15mm piping and the need for flow separation
Posted by: @heacolit is not always possible to achieve a perfect scenario, but the best you can get with your current installation, will still be cheaper to run than a gas or oil boiler,
Exactly. I don't have the experience to know the "practical tricks of the trade" as it were, just a background that makes the maths relatively easy to understand.
I just can't see how the current pipe work can get to the max output of the unit, which is 12kW [A7/W35]. It may not need to, most of the time.
Posted by: @mike-hI would love to get rid of my buffer tank, but my problem is the size of my existing pipework
I think that Brendons plan is a good practical one driven by experience. From a theory point of view, and assuming your radiators can dissipate it. the below is what you would need to achieve for max load (orange) and at about 40% (green). Just spot check my formula.
@william1066 Thank you, The heat pump and system will work, with reduced performance at a Delta T of up to 14 Deg C, above that, it will probably become unstable.
We do not live in a perfect world, and often we follow behind a bunch of idiots, our job is to make the best of the situation that is presented to us.
For interests sake, I have just posted this picture on LinkedIn, the screenshot was taken about 2 hours ago, the house is about 260m2, uninsulated, solid stone property in the Lake District, the primary pipework is 22mm at one end of the house (about 30 meters long) and about 50% of the radiators are on 8mm microbore. The data is taken directly from the 12 Kw Panasonic's online system. An installation, considered by the industry as impossible.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@heacol I suppose on a new system with new rads and new pipework, some inhibitor and simple Strainer will suffice?
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Correct, Most manufacturers just specify, and supply a strainer, not a magnetic filter, for any systemPosted by: @hughf@heacol I suppose on a new system with new rads and new pipework, some inhibitor and simple Strainer will suffice?
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@heacol Thank you so much for your advice. That is really helpful. My understanding of heating systems has been gradually increasing since joining this forum, especially from following your posts. I have not come across auto bypass valves before, so will need to do more research on their usage. I am presuming that they maintain proper flow through the HP, while allowing lower flow through the 15mm pipework. The 22mm pipework would still need the same flow rate as the HP though. Interestingly, even on the lowest setting of the secondary pump, the delta T between the water going to and returning from the radiators is only 7 deg C. The drop across the buffer is 4 deg C!
Posted by: @william1066
- Samsung documentation says min/max for heating dT is 5-15 (though mine accepted a setting of 3 and delivers 3 - I think recommended is 5)
@william1066 are saying you able to adjust the HP's target DT directly on the samsung?
If as per the OP, you knew your system wasn't able to cope with the higher flow rate of a lower DT due to smaller pipework, can you set its operating parameters so that it runs at a wider DT and thus lower flow rate can deliver the necessary heat transfer?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @william1066@mike-h With your Internal Diameter of 20.6 and flow of 22 you have a speed of 1.1 m/s. That will give you 6.27 kW of heat at dT 5. I will, at some point, find or build a google spreadsheet with the calculations mentioned in my post, then you can take a look. I think that taking your time is the right thing to do. If you did the maths on the efficiency delta between having and not having a buffer thank, it is probably not great in the short term. Over 20 years, it likely adds up, but I think taking your time to make the right changes is important.
@william1066 Thanks for this. I have been looking at all the formulae. Assuming a velocity of 1.0 m/s is acceptable (0.9 m/s being the recommended value), then 20 L/min at a Delta T of 7 would have a velocity of 1.0 m/s and provide 9.8 kW of heat which is my design heat loss at -3.7 deg C. That assumes I ditch the glycol and install anti freeze valves. As my current flow rate has often hovered around 20 L/min and still warmed the house, I am hopeful that this might be sufficient. I am not sure whether it is more efficient to have a higher flow rate and a lower delta T, but in one of Brendon's posts he says that a delta T of 8 deg C is the most efficient. I have altered the target delta T on my Samsung to 8, but it still seems to operate around 4-5 deg C, presumably as the heat requirement is lower now it is milder and it can't adjust the flow rate. Either that or the value I altered doesn't mean what I think it means.
Assuming the flows to my 11 radiators are all equal, which of course they won't be, the flow in my 15mm piping should be around 4/11 of the total flow, which for 22 L/min total flow would equal 8 L/min. This produces a velocity of 0.92 m/s which is ideal.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 19 Online
- 3,410 Members
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist Cosy is a really good tariff for heat pu...
By ChandyKris , 6 hours ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 7 hours ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 8 hours ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 8 hours ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 13 hours ago
-
Benefits of an extra horizontal loop for GSHP
Hello everyone, We're in the process of installin...
By thewiseoldbird , 1 day ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 2 days ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 2 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 3 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 4 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 4 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 4 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 5 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 7 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 7 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 1 week ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 1 week ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 1 week ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 1 week ago
Members Online
No online members at the moment