it is not always possible to achieve a perfect scenario, but the best you can get with your current installation, will still be cheaper to run than a gas or oil boiler,

Exactly.  I don't have the experience to know the "practical tricks of the trade" as it were, just a background  that makes the maths relatively easy to understand.

I just can't see how the current pipe work can get to the max output of the unit, which is 12kW [A7/W35].  It may not need to, most of the time.

Posted by: @mike-h

I would love to get rid of my buffer tank, but my problem is the size of my existing pipework

I think that Brendons plan is a good practical one driven by experience.  From a theory point of view, and assuming your radiators can dissipate it. the below is what you would need to achieve for max load (orange) and at about 40% (green). Just spot check my formula.

image

 


   
ReplyQuote
(@heacol)
Noble Member Contributor
2477 kWhs
Expert
Joined: 4 years ago
Posts: 393
 

@william1066 Thank you, The heat pump and system will work, with reduced performance at a Delta T of up to 14 Deg C, above that, it will probably become unstable.

We do not live in a perfect world, and often we follow behind a bunch of idiots, our job is to make the best of the situation that is presented to us.

For interests sake, I have just posted this picture on LinkedIn, the screenshot was taken about 2 hours ago, the house is about 260m2, uninsulated, solid stone property in the Lake District, the primary pipework is 22mm at one end of the house (about 30 meters long) and about 50% of the radiators are on 8mm microbore. The data is taken directly from the 12 Kw Panasonic's online system. An installation, considered by the industry as impossible.

44

Director at Heacol Consultants ltd


   
👍
1
ReplyQuote
(@hughf)
Noble Member Member
3009 kWhs
Joined: 3 years ago
Posts: 487
 

@heacol I suppose on a new system with new rads and new pipework, some inhibitor and simple Strainer will suffice?

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote



(@heacol)
Noble Member Contributor
2477 kWhs
Expert
Joined: 4 years ago
Posts: 393
 

Posted by: @hughf

@heacol I suppose on a new system with new rads and new pipework, some inhibitor and simple Strainer will suffice?

Correct, Most manufacturers just specify, and supply a strainer, not a magnetic filter, for any system

 

Director at Heacol Consultants ltd


   
ReplyQuote
(@mike-h)
Reputable Member Member
1837 kWhs
Joined: 3 years ago
Posts: 197
Topic starter  

@heacol Thank you so much for your advice. That is really helpful. My understanding of heating systems has been gradually increasing since joining this forum, especially from following your posts. I have not come across auto bypass valves before, so will need to do more research on their usage. I am presuming that they maintain proper flow through the HP, while allowing lower flow through the 15mm pipework. The 22mm pipework would still need the same flow rate as the HP though. Interestingly, even on the lowest setting of the secondary pump, the delta T between the water going to and returning from the radiators is only 7 deg C. The drop across the buffer is 4 deg C!


   
ReplyQuote
(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

Posted by: @william1066
  1.   Samsung documentation says min/max for heating dT is 5-15 (though mine accepted a setting of 3 and delivers 3 - I think recommended is 5)

@william1066 are saying you able to adjust the HP's target DT directly on the samsung?

If as per the OP, you knew your system wasn't able to cope with the higher flow rate of a lower DT due to smaller pipework, can you set its operating parameters so that it runs at a wider DT and thus lower flow rate can deliver the necessary heat transfer?

 

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
ReplyQuote
(@mike-h)
Reputable Member Member
1837 kWhs
Joined: 3 years ago
Posts: 197
Topic starter  

Posted by: @william1066

@mike-h With your Internal Diameter of 20.6 and flow of 22 you have a speed of 1.1 m/s.  That will give you 6.27 kW of heat at dT 5.  I will, at some point, find or build a google spreadsheet with the calculations mentioned in my post, then you can take a look.  I think that taking your time is the right thing to do. If you did the maths on the efficiency delta between having and not having a buffer thank, it is probably not great in the short term.  Over 20 years, it likely adds up, but I think taking your time to make the right changes is important.

@william1066 Thanks for this. I have been looking at all the formulae. Assuming a velocity of 1.0 m/s is acceptable (0.9 m/s being the recommended value), then 20 L/min at a Delta T of 7 would have a velocity of 1.0 m/s and provide 9.8 kW of heat which is my design heat loss at -3.7 deg C. That assumes I ditch the glycol and install anti freeze valves. As my current flow rate has often hovered around 20 L/min and still warmed the house, I am hopeful that this might be sufficient. I am not sure whether it is more efficient to have a higher flow rate and a lower delta T, but in one of Brendon's posts he says that a  delta T of 8 deg C is the most efficient. I have altered the target delta T on my Samsung to 8, but it still seems to operate around 4-5 deg C, presumably as the heat requirement is lower now it is milder and it can't adjust the flow rate. Either that or the value I altered doesn't mean what I think it means.

Assuming the flows to my 11 radiators are all equal, which of course they won't be, the flow in my 15mm piping should be around 4/11 of the total flow, which for 22 L/min total flow would equal 8 L/min. This produces a velocity of 0.92 m/s which is ideal.

 


   
ReplyQuote
Page 2 / 2



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

Members Online

 No online members at the moment

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security