which works for us.

PS I've also learned/worked out that it could be automated just on temp and having automatic adjusted flow meters, but that's starting to get beyond me so no longer looking at it


   
ReplyQuote



Transparent
(@transparent)
Illustrious Member Moderator
12955 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2278
 

Posted by: @heacol

I don't believe the installation of a buffer tank, complies with the building regulations.

Wow! 😮 

I think this needs raising with Citizens' Advice.
They hold the remit for operating the Consumer Rights Act (2015).

I suspect they have a heat-pump specialist to advise the separate offices.
They must have centralised policies on which cases can go to arbitration.
I already know they have a representative who specialises in Smart Meters, for example.

@editor - the ball's just bounced into your side of court

Save energy... recycle electrons!


   
👍
1
ReplyQuote
(@jamespa)
Famed Member Moderator
10773 kWhs
Veteran
Joined: 2 years ago
Posts: 2031
 

Posted by: @uk_pete_2000

Its the anti-freeze cycle that just keeps water flowing through the heat pump for 12hrs when it's below 4c, that will draw heat from the house with no buffer. And as the CH pumps are off at this time it confines the water flow to just the buffer. 

OK thats definitely a different problem.

The buffer will presumably cool down fairly quickly in relation to 12 hrs and at that point I imagine that the heat pump might switch itself on to heat, in order to protect itself.  This being the case would it be any worse simply having a pressure operated bypass valve?

That said, when its 4C outside could you reasonably operate 24*7, or is your heat pump so oversized that this isnt possible/cost effective.  

This post was modified 1 month ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10773 kWhs
Veteran
Joined: 2 years ago
Posts: 2031
 

Posted by: @transparent

Posted by: @heacol

I don't believe the installation of a buffer tank, complies with the building regulations.

Wow! 😮 

I think this needs raising with Citizens' Advice.
They hold the remit for operating the Consumer Rights Act (2015).

I suspect they have a heat-pump specialist to advise the separate offices.
They must have centralised policies on which cases can go to arbitration.
I already know they have a representative who specialises in Smart Meters, for example.

@editor - the ball's just bounced into your side of court

Well this is an interesting line of thought and I wonder where MCS would sit (on the fence? as far away as possible?)

If manufacturer insists on a buffer tank I cant see a case based on building regs succeeding (the word 'reasonable' applies), but if they don't (or strictly didn't at the time of installation ) then there is a good argument.  In that situation the case would be against the installer.

 

This post was modified 1 month ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@uk_pete_2000)
Estimable Member Member
387 kWhs
Joined: 4 months ago
Posts: 69
 

The heat pump only turns on when we request heat. Never really tested what happens if we leave if off for 24hrs and its below 4°. I think even our house would have lost so much heat that it would take 24hrs to get back up.

Posted by: @jamespa

That said, when its 4C outside could you reasonably operate 24*7,

It's not that it can not work 24hrs, I did it for a couple of days at the start of Jan and it worked fine. 

The problems are, we need minus figures to keep it working 24/7

It's the fact it will not go below 23° flow temp and still heat the house up when it's freezing outside. 

At preset I just leave it at 27° flow temp. Then on a average day I run it 6hrs, much colder nights I run it for 8hrs a day and if we get very cold days/nights I'll run it 12hrs a day.

And YES it's oversize due to MCS calculations at the time. But it will cost too much to replace it, so I work with it.


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10773 kWhs
Veteran
Joined: 2 years ago
Posts: 2031
 

Posted by: @uk_pete_2000

The heat pump only turns on when we request heat. Never really tested what happens if we leave if off for 24hrs and its below 4°. I think even our house would have lost so much heat that it would take 24hrs to get back up.

Posted by: @jamespa

That said, when its 4C outside could you reasonably operate 24*7,

It's not that it can not work 24hrs, I did it for a couple of days at the start of Jan and it worked fine. 

The problems are, we need minus figures to keep it working 24/7

It's the fact it will not go below 23° flow temp and still heat the house up when it's freezing outside. 

At preset I just leave it at 27° flow temp. Then on a average day I run it 6hrs, much colder nights I run it for 8hrs a day and if we get very cold days/nights I'll run it 12hrs a day.

And YES it's oversize due to MCS calculations at the time. But it will cost too much to replace it, so I work with it.

All fair enough.  I dont think I can really add much more beyond what I've already said.  if somehow you need to accommodate it switching itself on at 4C, but not heating, then a byass or buffer is the only way.  I would be concerned that, at - temperatures, the water would still cool below freezing if left off for 12 hours but recirculating through the unit (unless the HP also switches to heat, which I imagine it might), I guess that where anitfreeze valves or glycol come in.

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26280 kWhs
Veteran
Joined: 4 years ago
Posts: 2986
 

@iraknic, as promised, the episode is out. Well worth watching IMO. Your case is around the 23 minute mark.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
👍
1
ReplyQuote



(@iraknic)
Trusted Member Member
197 kWhs
Joined: 2 months ago
Posts: 24
Topic starter  

@editor thanks, i will watch it


   
👍
1
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26280 kWhs
Veteran
Joined: 4 years ago
Posts: 2986
 

 In the coming weeks, I’ll be scheduling another session on buffer tanks, where viewers can submit videos and images for our panel to assess and provide advice.

If you’d like to take part, please send us a question about your system and submit high-resolution photos and videos via WeTransfer.com to editor@renewableheatinghub.co.uk.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26280 kWhs
Veteran
Joined: 4 years ago
Posts: 2986
 

@iraknic out of curiosity how did you check your delta T. Was it just purely from your control panel?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
Page 6 / 7



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security